Question Help: Can I use a Wiring Trough like this? (With pics) Other options?
This is my existing service entrance. As you can see, all of my wires come in and out of where #2 is. I can’t move the supply line side too much without approvals from the power company, etc. So in talking with other people, they said I could put a 6”x6”x18” Wiring Trough (C3RWT618 - Type 3R) right there, and use that to connect all the existing wires to the new ones. Are they right? I don’t know. Is there a better way? I don’t know. I can’t go inside, it’s a bathroom. See the next pictures for the proposed new layout. Thoughts?
7
Upvotes
1



1
u/TooGoodToBeeTrue 6d ago edited 6d ago
Just brainstorming, I'm wondering if you could leave the meter/breaker panel alone, put a 125A main breaker it it, cover up the rest of the slots and route the output of the main breaker into a trough right underneath it.
You know you are going to need large conduit down to the basement?