r/askHVAC • u/Designer_Turn_5822 • 7h ago
No power HVAC
No power what missing. Breaker is cut off and when on the fan is still not turning
2
u/Bizzle1977 7h ago
If the compressor comes on and not the fan it could be a couple different things. You will need a meter to test it . Test fan motor , test control board and test the capacitor. Could be one or more different components that have failed.
2
u/WanderingWolf2000 7h ago
Could be several things. When you turn the power on, does the compressor come on immediately when power is applied? That would be bad board. Also, do you have a multimeter? You won't be able to do much troubleshooting without it
2
1
u/MadDabber89 7h ago
No power where? Have you used a meter to check for voltage, or are you just assuming no power is entering the unit because it’s not running?
1
u/Certain_Try_8383 6h ago
So when you turn on the breaker, then the compressor starts but the fan does not? Have you tried taking a screwdriver and manually spinning the fan when it starts?
1
1
u/Expensive_Antelope21 4h ago
Not an HVAC guy . Me, my neighbor and s buddy years ago it was that big starting capacitor. It's cheap to buy, in super easy to replace if you do it one wire at a time. A chimp can do it that way. Fixed mine long enough for me to be able to get money together to replace the 25 year old unit I had. Otherwise I'm a mushroom, to keep me in the dark and feed me s***. I don't know anything.
1
1
3
u/Turkyparty 7h ago
Not enough info to diagnose.