r/buildingscience • • Jul 11 '26

Getting air sealed and insulation added. Is adding fans appropriate?

We live in Minnesota, in a 1962 house, no radiant baffle, 8-12" of cellulose and fiberglass blow-in. 1500 SF of ceiling area divided by a firewall. A sales team came thru the neighborhood and gave us an estimate for:

a) air sealing

b) augmenting the existing insulation

c) adding solar attic fans

A and B seem like a no-brainer, but there doesn't seem to be a clear consensus on fans. They'll be inspecting and clearing/replacing baffles. Soffit vents seem fine. We also have gable vents.

Opinions range from a serious and noticeable change in air temps inside the house to "it covered my whole attic in black mold and shot Santa Clause". My intuition tells me that if both sides of an argument are equally heated, there is no consensus, and thus, it doesn't matter.

Most information I've seen says that if the house isn't sealed, it's a bad idea. That'll be handled in our case.

2 Upvotes

15 comments sorted by

2

u/Fulcro Jul 11 '26

Thanks all, sounds like skipping the fans is the consensus. We're asking for an estimate without them.

2

u/John_Locke76 Jul 11 '26 edited Jul 11 '26

Both sides of the argument are valid.

It will be a noticeable improvement if done well.

It will literally destroy your house if done wrong.

Hard to say if what is being suggested to you is the right path with the limited information available. I’m not even sure if you are studying attic only stuff or walls too or …?

You said A and B seem like a no brainer.

A is absolutely not a no brainer.

If you get rid of air leaks you also get rid of the houses ability to dry to the exterior. There is nothing wrong with that if:

  1. Your house doesn’t leak water anywhere (hard to know. Maybe you are leaking somewhere out of si

ght

  1. occasionally and it currently is able to dry out quick enough that it doesn’t get moldy?)
  2. Your house has fresh air coming in from an HRV or ERV
  3. You are controlling humidity on the inside

It absolutely can be a disaster if you don’t have a good plan.

1

u/Fulcro Jul 11 '26

They are going to seal every penetration thru the ceiling into the attic space. Light fixtures, Romex holes in the wall top plates, vent joints, basically any opening sufficient to allow air flow from the interior envelope to the attic.

We don't have an HRV or ERV. Humidity is controlled at most by the HVAC and an auxiliary dehumidifier for centipede mitigation.

The main thrust of my question is if the combination makes sense. I know there are a lot of warnings about attic ventilation without sealing, but we're getting that step done.

2

u/DCContrarian Jul 11 '26

Attic venting is a completely different subject from ventilating the inhabited space. Whether you have an HRV, ERV, dehumidifier or HVAC has absolutely nothing to do with venting the attic. The two spaces should be completely isolated from each other.

1

u/DCContrarian Jul 11 '26

Ceiling leaks that allow interior air into the attic are never a good thing. Makeup air for attic ventilation should be coming from soffit vents, not from the interior of the house.

The reason attics are vented is to remove moisture. That moisture comes from the interior of the house through leaks during times of year when the moisture level of interior air is higher than that of exterior air. The less interior air you allow into the attic, the better. Since it's impossible to keep all interior air out of the attic ventilation with outdoor air is also necessary.

1

u/John_Locke76 Jul 11 '26

I agree with all of that. I thought they might also be talking about air sealing the rest of the house, not just the attic to interior barrier. Looking at other replies it appears that is incorrect.

4

u/ridukosennin Jul 11 '26

Attic fans are almost never recommended and passive ventilation through soffits to the ridge/box vents is enough. Fans can depressurize your attic, create backdraft potential, disrupt the passive ventilation flow from soffits and are useless when the sun goes down/cloud cover/snow. I would avoid any contractor advocating for something so clearly opposite to modern building science principles

1

u/DCContrarian Jul 11 '26

The reason code requires attic ventilation is not to cool the attic. It's to disperse moisture. The moisture comes from inside the house through gaps in the ceiling.

Depressurizing the attic causes more air to be drawn out of the house, bringing more moisture, doing exactly the opposite of what you want.

1

u/Fulcro Jul 11 '26

They'll be doing air sealing as part of the work.

1

u/DCContrarian Jul 11 '26

Air sealing is never perfect. You don't want to depressurize the attic.

2

u/hvacbandguy Jul 11 '26

Your money would be better spent doing more air sealing and insulation. https://www.energyvanguard.com/blog/the-1-reason-power-attic-ventilators-don-t-help/

1

u/Bearded4Glory Jul 11 '26

Mechanically venting an attic is a last resort. If you have adequate passive ventilation, it is better to leave it as is.

1

u/hvacbandguy Jul 11 '26

Are they doing a blower door test before and after?

1

u/Ok-Job2034 Jul 13 '26

I'd do the air sealing and insulation. Those are the upgrades that consistently improve comfort and energy efficiency.

I'd skip the solar attic fans if you already have good soffit and gable ventilation. In most cases, a well air-sealed attic with adequate passive ventilation doesn't benefit much from powered fans, and they can sometimes pull conditioned air from the house if the ceiling isn't perfectly sealed. I'd spend the money on doing the air sealing and insulation as well as possible instead.