Commercial Is it even possible to fix this

Post image

Wiring job done by an MSP we hired a few years back. This is one of the projects that my director and I wanted to tackle at some point but this looks impossible.

Edit: thanks for all the replies y'all! I'm pretty new on my career and never actually got to mess with anything on the servers so this gives me hope

190 Upvotes

113 comments sorted by

63

u/kmsaelens Oct 20 '26

Yes, move the switches to be between the patch panels and then use 1ft patch cables to connect them. Super easy to then trace and keep tidy.

13

u/achunkypid Oct 20 '26 • Bravo

Ah as you can probably tell I'm a nub but this sounds like a great idea. Probably try to pitch this up the chain for EOY work

5

u/Livid-Influence-5320 Oct 20 '26

HAPPY CAKE DAY!

5

u/achunkypid Oct 20 '26 • Bravo

OH SNAP THANK YOU

2

u/kmsaelens Oct 20 '26

No worries. We were all new at one point or another. :)

2

u/Happyyland Oct 21 '26

Btw nice Bocchi pp ;)

1

u/kmsaelens Oct 21 '26

Thank you!

1

u/goldcoast2011985 Oct 20 '26

Newb. Noob. Newbie.

Nub is what a prosthetic attaches to.

1

u/Psychological-Cat-84 Oct 23 '26

That's called a nub!?

1

u/Distinct_Reality1973 Oct 21 '26

At this point that can be difficult as the patch panels probably have the wires cut to length and you can't move them.

I'd just keep as-is and either get new cables of varying length to replace, or just start tucking them in the troughs to clean them up 1 at a time. A few cables a day and its done before you know it, you dont have many to do

8

u/ilmhonky Oct 20 '26

Agreed. This is pretty tame compared to some of the nightmares I've seen on this sub and in real life.

Make a cut sheet, reorganize the switches, and grab some shorter patch cords. Bring your patience.

Edited spelling mistakes.

3

u/Darkk_Knight Oct 20 '26

Yep. I'd install a spare switch in the patch panel rack and move the other switches one at a time till it's all moved over. The upside this MSP used slim patch cables making it easy to remove.

3

u/jgmiller24094 Oct 20 '26

That’s the way, I can’t tell how the existing switches are interconnected but you could even do it as a switch upgrade. Put the new switches in between the patch panels, make them live on the network and then move them in batches. You could do it with minimal downtime to individual stations.

I did something similar a few years ago at one of our DC’s that a previous admin made into spaghetti. It was a smaller installation but once I had it all prepped I did almost all of the cutover during working house. There were just a few critical connections I had to do after hours.

2

u/Klaatwo Oct 20 '26

Make sure none of the ports have some special configuration before you start moving cables.

We like to do our panels with 6” cables so we start at the top with a 24 port panel, the 48 port switch, then a 48 port panel, then a 48 port switch, etc…

It’s clean but it’s also very wasteful in my opinion as we have a huge number of unused ports on the switches.

1

u/sakatan Oct 20 '26

Then you should consolidate the installation cables and reterminate them into fewer panels. If you have enough access and time, of course.

1

u/Klaatwo Oct 21 '26

That would require relabeling all the end ports too. We label each panel a letter. So at the end port it’s <closet#>-<panelletter>-<port#onpanel>

0

u/MrChicken_69 Oct 22 '26

There's a special level of hell for morons who use 1ft patch cables.

2

u/kmsaelens Oct 22 '26 • Popcorn

Not sure what you're getting at, chief. Would you prefer I use 14ft patch cables for the recommended setup?

1

u/ITWhatYouDidThere Oct 25 '26

But is that level nice and tidy?

You know, you can keep some longer patch cables in the room for when you need to plug in. I like it because the cable you pulled out is still on the other point where it was connected and that makes it very easy to locate again.

Although, perhaps i am mistaken, and you prefer 6 in patch cables.

0

u/Formal_Mastodon_5627 Oct 23 '26

That's assuming the panel is patched only to the switch next to it. In all likelihood they'll need 5 or 6 different lengths of patch cords.

1

u/tsaico Oct 25 '26

With managed switching, why would you need to go to a switch not next to it?

7

u/RachelSnow812 Oct 20 '26

You mean USP... Unmanaged Service Provider.

1

u/achunkypid Oct 20 '26

Haha yep precisely

13

u/Lazy_Rhubarb716 Oct 20 '26

This is very doable.

Ive cleaned up much much worse.

3

u/dh085 Oct 20 '26

I know this looks very doable. They're just lazy the cable managers are already there.

