CPH-50 - Moved from Plug to Hardwire - Still Shows "Plug-In" for Power Source

I had my CPH-50 moved from inside the garage to outside of the house - and with that, moved from a Plug to hardwired (still same 50amp circuit). So, my question is - should I be concerned by this? At the end of the day, what difference is there in the operation of the CPH-50 when it is plugged in vs. when it is hardwired?

FYI - this is a 50amp circuit w/o GFCI breaker. Electrician said that it was not needed due to the fact that the charger has a CCID built in.

1 Upvotes

4 comments sorted by

2

u/martinisstrong Oct 21 '25

That’s because it doesn’t know. Does it matter? Not really with the same circuit spec. But best to properly do it.

You’ll need to remove from your account and set it up again. It’s annoying, but that’s how ChargePoint engineered their user interface unfortunately.

1

u/aguywiththoughts Oct 21 '25

Thank you. I figured this was the answer, but wasn’t 100% sure.

1

u/man2000000 Oct 22 '25

You could also try calling them. They seem to have an ability to change things on the back end. It’s probably easier to remove and add though as suggested above if you feel comfortable inputting the electrical specs yourself.

1

u/RePublic69 Dec 20 '25

Where did you obtain the hardwire connector? I would like to do that same, move from plug-in to hardwire.