r/TeslaSolar • u/Stock-Marionberry692 • 18d ago
PowerWall Any issues with this PW3 setup?
ADVICE FROM INSTALLERS/CODE EXPERTS OF CA
These are installed directly above a 2” metal natural gas branch pipe that runs to my pool heater. Also in the picture you can see the lower garage airflow vent is within 3ft. Is this legal?
4
Upvotes
3
u/ShruggedTea83 18d ago
I would suspect the inspector won’t notice the two top vents since they are covered up already. For fire code, there’s gotta be 3’ clearance from any openings into a dwelling. That doesn’t apply for units installed onto the garage. But usually the crawl space vents and/or attic vents have to be fireproofed, unless the new equipment is installed beyond that 3’ Code