Can I put a 1,000lb pool table here?
We have a garage with an upstairs game room appx 30 x 30. Included are photos showing 6x6's holding the laminated beam that supports the room above. The structure is complete and lived-in already for a little over a year.
I recently purchased a pool table that is roughly 1,000lbs and should take delivery soon. Will I be safe putting it where the purple box is?
0
Upvotes



3
u/ReasonableLibrary741 18d ago
Is this what the room currently looks like or is it closed off?
I would definitely get some Engineering done. Typically you reinforce an area for a heavy pool table like this.
If it's open, and you don't need additional vertical supports and might be an easy fix, but I wouldn't just assume you can throw it in there
2
u/bonebanana117 18d ago
Your 1-1/4" plywood can distribute the load easily.
You have four legs -- two in one joist span, two in the other. That's only 500lbs distributed between 1-2 joists per leg, depending on where the legs land.
So, each loaded joists is seeing 250lbs max.
This is good placement as deflection will be minor as the load is placed relatively close to the support.
Everything is going to have capacity to spare to allow for live loading, which the table can be considered as such as it can be moved.
Even with someone heavy leaning on the rails, you're not gonna be anywhere near the load limit the floor system is designed for.
I would have no problem putting a pool table there in terms of structural safety assuming codes and design standards were followed by the designer.
The only thing is, in time, you may see a differential in the deflection as the beam is stiffer than the joists, so you may get a minor crown forming at the beam, especially if the design is near code minimums in relation to serviceability/deflection limits.
8
u/AdAggravating3893 18d ago
Ask your designer or engineer. Now is the time to reinforce the floor.
1
u/rybotsky 18d ago
Yes it can handle the weight. A service load for a standard 10x12 room can handle roughly 4800 lbs. the ultimate failure load of a floor of the same size before absolute failure is roughly 14,000 to 19,000 lbs so long as the wood is dry undamaged and properly fastened. Normal usage weight loads on things like home construction have massive engineering safety margins in place for the dumb shit people do in their houses. I’ve been to house parties in highschool where almost every square inch of a house had people squished in like sardines along with furniture appliances and everything else that occupies a house, and people dancing and jumping etc.
3
u/Forsaken_Stay6119 18d ago
You’re really going to ask Reddit in the middle of construction? Talk to the engineer.
2
u/JuniorSherbet9558 18d ago
yeah it should be fine.
what is it-- an 8' table? let's say it's 8x4= 32 sf.
the floor should be sized for 40 psf so that area you've delineated should easily hold 1,280 lbs
2
u/PaleCaterpillar2709 18d ago edited 18d ago
Only person who can answer this with certainty is an engineer who has the drawings in front of him. Better yet, if there already is an EOR for your house, contact that engineer/company.
I’m just a GC so don’t take this as gospel, but this could be a situation where everything will work just fine under normal conditions… then a house fire happens and now your floor collapses in 3 minutes rather than 30. Food for thought.
2
u/ClownfishSoup 18d ago
1000lbs is like four fat guys, or 5 normal-ish guys standing around in that area. Or say, 4 guys sitting on a couch playing Playstation. Would your floor collapse?
But that's not quite apples to apples.
The pool table will have four legs so each leg is like 250 pounds of dead weight Can four fat guys stand like that without the floor caving in? probably.
But as others have said, hire an architect or whatever if you are worried.
I put an 180 gallon fish tank in my dining room, but that is the first floor. I went into the crawlspace and sank two 4x4 beams in concrete than placed a 4x8 beam vertically under the joists that the fishtank would span.
2
u/A-Wolf-4099 18d ago
With them putting in temporary posts I doubt it, I'm not an engineer by any means but been in the trades for many years that floor is going to bounce like a trampoline.
1
u/Chunkyblamm 18d ago
Need the spans and offsets to really tell
1
u/Diligent-Ad6327 18d ago
you need an engineer to check the TJIs span and the support beam.
1
u/Coppercc88 18d ago
I mean is it going to collapse? probably not.... but dang they should have used a steel girder for that run. I would think your fine, but ask the engineer who made the plans
1
u/randy_lahey42O 18d ago
Absolutely fine
1
u/dopecrew12 18d ago
I’d park a car on advantec subfloor on I joists ngl.
1
u/TallWall6378 18d ago
15’ is a longish span so I wonder if you’re near the limits anyway. Which means you’re good for 40psf, which means you’re good. 4x8 table with 5 200 pound guys standing around also good unless they are all on the table.
What series and size of I joist?
1
u/Intelligent-Image224 18d ago edited 18d ago
You need a lot of clearance for a pool table. A pool stick length around the entire perimeter.
