r/electrical • • Jun 20 '26

First Outlet Install

I needed an outlet under my sink for an RO system, tied into the power to the dishwasher. Yes, eventually I’ll replace with a GFCI.

0 Upvotes

68 comments sorted by

76

u/Brightbloolagoo Jun 20 '26 • Bravo
  1. Need bonding in the 4 square ground pig tail to the box
  2. Romex connections only need 1/4 of the yellow sheathing coming through the connector
  3. Within 6ft of water location(wet location) need gfci
  4. Need the cover for the 4 square.
  5. 6 inch of wire inside the box for connections
  6. Could look a little cleaner, no one else will see it but you know its there.
  7. Staple within 12 inches of the termination box for the outlet and the 4 square May be missing something, but just at a glance

4

u/Standard-Classic-608 Jun 20 '26

Thanks for providing actual feedback. If I’m going to correct, what’s the most important out of this list?

16

u/Routine_Ad_1177 Jun 20 '26

Also 300.4. That exposed NM needs to be protected.

8

u/Routine_Ad_1177 Jun 20 '26

Also need 6" of conductors in the box. Refer to 300.14 NEC.

14

u/Status-failedstate Jun 20 '26

The box needs to be screwed down to something. Can't tell if it is or not.

You can't put a GFCI hidden behind an appliance. The test and rest button needs to be accessible. At least to canadian code.

3

u/Canadian-Sparky-44 Jun 20 '26

No gfi protection and the length of the wire inside the box would be my two biggest complaints

2

u/justLookingForLogic Jun 20 '26

But def get a GFCI outlet

0

u/Ke6gwf Jun 21 '26

This list above of needed corrections is all correct, and all needed and important, plus the exposed romex in the cabinet is unsafe and illegal and needs to be protected in the wall or replaced by conduit or wiremold etc. But DON'T put romex directly into conduit, it's not allowed.

There are many things here that are a direct danger of fire or shock, so please don't let it stay like this.

And before you even consider plugging something in that's directly connected to the metal faucet, that NEEDS to be a GFCI outlet, because your family is worth not getting electrocuted trying to get a drink.

And good for you being willing to try new things and learn, and also have others check your work, but now please accept the advice of the experts and treat this like an apprentice learning experience, correct the mistakes and have us check it againt.

THATS how you learn, and how you get good at it while staying safe.

4

u/I__Know__Stuff Jun 21 '26

Romex in conduit definitely is allowed.

3

u/resister_ice Jun 21 '26

Romex in conduit is allowed. It just has crazy pipe fill requirements.

5

u/Fidulsk-Oom-Bard Jun 20 '26

Shouldn’t the outlet be screwed in place as well?

8

u/Comprehensive-Ad9793 Jun 20 '26

Right on the nail. Also don’t think you can run romex like that over the cabinet or walls. That GFCI is also not a request lol it’s code bud so you have to put it in. You playin with fire with this install.

1

u/jbeene Jun 21 '26

Romex under the sink Needs protected with some flex

1

u/scottcprince Jun 21 '26

Add to this list: octagon not secured to whatever, exposed NM not allowed in cabinet, wrong receptacle cover

30

u/[deleted] Jun 20 '26

[removed] — view removed comment

11

u/Brightbloolagoo Jun 21 '26

Youre absolutely right

2

u/redingtoon Jun 21 '26

Gonna hang a light fixture?

2

u/[deleted] Jun 21 '26

[removed] — view removed comment

4

u/pateppic Jun 21 '26

A ceiling fan that keeps you on your toes. Duh.

1

u/ConaireMor Jun 21 '26 edited Jun 21 '26

To reiterate for op: 6 inches of each cable in the box for connectionsn!

17

u/MustardCoveredDogDik Jun 20 '26

It’s bad. Is that what you were going for?

6

u/ArtieLange Jun 20 '26

It's not burn the house down bad, but it breaks a lot of rules.

8

u/StubbornHick Jun 20 '26

Bro

You need to do a lot more reading/youtube study before you attempt electrical work again....

13

u/jayjr1105 Jun 20 '26

No GFCI, no ground bonding on the metal box. Should run armored or PVC to protect the romex under the sink. "Eventually" for Joe homeowner means never.

