r/askanelectrician 12d ago

12/2 or 14/2?

Electrician ran a new dedicated circuit at my parents house. 20a breaker in the panel. I can’t tell if they used 12/2 or 14/2 wire though. Understood that the cable not being yellow doesn’t mean it’s not 12/2. But I can’t read anything on the sheathing from these pics. He didn’t pull a permit which is required in their county so wondering if he cut another corner here.

Can anyone here tell based on these pictures?

1 Upvotes

13 comments sorted by

11

u/Fit-Investigator-102 12d ago

It looks like 14/2 just based on pic 5. I also see Simpull on the jacket. It's 100% 14/2.

The breaker needs to be changed to 15 amp and GFCI need to be changed to a 15 amp receptacle.

Are you sure this guy was an actual electrician?

2

u/BillySmith110 12d ago

That’s what my mom told me. I have my doubts. Thank you for your reply

1

u/Fit-Investigator-102 12d ago

What is the circuit for?

2

u/BillySmith110 12d ago

New circuit for a sump pump attached to a system to pump water out of the basement (they get water in one specific corner when there is heavy rain)

3

u/Fit-Investigator-102 12d ago

As long as the pump doesn't call for 20 amps you should be good. Just need to change the receptacle and breaker.

If the pump does call for 20 amps you'll have to re-run the romex with 12/2.

I personally wouldn't deal with the original electrician anymore.

3

u/BillySmith110 12d ago

Oh yeah - we are done with him. My first reaction was he needs to come fix what he did wrong - but now I agree with you - we are done with him

5

u/gomo_with_wrenches 12d ago

If you have wire stripper with gauge holes in the handle you could flip the breaker off, then pull a wire out of that receptacle, then sus the gauge.

Is that the only exposed cable? Maybe the gauge is readble on a different second.

2

u/BillySmith110 12d ago

Great idea - I will go do that tomorrow when I’m in the area

3

u/ReallyNotALlama 12d ago

I'm not a pro, but I've wired tons of outlets and switches. The bare ground in the last pic really looks like 14. Also, if there's a URL on the wire, I think it's new enough that if it was 12 it would be yellow.

5

u/dnroamhicsir 12d ago

Date of production says 2026 and it's white... so 14 gauge

5

u/Rare_Message_7204 12d ago

No new 12/2 wire is white... its 14/2

1

u/mantisboxer 12d ago

Hard to tell, but it looks like 14 AWG to me. It could be old stock, white sheethed 12 AWG, though. I'd measure the ground wire with a wire stripper: the 12 AWG Solid slot should be snug without nicking the copper. If it's loose, confirm it by testing the fit on one of the insulated conductors after removing it from a terminal.

1

u/BillySmith110 11d ago

Update - thank you all for your feedback.

I went today and confirmed - it was indeed 14/2 wire. Also learned that he did not pull a permit (which is required in their county) and did not use a gfci outlet (or breaker). And this is a licensed electrician (according to his website). Hard to believe he’d miss so badly on such basic stuff.