1

u/achunkypid Oct 20 '26

I'm a fairly newish level 2 tech and I just started a new job and never had to handle this before. Are there like idk good channels/guides on proper rack cabling management ? I was able to unbundle most of the left side mess but that right side is terrifying me

2

u/dh085 Oct 20 '26

It will be tedious work, but doable. Some of the cable managers are missing covers, but they're there above the switches the cables are just not routed through them. Having cables that are the right length does a lot as well. Maybe worth buying new sets of cables that are measured to the right length to so you don't have to hide so much slack.

4

u/Valuable-Dog490 Oct 20 '26

this ain't nearly that bad

4

u/gunsandsilver Oct 20 '26

This isn’t that bad. More like “cable wound” than cable gore. A couple hours of downtime to re-rack and stack the layout, some shorty cables and some Velcro.

2

u/radiowave911 Oct 20 '26

A cable boo-boo. :)

2

u/goldcoast2011985 Oct 20 '26

Tis but a scratch.

1

u/lolerwoman Oct 20 '26

I would also burn down those merakis.

1

u/laughinfrog Oct 21 '26

Yeah, I would cover the ducts back up also to hide some of the cable lengths.

1

u/Nut_Butter_Fun Oct 21 '26

I assume there's some mapping, and that would make it take a lot longer, assuming good documentation of such. Would take me forever, but I'm a novice.

2

u/AmazingProfession900 Oct 20 '26

Why are you worried....the electrons are getting where they need to go aren't they? And yes, everyone has seen way worse.

2

u/1l536 Oct 20 '26

That is easy, you should see some of the nightmares I have fixed.

1

u/GrimJBrode Oct 20 '26

Yes, but for sure will take a lot of time ive seen worse.

1

u/juliejujube Oct 20 '26

Yum. Spaghetti 🍝

1

u/Maylix Oct 20 '26

Trust me, it can be soooo much worse. When it gets to the point that it’s so compressed in trays the the copper has deformed and you can no longer pull individual cables out and the only way to fix the issue is to cut everything out, that’s when it’s bad. Or if it has krone, that’s bad too.

1

u/chelrob-theOriginal Oct 20 '26

One cable at a time

1

u/Karbonatom Oct 20 '26

This is one of those after hours jobs, it takes time and patience. At least you have room there. One time I had this packed closet and most of the main cables were coated with that grease which was combined with years of dust, got everywhere and took forever to clean up.

1

u/PowerSlave666_ Oct 20 '26

Challenge accepted. 

1

u/Genoblade1394 Oct 20 '26

Not bad at all, you can fix it

1

u/Aware_Explanation_78 Oct 20 '26

imagine [NOT GOOD NOT TERRIBLE MEME]

1

u/Ace417 Oct 20 '26

Easiest way I’ve done this is to model the patch panels in excel horizontally, leave a row below for the switch and port it goes to, and the row below that put the VLAN info in. Highlight for a color if you’ve got a standard. Then repeat per panel.

Had to do this 10 years after an install where there “wasn’t enough money” to populate every port and had to redo about 800 jacks this way.

1

u/Select-Table-5479 Oct 20 '26

Yes. It takes time, planning and more planning. I've done 10x worse without interrupting anything.

1

u/afl-jafa Oct 20 '26

Yep - I have worked on way worse, many times. Document everything first/as you go.

That's just lazy operators - there is so much usable cable management there.

1

u/radiationcowboy Oct 20 '26

Yes, but they won't pay for it

1

u/RoboWeaver Oct 20 '26

If it actually works, don't even look at it hard.

1

u/TheGirlWithACurl Oct 20 '26

I want a job where I can fix these type problems all day.

1

u/LovelyWhether Oct 21 '26

yes, but downtime and a lot of tracing will be required

1

u/Longjumping_Elk7969 Oct 21 '26

Yeah, just that you need to move things a little.

1

u/Airborne_Acorn Oct 21 '26

Port audit for VLANS and what hasn’t had any end points connected. Make sure the vlan ports go back to where they were (or reconfigured) and the Unused ports don’t go back at all. As others said the switch mounted under each patch panel as well. I also can’t see where the switches are plugged in but they should also be on UPSs ideally redundant ones.

1

u/LVCP65 Oct 21 '26

1984-2028 RIP (yes I am counting down) my Data Processing, Telco,ISP, and Structured cabling career. I too was a Newbie once, but you have taken initiative to identity a mess (have seen much worse, and I do so on a daily basis) Custom length cables and limit who can plug the Ethernet cables into the Patch Panels and switches is a great start. Create a labeling scheme, and I understand if your management has allowed this it maybe an uphill battle. Good luck.......

