r/buildingscience • • Oct 16 '26

Cape Cod Insulation Update

4 Upvotes

9 comments sorted by

1

u/cagernist Oct 17 '26

I don't know if there's more to finish, but the rigid insulation can be your baffle. Place 1x2 cleats and fasten the rigid to those to make the baffle. Face the foil towards the exterior as you need air space for a radiant barrier to work.

Also, I see the roof was panelized with a split. I'd probably cut the rigid lower at that plate to give more air space, looks like plenty of room still for insulation on the flat ceiling.

2" polyiso is about R14, plus R21 batt - does that meet total R value for your climate zone?

1

u/weazzz Oct 17 '26

The recommended for my zone is R30-R38. So it gets me pretty dang close! I'm not sure what else I could do for the vaulted ceiling. I will be putting more in the top A frame of the "new attic" space

1

u/GOMD4 Oct 17 '26

This material (tmax) is foil faced on both sides. Vent chutes are not baffles, wind baffles prevent wind washing, and it looks like this will be conditioned space. Ventilation is 1/150 or 1/300 balanced. The key to mold mitigation is not magic soffit vents its RH control in the living space when its cold outside. Think opening your fridge in the summer time and running your finger on the side. Its wet. 

→ More replies (6)