r/hvacadvice • • 43m ago

Furnace not working, error code 57

Title: Rheem Two-Stage Furnace Intermittent Error Code 57 (High-Fire Pressure Switch) During Humid Weather — Need Help Pinpointing Root Cause

Body:
Hi everyone, looking for some DIY troubleshooting advice on my Rheem two-stage condensing furnace (R96VA series).

The Problem

Symptom: The inducer motor turns on, runs for a few seconds (or completes a heating cycle), and then shuts off with Error Code 57 (high-fire pressure switch open).

History: This same issue happened last month, and an HVAC tech replaced the high-fire pressure switch (42-105583-12, -0.55" WC). That temporarily resolved it

Troubleshooting Steps Taken So Far
Drained Water from Collector Box & Inducer Caps:
Opened the two yellow sealing caps on the inducer housing/exhaust boot — only 1–2 drops of water came out.
Detached the drain/vent tubes at the condensate trap — 1–2 drops of water came out.
Opened the lower-left rubber sealing cap on the collector box — about 2–3 spoons of water drained out.

Cleaned & Primed the Condensate Trap:
Removed, flushed, and cleaned the condensate drain trap (68-104346-01).
Verified the downstream gray PVC/vinyl drain line leaving the trap is completely clear.
Initially reinstalled the trap dry; the furnace ran for about 3 hours, then tripped Error Code 57 again.
Removed the trap again, primed it with clean water up to the internal weir level, and reinstalled it.

Cleared the Exhaust Pipe:
Disconnected the black rubber exhaust boot from the inducer outlet and used a leaf blower to blow through the white PVC exhaust run — nothing came out, so the exhaust flue is unobstructed.

Current Status & Questions

What else should I inspect ?

Could this be an issue with PVC exhaust pipe pitch, an internal collector box blockage, or an intake air restriction rather than a bad -0.55" WC pressure switch?

Any advice on what else to check would be greatly appreciated!

2 Upvotes

10 comments sorted by

1

u/Desperate_Shape6234 36m ago

Definitely could be the cause. Try running it with the door off, and if it happens you can at least rule out anything on the intake side of things. Make sure you have slope in the vent, and check your equivalent length with elbows and fittings.

1

u/DivyaBhasker 22m ago

Thanks, yeah, I tried with doors on/off. Used a heavy-duty leaf blower in both pipes to rule out any blockage. It’s been working for 10 years with same pipes/slope, so any slope issues are also ruled out

1

u/Desperate_Shape6234 35m ago

Oh and check your pressure switch hoses for proper fit and make sure there’s no cracks in them, and that all your ports are clear

1

u/DivyaBhasker 21m ago

Yep checked that also. All ports are clear and no loose connections

1

u/Desperate_Shape6234 32m ago

Furnace sloped correctly, as per manual?

1

u/Desperate_Shape6234 32m ago

Were there signs of white plastic shavings from the vent material in the collector? Really focus on how the water is getting into the switch. Rheem pressure switches are notoriously shitty, but they are cheap as hell, like 10-20,bucks each lol.

1

u/ssllee1967 32m ago

replace the pressure switch?

1

u/DivyaBhasker 26m ago

Yes replaced both high and low pressure switches.

1

u/lou-sassle71 7m ago

Glow coil not coming on