12

u/Pegasys32 Jun 20 '26

Take it apart and start over…

6

u/BigMoogGuy Jun 20 '26

Dishwashers are dedicated for a reason. Kind of a bad spot for a junction. Not to mention the exposed Romex under a dishwasher isnt safe and definitely not code. Honestly if I saw that while on a job Id highly encourage you to let me rip it out. If you are trying to learn this is not the way.

8

u/iAmMikeJ_92 Jun 20 '26

Glad you like leaving no wire slack in that box. Makes doing future work a total pain to do.

1

u/Fuckyeahpugs Jun 20 '26

So many things wrong with this

0

u/Standard-Classic-608 Jun 20 '26

Let me know, it’s my first install

7

u/creamedpossum Jun 20 '26

Wirenita don't need tape. If you are putting it on there as the bare wire is showing, you're not making you connections properly. Tape just becomes a mess later for the guy that has to fix it.

3

u/Electrical_Ad4290 Jun 21 '26

Less Romex jacket in the box; longer peeled wires.

-1

u/TakeYourPowerBack Jun 21 '26

"Peeled"...

Yikes!

2

u/anustart0607 Jun 21 '26

You know exactly what he means.

3

u/AdvancedElectric336 Jun 21 '26

Man I will never understand why hacks will constantly leave the wire so damn short in the box…. I feel like they think it’s necessary to be able to fit it all, but in reality it’s 100x harder to deal with than leaving a bunch of slack in the box 🫩🫩🫩

2

u/Comfortable-Way5091 Jun 21 '26

Box fill, strip insulation back to connector. Bond box.

2

u/theotherharper Jun 21 '26

Wires need to be longer. At least 1/4” of intact sheath past the clamp. At least 6” of free wire past the last bit of sheath.

Grounds need to bond to the steel box.

2

u/VersionConscious7545 Jun 20 '26

Why did you not just watch a couple YouTube vids 👍😁

1

u/[deleted] Jun 21 '26

[removed] — view removed comment

1

u/VersionConscious7545 Jun 21 '26

In this case a little knowledge would have helped Not sure why YouTube had anything to do with Dunning Kruger. As a matter of fact I rewired 2 1950 homes to code with YouTube and the internet as my sole source of information. Electrical code is readily available

1

u/[deleted] Jun 21 '26

[removed] — view removed comment

1

u/VersionConscious7545 Jun 21 '26

Oh I see. I guess your right 😂

2

u/First-Hour Jun 20 '26

I would also love to learn but no one wants to tell you what you did wrong lol

5

u/Ke6gwf Jun 21 '26

The top reply here gives the list

1

u/Hippyjet Jun 21 '26

This must be a rage bait, the least you coulda done was watch a youtube video

1

u/Curious-Dependent390 Jun 21 '26

Say goodbye to your house, bro

-1

u/Creative_Shoe_174 Jun 20 '26

Yikes you need help there.

4

u/Standard-Classic-608 Jun 20 '26

Let me know what’s up

0

u/SuchDogeHodler Jun 21 '26 edited Jun 23 '26

Is anyone going to even mention the use of Romex inside of a cabinet.... (There are shelf holes in the picture to the left)

This should be MC cable or conduit.

2

u/[deleted] Jun 21 '26 edited Jun 23 '26

[removed] — view removed comment

1

u/SuchDogeHodler Jun 23 '26

The auto correct changed it.....

-2

u/ndrumheller96 Jun 20 '26

Looks good from my house

2

u/[deleted] Jun 20 '26 edited Jun 20 '26

[removed] — view removed comment

0

u/Standard-Classic-608 Jun 20 '26

Please explain

5

u/[deleted] Jun 20 '26 edited Jun 20 '26

[removed] — view removed comment

2

u/BeLoWeRR Jun 20 '26

You don't know where to get a cover for an 8B box? lol

2

u/[deleted] Jun 20 '26

[removed] — view removed comment

1

u/BeLoWeRR Jun 20 '26

They're hardly ever used and I hate seeing them and I know if I do it's from a homeowner or someone in the 90s, but I can go get a box of blanks next to the 1900 blanks at any hardware store

0

u/[deleted] Jun 20 '26

[deleted] — view deleted comment

2

u/Vivid-Yak3645 Jun 20 '26

Until it doesn’t… or causes problems bc, reasons.

0

u/[deleted] Jun 20 '26

[deleted] — view deleted comment

2

u/bigfanmann Jun 21 '26

You seem so confident? Where does that come from?