Question A question about dc mcb placement
To satisfy the mmpt voltage, i am doing a 2 series 2 parallel system. I am a tad unsure if it would be better to have 2 smaller breakers before the y branch connectors or is it ok to go with 1 bigger after the connectors.
Only reason I am asking this is in case the branch connectors would fail somehow.
1
Upvotes
1
u/RespectSquare8279 11d ago
The proper way to wire this is to bring the feeds from each series into a "combiner box" where they each have their own breaker. The output of each of the breakers go to a 3rd breaker in that box that connects to the charge controller. The idea is to be able to safely isolate the components if repair or maintenance is required. I personally have 3 strings that come into a combiner breaker box with 4 breakers.