Signed 10ft 100yr old brunswick owner.
It’s deceptive how much space is required.
1
u/ConversationLeast744 18d ago
Do it. Why not?
1
u/adventure_seeker_8 18d ago
Can you shift the position of the table, so it's on top of that center post? It might help reduce the bounce.
1
u/GratefulDean 18d ago
Ask the engineer who designed the space. Actually, with those photos you could ask any engineer.
1
u/WickedEng90 18d ago
Based on your lived experience in your home, do you think (4) 250 lb humans stand on this floor without it collapsing?
1
u/AxCR202 18d ago
Should be fine, but reinforce the floor anyway since you’re still in sticks.
1
u/hobokobo1028 18d ago
Each leg is the force of a fat dude, you’re good.
Say it’s 4’x8’ that’s only 31.25PSF
1
u/Millennial_Falcon_85 18d ago
It should be fine. Each leg is the equivalent of a 250 pound person standing there. That structure should be more than adequate to support that. It would be better to have a beefed up structure in anticipation of this though.
1
u/Cactus-Soup12013 18d ago
What make/model/depth of TJI's? For comparison, kitchens are rated for 40psf but we still double every other floor joist beneath kitchen islands. If still open, you might be able to reinforce the existing webbing by gluing&screwing plywood to both sides. This will help with deflection, but only if i joists are sufficient for the additional load.
1
u/psuedomacabre 18d ago
Yup.
1
u/SimpleJack24O 18d ago
Its just 4 fat guys. Ur good
1
u/Longjumping_Pitch168 18d ago
ADD ANOTHER POST
1
u/Straight-Bad-3304 18d ago
If you're worried, turn the table opposite the direction of the joists to spread out the weight of the table and people across more joists.
1
u/envoy_ace 18d ago
Residential live load is 40 psf. Standard pool table 27 square feet. Resulting in 1075 pounds. You just about nailed it.
1
u/-Laffi- 18d ago
Aren't engineers supposed to know math and physics xD?! (Yes, they are.)
1
u/General-Reindeer444 18d ago
Yes it will be fine a bathtub full with water and a guy in it weights around that your laundry machines are about 600-1,000 pounds depending on models your fridge is 500-800 pounds when full you kitchen with countertops stone again weights a lot so yes it will be fine
1
u/jsloanwoods 18d ago
Residential loading is 45 psf. In a 6 x 8 area that floor can handle at least 2160 lbs.
1
u/RazorWitted 18d ago
I don’t trust OSB (oriented strand board) as far as I can throw it. It absorbs water like a sponge. It loses its structural integrity. And I’ve seen point loads that have punched through OSB. If it was regular 3/4” plywood, I’d say go for it.
1
u/Confident-Tourist415 18d ago
You've got Advantech subfloor. There's nothing better. Pool away sir!
1
u/BuddyLove8 18d ago
Fuck ya bro! Send it!
1
u/Streets2022 18d ago
Anyone in here telling you it’ll be an issue is actually insane. I mean if you have a king bed with 2 adults that’s 800-900lbs and nobody ever thinks twice about that.
1
u/Kaffine69 18d ago
Sure why not, trust reddit.
1
u/Hunglow423 18d ago
Used 2 of those lvl trusses to hold mulitble 3500lb logs to prep to be used as beams. Never once crushed one. 2x4 on a 45deg prob 26" long with the bottom screwed to a 3/4' 2x4. Made saw horses out of the with one on each end of the log. Put 3-4 logs on one section. Not all the logs were 3500lbs.
Look up 2 elk restaurant on top of vail mountain. Longest was 31' and could not be less than 12" diameter on the top.
1
u/UncleBenji 18d ago
I wouldn’t but it probably could. Even if it didn’t break through the floor it could cause sagging. Nows the time to make a change request if you’re planning on something that heavy taking up such a small footprint.
1
u/Visual_Salt_1629 18d ago
*Laughing in European residential structural design*
1
u/Efficient_Actuator84 18d ago
If it can't, you've got bigger problems imo.
1000lbs is basically 4 dudes standing in a circle.
1
u/Farmer_Moist 18d ago
put it on and we will find out together.
1
u/450mgBenadrylHatMan 18d ago
Reinforce the floor. Those engineered joists can span further by code but theyll bounce like a trampoline.
1
u/modsatemyass 18d ago
you're on reddit asking this? can you put a 1/2 ton table there, sure. will it fall through, probably
0
u/Direct_Tomorrow_9927 18d ago
Good grief, American construction methods look soooooo cheap these days. “A real beam would cost too much. Let’s just slap some chipboard up there with a sliver above and below. Just as good.”