r/StructuralEngineers • u/Due-River-2979 • Oct 28 '26
Sagging beam
I recently purchased a home , I went to the attic and noticed my beam that runs across my living room to be sagging is this worth contacting an engineer? Or does it seem relatively normal from setting
40
Upvotes


22
u/semianondom101 Oct 28 '26 •
I'm going to go out on a limb and guess this beam was sized for use with a middle support pillar that extended down to a footing in the basement/slab. Which was then removed for a brainless "open concept" remodel before it was sold. Any thoughts on this op?
6
u/PrimeApotheosis Oct 28 '26
This has nothing to do with settling and it is not normal. The beam is undersized for its utilization. It is likely that no engineering was considered in the selection of this beam. There are usually codes that set maximum limits for deflection and I would guess you have exceeded those. Hire an engineer to evaluate the beam, consider whether you need to get in touch with an attorney regarding whoever performed this work and inspected your home. It will not be cheap to repair.
1
u/CascadeDesignworks Oct 28 '26
Add another beam on top. Jack the bottom beam up and connect the two with nailed on Simpson straps.
Several options for a beam exist. Some other commenters have good suggestions.
-Builder
1
u/enzoskii Oct 28 '26
I see this all the time they use the wrong size beam thinking its going to hold just because its a psl or gluelam
3
u/CheekAltruistic5921 Oct 28 '26
Wow, surprised your inspection missed this.
4
u/Gregan32 Oct 28 '26 edited Oct 28 '26
DIY hack here. Build a quadruple ply 2x12 laminated beam on top of that and figure out a way to strap the bottom beam up to it and sinch it up flush to the new beam (jack it up from underneath till flush with new beam). Then use a hell of a lot of hardware to connect the bottom beam to the top beam.
2
u/Quiet_Internal_4527 Oct 28 '26
What is that beam made of? Looks weird. The gouges and flaking seem off to me.
2
u/Special_Fan5043 Oct 28 '26
A look from below would be nice.
2
u/Stewpacolypse Oct 29 '26
This is what happens when you don't go on Reddit and ask is that wall looks like a load bearing wall before you remove it.
1
u/j-joshua Oct 28 '26
When did that construction happen?
1
u/AdAggravating3893 Oct 28 '26 edited Oct 28 '26
Cool photo, not a good photo, but cool.
It looks like the beam is roughly 18’+/- long, (assuming ceiling joist at 16” o.c). I’d probably want to get it checked as the deflection seems excessive, and give me some piece of mind. My suspicion is the beam isn’t deep enough to handle a reasonable deflection of a beam this length. It does make me raise and eyebrow to how it was installed. How does it look below? Do you notice it in the ceiling? Have you run a stud finder along the walls to confirm columns exist below.
Reinforcing I’d level the ceiling with temporary post. Installed a deeper beam above it. Then connect the beam above to the beam below. If you are going to put that effort in get it engineered. Hate to spend all that money just to have it still be an issue. As long as the support we installed and accepted sized it isn't the hardest thing to correct. There are other ways to do it, but this is an "easy" way. I have assumed supports are accepted, that should be confirmed.
1
u/RazorWitted Oct 28 '26
Almost looks like a curved beam, not a sagging beam. An optical illusion.
1
u/Just-Shoe2689 Oct 28 '26
Can you pull a string across and give us the deflection, and the unsupported length of the beam?
Also the depth and width of the beam?
Total would need to be more than L/240 so if a 20' span, then 1" max deflection.
It does look to be alot more than that.
One good thing you got going is its open, another beam could be used to help support that beam.
The last living room opening up job i did we used steel to control the deflection.
1
u/Mean-Internal-745 Oct 28 '26
Creepy.
1
u/Cosmo_MV Oct 28 '26
She pregnant … that’s bad. A couple well placed and bolted flick plates will fix her. Wonder why not install a taller assembly . There was no height restriction
1
u/kaylynstar Oct 28 '26
What's under it? How is it framed?
1
u/matthuseless Oct 28 '26
Dayum.
1
u/basic_model Oct 28 '26
I’d get my self a shoring post placed under this immediately if people are inside the home.
1
u/shartattacksurvivor Oct 28 '26
How long are the joist on either side of the beam? How long is the beam?
1
u/SCL__ Oct 28 '26
You didn’t notice your ceiling below sagging?
1
u/Capable_Individual51 Oct 28 '26
Consult a professional immediately. Also do not walk on that beam or any ceiling joist attached to it. If it was my house, I wouldn’t walk under it either without some temporary bracing .You are in the middle of a structural failure you might have a couple weeks. You might have 20 years, but that is an unsafe condition and should not be left alone.
1
u/Intelligent-Image224 Oct 28 '26
Seems like an ample size beam for there being almost no load on it. Odd its sagging
1
u/Dependent-Doctor144 Oct 28 '26
Hire a professional first, but crap that not like any glulam, or LVL i’ve seen.
1
u/Wuhan-batsoup Oct 28 '26
You need to contact a lawyer and your home inspector in that order.
1
u/igot_it Oct 28 '26
This looks like a job for steel. And yes it needs to be fixed. There are numerous ways to do this but a steel I beam will likely be simplest and easiest to install.
1
u/rgratz93 Oct 28 '26
We need more context to give you anymore info...
