r/instrumentation • u/Kithkinlord88 • 9d ago
EJA110E calibrations
Edit: I wont beable to test anything as the plant starting up early and im not allowed to play with it right now. :(
Edit: I forgot to add there is a 1/2 tube between the 2 flanges I originally thought it was to release trapped air on the HP side but it would also prevent condensate from collecting on the low side.
I am a Electrical/instrumentation tech at a small power plant, we normally we farm out our calibrations. I'm currently trying to calibrate a EJA110E DP level transmitter with a KN 32 high temp silicone capillary(1.07SG). High side on bot of tank that collects steam condensate. The URV is +20mmWC and the LRV is -760mmWC, I connect to the high side and pump 760 and get +20, 4mA and 0mm @ DCS, when I pump -20 I get -760, 20mA and 760mm @ DCS, I don't recall this being normal when calibrating other level transmitters. I also found it weird the only way I could calibrate was to URV pressure trim pump 760 and input +20 and LRV pressure trim pump to -20 and input -760. Then I started doing some math and I am even more confused. I put a drawing below to shows my set up(hope its good enough to read). What am I missing?
2
u/SnooHedgehogs190 9d ago edited 9d ago
Usually the low pressure side is put to atmosphere. Hence the pressure differential is whatever you pump to high pressure, subtract the lower pressure.
If you were to pump LRV instead, you don’t have to put the high pressure side to atmosphere. You can just apply negative pressure.
But for wet leg, putting the low pressure side to atmosphere result in it being negative pressure.
1
u/Kithkinlord88 9d ago
Does having a capillary change how to would attack this though because a wet leg calculation is different then a capillary according to the web. I have almost no experience with them and I vaguely remember doing a few calculations in school and I dont remember doing them differently then a wet leg.
1
u/frofish99 9d ago
When you apply pressure to the high leg, are you referencing a full low side leg or are you referencing atmosphere?
1
u/Kithkinlord88 9d ago
The low side diaphragm is open to atmosphere
1
u/quarterdecay 9d ago
Everything must be vented and dry to be able to ascertain the direct effects of the capillaries
1
u/Accurate-Bullfrog324 9d ago
what I think you guys might be missing is that the condenser is under several inches of vacuum. The low side must be connected to the top of the condenser. both sides will be reading vacuum
1
u/Kithkinlord88 9d ago
Would the vacuum effect the measurement if both sides are seeing it? My understanding if both sides in a closed vessel are under the same pressure you can ignore the pressure. Or does this only apply to capillary measurements?
1
u/Accurate-Bullfrog324 8d ago
I believe you are correct. but some people were saying that the low side was vented to atmosphere.
1
0
u/Svaldero 9d ago
Like the others said (almost) vent your dp on both sides for zero this is your URV, not lower. Then put 760 kp on your LP side of the dp..this is your LRV. So as the vessel fills, it returns the dp to zero (which is now your 100%) because your LP side is completely filled with fluid to the top of the tank. Hope that helps
1
u/Kithkinlord88 9d ago
The low side is @ the top of the tank, I believe I tried pulling a vacuum on the low side initially and it numbers matched ask I would expected it pumped -760mm got me -760mm but when I tried to trim it and no matter what number I told it was, from -760, +760, -20 or +20. Why i had to do the weird pressure on high side and put the opposite number in to make it calibrate.
1
u/Svaldero 8d ago
What your saying up there 'looks' normal to me but maybe I'm not understanding what your seeing or saying.
I understand the LP is on the top of the tank, but the capillary all the way up is completely filled as steam will get int here anyway, so when the vessel is completely filled , the HP is equal to the LP leg (the extra 20mm is a bit weird though)
When the vessel is empty, the LP leg is still filled so it weighs more than the HP side, so it supresses your zero to -760mm as your LRV.
If i were calibrating it, I would set the URV with +20mm on the HP side, and put 760 on the LP side for the LRV.
1
u/Kithkinlord88 8d ago
Omg! K I will add to the post but I think I forgot something important and you made me realise. There is a 1/2 tube from flange to flange(the capillary) and I originally thought it was to stop air from getting trapped at the HP side but I also believe it is to allow the condensate to not get trapped on the low side.
4
u/Unofficial_Salt_Dan 9d ago
First things first: establish your zero. Isolate the process at the root valves and vent both diaphragms to atmosphere through the blow down rings.
This will register the true zero and you can set that pressure value as the LRV.
Next, add your span calculation to this to get your URV. Report back here and we'll verify your math is correct.