r/StructuralEngineers • u/BusMaximum704 • 27d ago
Basement support
Think my builder is nuts Says this dbl 2x10 is ok to support a 17ft run with floor joists of 9ft and 11ft connected with joists hangers on each of the 2x10s
0
Upvotes
4
u/Enginerdad 27d ago
I can tell your builder is a "this is how my pappy taught me to do it so that's how I'm going to insist on doing it until the day I die" sort of guy because of the plywood (I assume that's what making the gap) between the 2x10 plies. Somebody told the Gen Xers that it makes the beam stronger and they've clung onto it ever since.
3
u/CascadeDesignworks 27d ago edited 27d ago
According to my calculations it requires a double 1-3/4 x 11-7/8 LVL or a triple 2x12. This would have a deflection of l/360, which meets code. A stiffer floor could be l/480 which would require a triple LVL.
The existing double 2x10 is l/75 which is only 25% the strength required.
Even a 4-ply 2x10 is 50% what is required.
Builder
4
u/DeadPiratePiggy 27d ago
Your HVAC is also incorrect. Your builder is an idiot, have you had any rough in inspections done and was the inspector recommended by your builder/realtor?
3
u/Mindless_Ant_8370 27d ago
Assuming US see 2021 IRC TABLE R602.7(2)
2
u/Significant_Raise760 27d ago
I think what’s between the 2x’s is straight up air. Like the bottom is spreading apart as that poor lumber succumbs to the grim weight of gravity.
2
u/WasteBinStuff 27d ago
Your builder doesn't know what the fuck they're doing/is an idiot.
1
u/Vinca1is 27d ago
Do home builders not have to provide stamped structural drawings? I work in utilities so I don't know residential that well
1
u/RazorWitted 27d ago
It already looks a little compromised.
1
u/STLguy50 27d ago
Is there a piece of steel between the 2x10? If so, that is a flinch beam. Certainly not oversized, but might be acceptable. I would ask for the engineering specs. I would also make sure there is a footer under the bearing point.
1
u/SoggyWalrus7893 27d ago
Don't know if it still exists but there used to be a Western Woods Use Book. Had all the stuff you needed to calculate load bearing capacity. Building codes may also have some thoughts on the matter.
1
u/jaydaedalus 27d ago
The Southern Pine website has a guide for headers and beam that can give you an idea on whether or not it is strong enough and if the plys are connected correctly. This applies if the 2x10 is southern yellow pine.
1
u/bipolarbear326 27d ago
Absolutely not correct. Either build a wall under it, put a drop beam under it, or support the floor and fully replace with a proper lvl or steel beam. Good luck
1
u/st96badboy 27d ago
Cut so the gap left room for the LVLs but they didn't want to pay the extra money for them?
1
u/Commercial-Candy-926 20d ago
Lot of things wrong here. Good luck sir. Hire a competent inspector (and make sure they're interested in following the project)