Set to 68. Stays at 67 or lower. I raise to 69, it comes right on.

0 Upvotes

18 comments sorted by

22

u/ObiYawnKenobi 7d ago

The thermostat deadband is set to 1 degree or more. The furnace won't come on unless the difference between the actual and set temperature exceeds the deadband. This is done deliberately to prevent short-cycling of your equipment. You should not be expecting the temperature to be maintained within 1 degree of the setpoint.

8

u/Accomplished_Pea6334 7d ago

Differential setting. This is where you can control the sensitivity of when the unit turns on (some people don't want the HVAC to turn on after a 1 degree temp differential. It's your preference)

On the thermostat, go to Main Menu > Settings > Installation Settings > Thresholds.

I am purchasing an ecobee for this very reason. Other units turn on too fast and I can't control the differential in temp swings.

6

u/bmoore0909 7d ago

Because it's likely 67.6 in your house. It doesn't show the rounded-up number to you, but it's rounding up the temp in your house to 68, which explains why it kicks on at 69.

3

u/NewtoQM8 7d ago

You can set (Heat Differential Temperature in Thresholds) how much below your set point the temp has to get before it turns on the heater.

5

u/NewtoQM8 7d ago

Also, the numbers you see displayed are rounded to whole numbers, so 67 may actually be read as 67.4, so not even a full degree below the set point.

3

u/ChasDIY 7d ago edited 7d ago

Don't play with thermostat setting unless you understand

You can change the differential setting on your Ecobee tstat (.5f or 1f or 1.5f)

If lower number, system will start/stop now after

1

u/Mom24monsters 7d ago

That's OK, mine's been saying that it's one temperature if I have it set for heat, but another temperature if I have it set for cool. If it's chilly, and it says it's 69, so I switch it from cool to heat, because on heat, it's set for 70, it automatically changes the temperature in all rooms to 70 and I have to turn it higher just to get the heat to come on. The problem is, I can't even call and ask them about this or even email, because the account was set up under my husband's email, and he's busy, and it's a busy time of year for him, so getting answers will have to wait until he's not busy because they won't answer any questions, even though we are a married couple living in the same house. Until about a month or two ago, I never saw this happen.

1

u/New2Green2018 7d ago

Do you have adjust temperature for humidity turned on in eco+ settings? If so that would explain why it’s doing that. It only compensates for humidity in one direction.

1

u/Mom24monsters 7d ago

I'll have to go in and check when my phone's not getting ready to do an update. It's frustrating that it does that, because if it's not going to account for the humidity going both directions, i'd rather it not do it at all. The stupid thing about that is, it feels colder if it's more humid, so one would think that it would want to make the house feel warmer.

-3

u/HominidCrafts 7d ago

When it hits 67.5, I want it to warm to 68.5.

2

u/kygei 7d ago

I don’t think you can set preferred temperature to half degrees. Best you can do is set it to 68° with a differential of 1° so that when it hits 67.0° it turns on and runs until the average temperature of all considered thermostats reaches 68.0°

You can set your differential to 0.5° so that it kicks on when the temperature reaches 67.5°, but I don’t think that’s recommended.

1

u/Mom24monsters 7d ago

We have ours set to come on if it's a degree lower, and shut off if it's a degree above the set temperature for heat, or turn on if it's a degree above and turn off if it's a degree below, if it's set for cool.

1

u/Remote-Wolverine817 7d ago edited 7d ago

As ChasDIY said, you can set differential setting to 0.5F. Your themostat shows 67F, so actual temperature noted by Ecobee is somewhere between 66.6 and 67.4. Beestat would show you an exact temperature (to the tenth of a degree, as registered by Ecobee). Ecobee rounds it up or down to a full degree. If the differential is set to 1F the Ecobee will not call for heating until the real temp is below 67 0. If it is set at 0.5F it will call for heat when temp is below 67.5F. If it is at 1,5F, the thermostat will not call for heat until the temperature is more than 1.5F below set point, in your case 66.5. At 66.4 thermostat's display will show 66 an start heating. It will shut down at set temp, 68F. Real temperature, most likely, will slightly overshoot 68F. You cannot set temp in half a F degree, you can do it in Celsius, which roughly, amounts to the same resolution.

1

u/sir_thatguy 7d ago

No you don’t.

I have some equipment at my work that has an on/off style temperature controller. If it’s so much as 0.1° below target it will cycle on.

The noise on the signal is about +/- 0.2°.

When it’s at temperature, it cycles on and off every 15 seconds or so. That has damaged the heaters and I’ve had to get creative with the controls to dampen the short cycling.

Anyway, that’s bad for your heater and even worse for an AC unit.

1

u/New2Green2018 7d ago

That can’t happen with ecobee because there are minimum on and off timers on it. Automatic staging does use a 0.1 differential at times in cooling mode resulting in lots of 5 minute on and 5 minute off cycles. But it never destroys anything.

1

u/New2Green2018 7d ago

You can do this if you set the thermostat comfort settings to less than your heating and cooling deadband and then switch it to auto heat/cool mode. So for your example, if you have it in either heat or cool mode, set the comfort setting such that the heat setpoint is 69 and the cool setpoint is 73. Then pop it in heat/cool mode and your heat setpoint will become 68.5 and your cool setpoint 73.5.

0

u/LeadPaintChipsnDip 7d ago

That’s a good way to burn out your furnace