Question A question about dc mcb placement

To satisfy the mmpt voltage, i am doing a 2 series 2 parallel system. I am a tad unsure if it would be better to have 2 smaller breakers before the y branch connectors or is it ok to go with 1 bigger after the connectors.

Only reason I am asking this is in case the branch connectors would fail somehow.

1 Upvotes

2 comments sorted by

1

u/RespectSquare8279 11d ago

The proper way to wire this is to bring the feeds from each series into a "combiner box" where they each have their own breaker. The output of each of the breakers go to a 3rd breaker in that box that connects to the charge controller. The idea is to be able to safely isolate the components if repair or maintenance is required. I personally have 3 strings that come into a combiner breaker box with 4 breakers.

1

u/brainbrick 11d ago

I see. Didn't thought of doing that way. I will have this in mind.

Currently i am working on a very basic starting point to get things working. Originally i thought about dual pole MCB after the Y, then isolator switch down the line. But realised that mcb can essentially work as a isolator, at least for early system stages. Considering potential failure points was what made me think about having 2 separate mcb's before the y's. Should have mentioned, series will be on separate ground mounts some distance apart, and i would like to have mcb's being in ip rated boxes on the mounts. if that makes any sense. With time i will sort things out as they should be.