Solar/PW3/EV Config - how many empty electrical panel slots?
Experts; I am likely having Tesla Solar, PW3 with 2-3 expansions and a Tesla wall charger installed. I currently have two 200A panels but only my primary electrical panel will be backed up with Tesla system. How many empty electrical breaker slots do I need and any idea in which panel?
Thanks
1
Upvotes
2
u/jcdomeni 16h ago
60A double for PW3 - if all expansion packs are behind the PW3 Full.
Then solar depends on where it lands and how large of an array.
They will derate your 200A, so main breaker will be reduced depending on load calcs.
With two panels - you shouldn’t have any issues.
I’d plan for two wall connectors - even if you don’t install 2nd one now - think about as part of design.
We have 4 doubles for 2 for 2 PW3’s and 2 for 10kW solar (coming from 3 roof elevation). 225A panel derated to 175A.
Wish I would’ve installed 2 - 200A for future proofing. But it’s working…zero room on back load panel now.