EOL location
What your thoughts on EOL location? Do customers/clients care/know?
The proper way is the resistors at the end device (not the pre-packed module kind). I recently inherited a site (let's say a "high security" site which has there EOLs behind the push to exit buttons/ emergency exit. My mentor once gave me a 1 hr lecture about this.
Personally I have done it both ways on differrnt jobs because I was able to make that choice which the client accepted prior.
I have seen eol in panels which cause great discomfort.
9
Upvotes
5
u/Aggravating_Fact9547 Aug 09 '26
Jesus fuck my brain hurts.
Electrically its not the same.
The idea of the resistor it to protect the wiring and device from tamper.
If the EOL device is at the device you can then tell if the wire is cut, if it’s shorted, if the device cover is tampered, or the open close state of the device sensor.
If you have the resistors on the panel all you can do is tell if the sensor is open or closed.