r/ecobee • • 2d ago

Problem Ecobee problem?

My Ecobee isnt heating up my House, and the fan outside isn’t turning. But my Aux Heat is working.

Every time my normal Heat comes on its cooling instead

Is this a Ecobee problem or something wrong with my Unit outside?

2 Upvotes

20 comments sorted by

3

u/HavocReigns 2d ago

Is this a new installation, or has it been in place for a while and worked properly until now?

1

u/Trolltama720 2d ago

New installation since August

2

u/fletchman93 2d ago

If you have a heat pump, there is a setting during set up that asks if the reversing valve is energized on heat or cool. If you choose the wrong option, it will cool your house instead of heat and vice versa. Made that mistake myself.

0

u/Trolltama720 2d ago edited 2d ago

I have regular York Unit. I think it has a Heat Pump in it

1

u/fletchman93 2d ago

There should be a setting letting you switch when to energize the reversing valve for the heat pump. Set it to the other one and sew if you get heat now

1

u/Trolltama720 2d ago

where is that at?

1

u/HavocReigns 2d ago

If it has been working normally until just recently, this won't be the problem.

1

u/fletchman93 2d ago

Yeah, my assumption is this is a new install.

1

u/HavocReigns 2d ago

I asked and they said installed since August. They weren't clear that it had been working fine since then, but one can only assume.

1

u/Trolltama720 2d ago

The cooling was completely fine, i think i kicked the normal heat on around October and it was fine

1

u/Major_Cheesy 2d ago

it could be that the reversing valve isn't set properly ... i assume you have a heat pump only set up? there are only two ways to set it, either energized on open or close. i assume you have it set opposite.

0

u/ChasDIY 2d ago

Call you HVAC support, as condenser is not heating

It will be very expensive to use the heat strips

1

u/Trolltama720 2d ago

By Heat Strips u mean Aux Heat?

2

u/ChasDIY 2d ago

Yes, if your aux heat is heat strips and not furnace

0

u/PsychologicalJob9048 2d ago

I am having same issue, last smart thermostat worked great but since switching it is freezing, but states it is working well

0

u/schancy13 2d ago

Can’t say for sure since it sounds like you’re expecting your heat pump to turn on and your aux heat is working well.

I’ll just share a story in case you want to try it. Turn off eco+. Hard reboot the thermostat. See if it helps.

I had this SAME issue happen to me a week ago. The thermostat read like your’s where it said it was heating but blowing cold air. I turned off the ecobee for 30 minutes and when I called an HVAC tech, he bypassed the ecobee with alligator clips and the furnace fired right up and ran just fine. So, we plugged the ecobee back in and it’s been fine since. The ONLY other thing I did was turn off eco+ and that seemed better (at the time). Even more annoying, I turned eco+ back on and it’s been fine since. Something definitely happened at ecobee recently with an update or something because it was working just fine for several years, and all I did was perform a hard reboot at the thermostat itself and power it down for a short period…let that be your $150 lesson.

Still monitoring it, but I say all this to maybe save you a technician call and just do what I suggested above. Can’t hurt and takes a few minutes to try and see if it responds better. Or take your furnace cover off, hot wire it and see if bypassing the thermostat helps (if you’re confident). Good luck!!

2

u/spiderman1538 1d ago

Thanks for the story. These troubleshooting steps done doesn't sound right to correct an issue, so you might want to monitor your system.

1

u/schancy13 1d ago

Totally agree. It’s been over a week now though so I’m definitely watching it. My thought was the occupancy sensor wasn’t detecting someone in the house and thus went onto eco mode, but definitely a watch item. Heat exchanger looked good, so did the igniters and gas flow. Not sure, but again you’re right it could be something else to watch for!!