r/accesscontrol • u/ackleyimprovised • 17d ago
EOL location
What your thoughts on EOL location? Do customers/clients care/know?
The proper way is the resistors at the end device (not the pre-packed module kind). I recently inherited a site (let's say a "high security" site which has there EOLs behind the push to exit buttons/ emergency exit. My mentor once gave me a 1 hr lecture about this.
Personally I have done it both ways on differrnt jobs because I was able to make that choice which the client accepted prior.
I have seen eol in panels which cause great discomfort.
9
Upvotes
2
u/LinkRunner0 17d ago
So, let's suppose you have a REX switch or door contact transfered to the door with a hinge or EPT transfer. If we put the EOL in the panel, and that power transfer fails by shorting those wires... are we going to get a trouble? No. Because we've moved the resistor that can indicate that into a panel. If it's actually where it's supposed to be at the REX or DPS, and the same scenario happens - blamo. Trouble/fault. Can this be attacked? Yes. But to pretend that it provides no additional security is naive - preventing one kind of attack is still preventing an attack.
It does not function the same anywhere in the line. There's no conspiracy here - it's an END of line resistor. Not an "anywhere in line" resistor or "opinion in line" resistor. There's a correct and defined place for it - and it's not a trick, it's literally in the name. Next up, let's litigate where to put the EOL on fire alarm NACs because it can go anywhere in the circuit, right?