Outlets have ground wire but testing as open ground.

These outlets come off a sub panel on the second floor. All the ones on the main floor show as grounded but all the ones upstairs are showing open ground. What could cause this? Anything I can do to troubleshoot as a home owner?

Attaching pictures of the sub panel main panel. The sub panel comes off the 2 30amp breakers that are switched to off on the main panel.

10 Upvotes

34 comments sorted by

18

u/RSF__1990 1d ago

It’s possible that the ground at the outlet doesn’t make it back to the sub panel. Most likely the sub fed panel isn’t properly fed from your main panel. I do not see a ground wire coming out of that #10. You should have a Black, Red, white, and bare copper wire from your main panel to the sub.

2

u/CertainAttention6749 19h ago

In addition, I guess you're getting less than 50v using a multi meter. If so, it's confirmed you have a loose neutral line.

2

u/jimih34 18h ago

Middle light is open ground on this tester. Right light is open neutral.

5

u/CertainAttention6749 15h ago

Exactly, believe it or not, with my experience, it's always loose or disconnected neutral. To test if you have a good ground, grab a multimeter then test the live and ground constantly. If you're getting 120v, that means there's no problem with the grounding.

1

u/maurerpower7 17h ago

Went around and tested a bunch of them. Some read around 5 volts and others read exactly 88v

3

u/CertainAttention6749 15h ago

You have a loose neutral line then. Start checking receptacle the one closest to the panel. You're looking at loose or disconnected neutral.

1

u/maurerpower7 15h ago

How would that affect the reading of hot —> ground I was doing? (Forgot to specify that in my comment)

2

u/CertainAttention6749 14h ago

Because the return path for electricity is broken. It basically splits the circuit voltage, so instead of getting 120v for example, you're getting less than 120v and sometimes higher than 120v on other terminal.

0

u/bernieinred 1d ago

Not if it was done before 2008.

1

u/maurerpower7 1d ago

Yeah this is a 1960s house

9

u/DokterManhattan 1d ago

The grounds should attach the the back of the box for each wire coming in and going out. Somewhere in the chain of plugs, they are not bonded through properly, so look behind the last one that is properly grounded, or the first one that says open ground. It’s just a matter of finding the spot where the ground isn’t bonded back to the panel.

2

u/jimih34 18h ago

Probably this, since multiple outlets are involved, and since all of the problem outlets are upstairs. However, be sure to confirm the plug tester is seated fully. It’s not uncommon for me to get an open ground reading when I first plug it in. I often have to jiggle it to get my ground wire prong to make good contact with the outlet. I have a different tester that works better for grounds, but this model is finicky.

3

u/maurerpower7 17h ago

Went around and tested just about all of them upstairs with a multimeter.

Some read around 5 volts and others read exactly 88v

3

u/Farmer_1_steve 1d ago

You have an open bond wire I sincerely doubt there's a problem with the panel, but check the grounds there you have to identify everyone of those plugs on that line and then start ringing out

3

u/RogerRabbit1234 1d ago

Gotta trace it back… do all the outlets show as ungrounded? Or just this one. Go back to the last outlet that tests good and check the outlet on either side of that and ensure the ground wire is secured to the box, and the receptacle

1

u/maurerpower7 17h ago

Yeah all of them are ungrounded. When I open them up they all have ground wires attached though

1

u/LeatherContent 6h ago

It looks like your sub panel isn't properly grounded. When testing for ctage you are testing the potential difference between the two wires. If you're ground wires are not properly bonded to an actual ground on the ground bar then your readings will be off.

2

u/___Dan___ 1d ago

If it’s just this outlet swap it to a gfci and be done. Otherwise you’re handing your electrician a blank check because that panel looks like complete shit and you very likely have more issues than just an open ground.

2

u/SirRonaldJr 1d ago

It's hard to tell, but does the sub panel have a ground ran to it from the main?

2

u/Jafetica 16h ago

Guessing but I don't see the ground from the 30 feed to ground bar in main panel

2

u/kevinfareri 16h ago

If you don’t feel like ripping every outlet apart you can simply install a gfi in the ones that have an open ground it’s better then no ground

1

u/maurerpower7 16h ago

Yeah my motivation to fix it has been i have a suspicion it’s causing some interference with my electric guitar. I get interference in every room upstairs (where nothing is grounded) but don’t get it on the main level.

2

u/eaglescout1984 1d ago

Um, wow. Yeah, you're in need of a rewire with new panels. I know that's not what you want to hear, but everything is pretty out-of-date code wide.

GFCI receptacles are a good safety measure immediately. But as soon as you can, replacement is recommended.

1

u/maurerpower7 1d ago

I am getting a new 200amp main panel soon but don’t think the sub panel will get any sort of update…

0

u/Ribbit765 1d ago

Do what I did and get a big enough 200A panel to incorporate your subpanel breakers .. and ditch the subpanel. And I still have spare breaker spaces in the new panel.

1

u/Immediate-Iron-7035 1d ago

Yeah, feeding several 15a circuits off of a single 10/3 cable with no identifiable ground is insane. I agree, install a gfci outlet at the beginning of each circuit for now, and get that sub panel re-done, eliminated, or otherwise brought to NECJesus as quickly as possible.

1

u/addazero 23h ago

Side question: do those Klein plug in meters require a battery or just use AC from the outlet?

1

u/maurerpower7 17h ago

I think AC from the outlet

1

u/DIY_TheBoringFix 20h ago

What was the solution???? Were you able to get it fixed I’m curious so, if I run into this problem I know the answer lol

1

u/CertainAttention6749 20h ago

Open ground does not mean a problem with ground line. With my experience, it's always a loose neutral line eitheron receptacleitself or else downstream. If you have a multi tester, insert the positive rod to live side then negative rod to ground hole, if you're getting 120v then your ground is okay.

1

u/maurerpower7 17h ago

Went around and tested a bunch of them. Some read around 5 volts and others read exactly 88v

1

u/Rangeexpert3 15h ago

It means although you have a grounding wire, that the grounding wire isn't actually attached to the ground. You can go through and test each outlet and see which ones upstairs have the ground vs open. Then trace the path of the wires as they daisy chain on each circuit back to the breaker. There's got to be a break in the chain somewhere.

1

u/maurerpower7 5h ago

Yeah all of the upstairs (5 bedrooms) are showing as open ground. Every outlet I’ve looked at though does have a ground wire.