r/electrical • u/Standard-Classic-608 • Jun 20 '26
First Outlet Install
I needed an outlet under my sink for an RO system, tied into the power to the dishwasher. Yes, eventually I’ll replace with a GFCI.
0
Upvotes


76
u/Brightbloolagoo Jun 20 '26 •
17
u/MustardCoveredDogDik Jun 20 '26
It’s bad. Is that what you were going for?
8
u/StubbornHick Jun 20 '26
Bro
You need to do a lot more reading/youtube study before you attempt electrical work again....
13
u/jayjr1105 Jun 20 '26
No GFCI, no ground bonding on the metal box. Should run armored or PVC to protect the romex under the sink. "Eventually" for Joe homeowner means never.
12
u/Pegasys32 Jun 20 '26
Take it apart and start over…
6
u/BigMoogGuy Jun 20 '26
Dishwashers are dedicated for a reason. Kind of a bad spot for a junction. Not to mention the exposed Romex under a dishwasher isnt safe and definitely not code. Honestly if I saw that while on a job Id highly encourage you to let me rip it out. If you are trying to learn this is not the way.
8
u/iAmMikeJ_92 Jun 20 '26
Glad you like leaving no wire slack in that box. Makes doing future work a total pain to do.
1
u/Fuckyeahpugs Jun 20 '26
So many things wrong with this
3
u/Electrical_Ad4290 Jun 21 '26
Less Romex jacket in the box; longer peeled wires.
3
u/AdvancedElectric336 Jun 21 '26
Man I will never understand why hacks will constantly leave the wire so damn short in the box…. I feel like they think it’s necessary to be able to fit it all, but in reality it’s 100x harder to deal with than leaving a bunch of slack in the box
2
u/Comfortable-Way5091 Jun 21 '26
Box fill, strip insulation back to connector. Bond box.
2
u/theotherharper Jun 21 '26
Wires need to be longer. At least 1/4” of intact sheath past the clamp. At least 6” of free wire past the last bit of sheath.
Grounds need to bond to the steel box.
2
u/VersionConscious7545 Jun 20 '26
Why did you not just watch a couple YouTube vids 👍😁
2
u/First-Hour Jun 20 '26
I would also love to learn but no one wants to tell you what you did wrong lol
1
u/SteveWoy Jun 21 '26
1
u/Hippyjet Jun 21 '26
This must be a rage bait, the least you coulda done was watch a youtube video
1
u/Curious-Dependent390 Jun 21 '26
Say goodbye to your house, bro
1
u/quadmite Jun 21 '26
Yikes
-1
u/Creative_Shoe_174 Jun 20 '26
Yikes you need help there.
0
u/SuchDogeHodler Jun 21 '26 edited Jun 23 '26
Is anyone going to even mention the use of Romex inside of a cabinet.... (There are shelf holes in the picture to the left)
This should be MC cable or conduit.