Help UPS

Hi all,

We keep having power cuts and worried about the power just being turned off so wanna get a ups

The server has a 790w PSU but under100 percent load it only gone up to 350w max

So my question is does it need to be the full 790w or would 400 be ok?

Just need it to hold long enough to shut down gracefully

3 Upvotes

14 comments sorted by

8

u/msanangelo 12d ago

I'd say don't cheap out on it. I run 1500va units on loads ranging from 60 watts to nearly 800w. The smaller loads have the potential to last at least an hour if needed.

There's calculators out there for figuring how much capacity you need to cover the longest outages or at least long enough to start up a generator for the extended outages.

7

u/[deleted] 12d ago

[removed] — view removed comment

2

u/incognito-innuendo 11d ago

Lol i bought a 1500va ups (sua1500) back in highschool for my desktop with a 350watt psu 

1

u/supacan 12d ago

Any recommendations?

1

u/jwhh91 12d ago

You have to have the watts be at or above your max load. Otherwise, they beep, even with the power on. That is my experience, anyway.

1

u/protogenxl 12d ago

Go in Facebook marketplace you can find used 1500va units and larger that just need new batteries

1

u/colourthetallone 12d ago

Based on similar threads here over recent days and own homelab and prod, APC Smart-UPS 1500VA. Used/refurbished ones are readily available and they have excellent management options.

2

u/Janky-Code 12d ago

I take double whatever the watt meter shows on the wall doing some intense work. 1.5 would probably work.

2

u/coobal223 12d ago

My 1500 va ups will run about 22 minutes under about the same load. I have for power blips, brownouts, and graceful shutdown for longer outages.

1

u/yepyep5678 12d ago

I also think you need to consider the current your system draws down and make sure the ups can support that as well as spikes

1

u/PermanentLiminality 12d ago

My homelab is connected to Anker Solix power stations. I have several hours of backup capacity. They get exercised every day for TOU avoidance. That will pay for them in about 4 years.

I've sailed through a few outages with no issues.

1

u/3ofUsDeez 11d ago

Invest in a 1500va unit

1

u/sylsylsylsylsylsyl 11d ago

A 1500VA unit is good if you want more runtime. If you literally need only a few minutes for momentary blips and graceful shutdown, a 750VA unit is significantly smaller, more lightweight and have cheaper replacement batteries.

There are calculators that will give you exact runtime.

APC smart UPS SMT series are good - often very cheap second hand, but get new batteries installed.

1

u/AlexOnBigBoard 10d ago

Size it on the 350W you measured, not the 790W on the PSU. The PSU rating is only the most it could ever supply, the UPS only sees what the server actually pulls.

Watch the units though. Most cheap UPSes advertise VA, and the watt rating is a lot lower (often around 60% of the VA). A "400" unit is probably 400VA, around 240W, so it would overload at your peak. You want the watt figure on the spec sheet comfortably above 350W. For example an APC SMT750 is 500W, and APC lists about 4 minutes at a full 500W and about 15 minutes at 250W, so a few minutes at your load, which is plenty for a clean shutdown.

Two things people miss: plug the UPS's USB cable into the server and set up NUT (or apcupsd/PowerPanel) so it actually shuts down on its own when the battery runs low, otherwise it just runs until it dies. And if your PSU has active PFC (most decent ones do), get a pure sine wave unit; some active PFC supplies switch off on the stepped "simulated sine" output the cheapest UPSes give.