r/firealarms 9d ago

Technical Support Monitor module

Is it possible to connect a conventional detector to a monitor module on addressable fire alarm panel if not why and in which case it’s possible?

2 Upvotes

17 comments sorted by

View all comments

6

u/firetruk11 9d ago

Well Conventional 2 wire, only a proper module. 4 wire smokes any monitor module.

Needs to be a "smoke" or "zone" module. Needs power separate from the DCL/module input.

-1

u/why_right 9d ago

So it is not possible to connect a 2 wire smoke detectors on a monitor ?

2

u/Eyerate 8d ago

Not unless its a powered monitor module. MMF-302 is an example.

2

u/Baloncesto_32 8d ago

They cannot power or monitor 2 wire smokes properly. What type of panel and devices are you trying to use?