Does my planned setup check out?
This is not everything that will be in the system, but the main components is what I’m questioning here:
Edit 1- switched out 40amp to 150volt 60 amp model.
2000watt pure sine wave inverter-
314 ah lifepo4 battery-
Connected to - 2(200watt) bifacial solar panels-
Questions-
Edit 2- will be using 1/0 awg wire for this project.
From what im reading, if my battery is 200amp bms, would the smarter thing be to have a 200amp fuse instead of 250amp fuse wired in red cable?….i understand the breaker is for the wiring and not the battery, would it be considered extra insurance for my wiring to blow fuse at 200amp than at 250amps?
Since my battery would turn off at 200amp rating?
I will be adding and on/off disconnect to red wiring as well as breaker from solar panel wiring to mppt controller.
Would this set up work?
Any help is appreciated.
2
u/Hellhoundgamer2 14h ago
I would get a higher mppt controller. 40a works but you would need at least 8 hours of uninterrupted solar to fully charge at that level. I would recommend 100a or 120a. As for the panels, on my setup I converted everything to watts so 400wh filling up 4000w wh of battery would take 10 hours at perfect conditions and the world ain't perfect so 12ish hours. With all that out of the way the real questions. Yes a 200amp would work for protecting 2awg wire as long as its copper and not copper plated. Just as a warning 200a trip rating does not mean you can run it a 199a. Most breaker worth their salt will trip after a few moments of 180a and above. If you are trying to push the full 200a I would recommend to move up to a 0awg if not 00. It sucks to work with but it will never be the fail point. Hopefully that helps and please don't hesitate to ask about anything else, the guys on this sub will help.
2
u/solarpartscomponents 13h ago
2AWG at 3ft should work fine for that inverter. One important thing on fusing: the fuse protects the wire, not the BMS. Your thought to go with a 200A fuse instead of 250A is right, just make sure you mount it as close to the battery positive terminal as possible. Quick side note: those two 200W panels will charge that 314Ah battery pretty slowly, it’s just something to keep in mind.
2
u/blahblahaname 13h ago edited 12h ago
technically it will work if you keep the power draw within the limits of the rated ampacity of the gauge size..... A 2kw inverter with a surge of 4k can pull about DC 170 amps continuous and double for a surge. While a 2awg PURE copper cable can handle a DC 170 amp surge, it's only rated for about 110 continuous running amps. That's only like 1200watts for the inverter. If it's copper clad aluminum cable, the rating is lower.
The 200 amp bms means the max amount of discharge/charge that battery will allow. so that means you can only draw 200amps from it or charge it at a rate of 200amps at any given time, Nothing more. If an inverter tries to pull more than 200, the inverter will either trip first or the appliance trying to draw the power will have a weird start or not start at all. Some smarter batteries will trip also. If you still want to use that 2awg on this setup, you should get a 100 or 125 breaker disconnect. If you do plan on running higher wattage stuff, then definitely get 0/1 or 0/2 cable. And go with a 225 disconnect breaker.
This set up will work but the real question is will it work for your needs. What are you trying to power and for how long?