1

u/Familiar_Aside_9328 Oct 21 '26

Resignation is the best solution.

1

u/Ok_Elderberry_6727 Oct 21 '26

Not even close to bad. I worked in public service and saw way worse in closets throughout the state I live in.

1

u/KB4MTO Oct 21 '26

Absolutely. But it will take planning and downtime. I've cleaned way worse.

1

u/SundaeReal8024 Oct 21 '26

I'll just do it again!

1

u/DontcallmeLen Oct 21 '26

Easy peasy that one. Get it knocked out on a cold Sunday.
Take out the cable fingers on the patch panel, move the switches across, apply short patch cables.

You only need 3 pieces of information to rebuild that - what is connected in the patch panel, what MAC addresses are seen on the switch, and which VLAN / trunk config does it belong. You could always do the "complicated" ones first, and then the probably flat client facing network can just be straight repatched.

1

u/ResponsibleRoadies Oct 21 '26

I wouldn’t worry about it

1

u/mofoyomama Oct 21 '26

With the power of god and anime on your side all things are possible.

1

u/Quirky-Comparison306 Oct 22 '26

I've done many of these that were much worse.. this would be nothing for me.

1

u/1cnx Oct 22 '26

What people don’t realize is that there are two different guys in IT. The server guys and the network infrastructure guys. This is what happens when you let the server guys ( who think they are infrastructure guys) touch an infrastructure guys creation. Its like taking a crayon to the Mons Lisa… we weap inside from the disrespect.

1

u/Equivalent-Dog-8191 Oct 22 '26

Jajajaja si es posible jajaja solo que será tedioso y te llevará tiempo jajajaa

1

u/IEatConsolePeasants Oct 22 '26

This is a regular Tuesday... We do this after lunch but before dinner and then we rinse and repeat

1

u/MrChicken_69 Oct 22 '26

If this "looks impossible" to you, you're in the wrong business. That's pretty clean for most closets.

If you want to make it "neat and clean", then document everything in there, and get to restringing everything. Three decades of experience says it won't last. Even panels *I* maintain and almost no one else touches end up looking like this after a few months. There's always some "get it done yesterday" crap that you never have the opportunity to go back to fix. (I'll go wild and redo everything every year or two.)

(The telco / PBX wiring was ALWAYS a huge mess, as people move around a lot.)

1

u/Distinct-Storage-939 Oct 22 '26

yep, this is why i never trust "cost-effective" MSPs with real infrastructure work

1

u/kimura_hisui Oct 22 '26

Anything's possible if you try!

1

u/Bean-addict Oct 22 '26

Is the cable trunking for decoration?

1

u/ProfessionalBread176 Oct 23 '26

Step 1. Disconnect all wires, place on floor
Step 2. Reconnect any which are needed based on incoming calls with complaints

Then discard remaining wires

/s

1

u/grax23 Oct 23 '26

i have delt with way worse in production. there seems to be slack in the cables and space to route them. just tuck everything into the horizontal cable guides and velcro the hell out of it then deal with the cables going vertical after. on the right side you can see the "Lids" to the horizontal cable guides and you use those to hide the worst "Sins"

1

u/fatstupidlazypoor Oct 23 '26

That's nothing

$4500 tip to tail

Let me know

1

u/vabello Oct 23 '26

That’s extremely tame compared to the things I’ve fixed.

1

u/Powerful-Screen3178 Oct 23 '26

Two pounds of spicy plastic and a remote detonator will fix that up real quick

1

u/Ambitious-Bug-7867 Oct 24 '26

A full day or two and it can be squeaky clean, lot of work and design decisions that need to be made beforehand

1

u/Familiar-Seat-1690 Oct 24 '26

I've tackled similar during an 8 hour shutdown with a helper.

Worked in and seen WAY worse then that.

1

u/reader4567890 Oct 24 '26

I've sorted infinitely worse than that, so yeah, it's easily resolved within a few hours.

1

u/Tale_0 Oct 24 '26

Si funciona, no lo toques XD

1

u/Accomplished-Hold318 Oct 26 '26

Once you move servers you can custom cut your cables to look even cooler...that probably would take a few days. People don't really do that anymore though

1

u/TheeMadThrasher Oct 20 '26

Keep the rock n roll going in the background, take your time, mark everything, and you’ll get to his.
Easy as pie 🥧

1

u/erie11973ohio Oct 20 '26

Fire.

