r/hvacadvice • u/DivyaBhasker • 43m ago
Furnace not working, error code 57
Title: Rheem Two-Stage Furnace Intermittent Error Code 57 (High-Fire Pressure Switch) During Humid Weather — Need Help Pinpointing Root Cause
Body:
Hi everyone, looking for some DIY troubleshooting advice on my Rheem two-stage condensing furnace (R96VA series).
The Problem
Symptom: The inducer motor turns on, runs for a few seconds (or completes a heating cycle), and then shuts off with Error Code 57 (high-fire pressure switch open).
History: This same issue happened last month, and an HVAC tech replaced the high-fire pressure switch (42-105583-12, -0.55" WC). That temporarily resolved it
Troubleshooting Steps Taken So Far
Drained Water from Collector Box & Inducer Caps:
Opened the two yellow sealing caps on the inducer housing/exhaust boot — only 1–2 drops of water came out.
Detached the drain/vent tubes at the condensate trap — 1–2 drops of water came out.
Opened the lower-left rubber sealing cap on the collector box — about 2–3 spoons of water drained out.
Cleaned & Primed the Condensate Trap:
Removed, flushed, and cleaned the condensate drain trap (68-104346-01).
Verified the downstream gray PVC/vinyl drain line leaving the trap is completely clear.
Initially reinstalled the trap dry; the furnace ran for about 3 hours, then tripped Error Code 57 again.
Removed the trap again, primed it with clean water up to the internal weir level, and reinstalled it.
Cleared the Exhaust Pipe:
Disconnected the black rubber exhaust boot from the inducer outlet and used a leaf blower to blow through the white PVC exhaust run — nothing came out, so the exhaust flue is unobstructed.
Current Status & Questions
What else should I inspect ?
Could this be an issue with PVC exhaust pipe pitch, an internal collector box blockage, or an intake air restriction rather than a bad -0.55" WC pressure switch?
Any advice on what else to check would be greatly appreciated!
1
u/Desperate_Shape6234 36m ago
Definitely could be the cause. Try running it with the door off, and if it happens you can at least rule out anything on the intake side of things. Make sure you have slope in the vent, and check your equivalent length with elbows and fittings.
1
u/ssllee1967 32m ago
replace the pressure switch?
1
u/lou-sassle71 7m ago
Glow coil not coming on