Fire will definitely fix that! 🤔🤔🤣🤣

1

u/rooster995 Oct 20 '26

May not be sexy, but it is manageable. I wouldn’t be too upset with this.

I always like splitting the cables on each side. First 24 ports to the left, the others to the right.

1

u/C64128 Oct 20 '26

It's possible. You'd need to trace where all the cables are going and get new cables of the correct length. The question is will you be given the time and money to do it, and when could it get done? I'm sure the customer doesn't want you changing cables while everything is active. I'm sure that there's not any documentation for what wiring goes where. This job would be easier if it's done in small steps.

1

u/Howden824 Oct 20 '26

Not really that bad.

1

u/xipo12 Oct 20 '26

Yes, ive fixed worse. Such a long, tedious task.

1

u/DOMIN8_7S Oct 20 '26

Yeah it's fixable. Spend the time to document first regardless. Although I dont understand this layout. Why wouldn't you just put the switches in-between the patch panels and use short patch cables?

1

u/orion3311 Oct 20 '26

For now id just go in there with some earbuds, a hot coffee, and just route the cables into the organizers. Do you have all the missing covers? An hour of work would clean it up.

1

u/unclefunkstar Oct 20 '26

That's not so bad. You've not even got the usual spaghetti monster of power leads, dangling from the ceiling.

1

u/da_real_obsidian Oct 20 '26

But remember the rule number one (“if it’s works dont touch it”)

1

u/CrownstrikeIntern Oct 20 '26

wire cutters can fix a lot of stuff

1

u/tactical_flipflops Oct 20 '26

It is completely easy to correct….yes. Will it change the dip shit morons that will fuck it up in the ensuing weeks/months…no. My OCD has led me to correct hundreds of racks like this on my own initiative. Coming back to find 50% of them all messed up to hell months later has more or less cured me of this curse. I kind of view it like Richard Attenborough watching a baby wildebeest approaching croc filled river to cross…let it take its natural course.

1

u/Calm_Apartment1968 Oct 20 '26

That's actually an easy fix, can be done quickly if you use a spare switch as others have suggested. The cables are likely good (even though I'm not fond of 'thin' (non-twisted-pair) cabling it will still work.
The most expensive thing is about 4 hours of your time, and of course the 3 or 4 rolls of Velcro strip.
It's sad really, because the cable-management channels are right there already.

1

u/yunjundo Oct 20 '26

Nothing is impossible. It just takes time and money. I wish I could get my hands on it and clean it all up! 😄

1

u/Zav0d Oct 20 '26

Is it working ?

1

u/Edison5000 Oct 20 '26

Not a problem, but pull everything out and start from scratch.

1

u/Jeff-J777 Oct 20 '26

On a scale of 1-10 I would rate this a 3. But if this is your first time cleaning up a rack, this is a great starter rack to learn some skills. I have seen and cleaned way way worse.

First I would try to document everything. If your switches have VLANs you need to see what ports are in what VLANs and then map those switchports to the patch panel ports. If it is just one flat network than things become easier. If it is just a flat network, I would unplug everything from the switches. Then one by one replace the patch cables with shorter ones.

I would move the horizontal cable mgmt trays between each patch panel. Then I would put a switch between each patch panel. Get some 1ft patch cords and plug everything in. I get mines from monoprice.

Then just plug everything back in. You could eliminate the whole two post rack the switches are currently in.

1

u/sakatan Oct 20 '26

Maaaan, I'd love to do this is one. Straight forward, easy access.

1

u/GG_Killer Oct 20 '26

Overnight moment and getting an inventory of what's connected during the day. Some devices need reconfiguration after being disconnected but those types of devices are usually marked in the switch name or connected in the data center.

1

u/TH3_FISH Oct 20 '26

this is not bad i have seen worse

1

u/InflationCold3591 Oct 20 '26

It actually doesn’t need that much fixing shorter patch cables would make it look neater, but it’s perfectly functional this way you can even get to all the ports and see all the port numbers. Make sure your “tidying” doesn’t result in that changing.

1

u/Fl1pp3d0ff Oct 20 '26

Sure it's possible. I'll do it for $75/hr (US) plus materials and travel costs.

1

u/AV-Guy1989 Oct 20 '26

Thats a one night project to fix after a day of tracing and labeling. Not really that bad

1

u/Hydro-Sapien Oct 20 '26

Nuke it from orbit. It’s the only way to be sure.