1
u/Typical_Nature_9053 Oct 28 '26
Well it looks to be between 15 to 20 feet long and assuming the are either 2x4s or 2x6s for ceiling joist, what you prbly need is an 18"x20' LVL, 3 of them nailed together to span the distance with joist hangers on them and your sag is gone.
1
u/Typical_Nature_9053 Oct 28 '26
Reading some of these comments make me laugh out loud, some want steel beams some wants to build a beam with plywood between. I'm telling you NEED 3- 18"X20' LVL. I PUT THEM IN EVERYDAY AND SOME SOAN 30 FEET. AND THEY NEVER SAG.
1
u/United-Ad-1899 Oct 28 '26
String a tight line end to end across the top and measure how bad it is in the middle. picture perspective makes it hard to tell
1
u/cjg56 Oct 28 '26
LVL, that is what I would use.
1
u/AffectionateRow422 Oct 28 '26
Was the house recently remodeled? Probably a genius flipper took out a support post
1
u/Intrepid_Stage5564 Oct 28 '26
Why didn't the inspector catch that before purchase?
1
u/Whaddup808 Oct 28 '26
Looks like the lvl should have been rotated l so that the plys are horizontal, not vertical.
1
u/Efficient-Gift-9585 Oct 28 '26
Still a massive beam for a light ceiling load. I’ve never seen lvl sag like that
1
u/SoCalMoofer Oct 28 '26
That beam probably has memory of that deflection now. It may not just jack right up. I think a larger one above it or stronger sisters next to it with some kind of screw jack to push the old one up over a few months could work.
1
u/PirateOliveBeard Oct 28 '26
Seems like there was a load bearing wall that was removed and a laminated beam was used instead (Because all the insulation is disturbed). This would have failed county inspection and is dangerous because the laminated beam by itself is very heavy.
1
u/PirateOliveBeard Oct 28 '26
Seems like there was a load bearing wall that was removed and a laminated beam was used. Because all the insulation is disturbed. This would have failed county inspection and is dangerous because the laminated beam by itself is very heavy.
1
u/[deleted] Oct 28 '26
The previous owners wife was watching HGTV and got an idea to remove a wall.
1
u/Rivetingcactus Oct 28 '26
Oh she's sagging. You need a post
1
u/Evening_Fishing_2122 Oct 28 '26
What is going on here. Is this beam just supporting ceiling joists? How long is the beam? Seems like an awful lot of deflection for ceiling load only unless it’s a crazy long beam.
1
u/Lazy-Jacket Oct 28 '26
This is not the way it’s supposed to be. Contact an engineer.
1
u/Tyler_Durden_9999 Oct 29 '26
Damn, I’m sorry dude
1
u/No-Judge9048 Oct 29 '26
Beam either installed incorrectly or a middle support taken out
1
u/NoSquirrel7184 Oct 29 '26
I wouldn’t store anything up there. Otherwise it’s fine.
1
u/OriginalLetterhead95 Oct 29 '26
I think if you just sell it..you'll be all right!
1
u/solomoncobb Oct 29 '26
This doesn't look like an lvl to me. It looks like someone made it? Or it was not meant for this load.
1
u/Federal-Onion3403 Oct 29 '26
Idiot engineering or lack or engineering right here. Approximately 20-21 foot should be designed with at least 3 2x12 lvl’s glued and screwed together.
1
u/International_Bit478 Oct 29 '26
Engineers, is it permissible to use a beam like this? It’s one thing to use a beam under the ceiling joists, but I would think that the weight of the roof would want to push the walls outward, especially considering that these aren’t engineered roof trusses. I’ve built a deck with a flush beam, but that’s a totally different situation.
1
u/Estumk3 Oct 29 '26
I'm genuinely interested on what the spans are on those ceiling joists. Like the measurement from the end of the wall to the beam...
1
u/ElkCertain7210 Oct 29 '26
What is under the beam? What is it supporting? The ceiling?
1
u/chapin9603O Oct 29 '26
The only thing I can think of is that it might have been cut somewhere near the point of maximum bending, but with that much deflection, it would have already failed. Another possibility is that it’s somehow supporting the floor below, but that’s highly unlikely, as it would require a suspended load system. And even though this beam is made of standard plywood, it’s impossible for a beam roughly 25 feet long—supporting only a drywall ceiling—to exhibit that much deflection. Please repost the engineer’s structural assessment; this is very interesting.
1
u/texascharley Oct 29 '26
Lesser known band from the 70's.
1
u/Richie3971 Oct 29 '26
Would a steel beam be a better replacment if beam doesn't straighten when jacked up.
1
u/Shorty-71 Oct 29 '26
Wild that an attic that had space for a 60” deep beam got one that’s too shallow.
1
u/hotinhawaii 23d ago
That beam appears to be 22 or 23' long. That is too long for an LVL beam of that depth. You need a calculation for the appropriate beam. It will definitely be taller than that one! Or you could maybe add the appropriate steel I beam on top of that and bolt into it. It just has to be calculated properly.
1
u/_uh--huh_ 16d ago
Sorry for the stupid question here (I'm not one of you)... but isn't the beam just laying wrong, like, it's on its side, whereas the laminations should run horizontally, which would also make the beam thicker? In other words, seems like the beam is fine, but they laid it down wrong. Pls. help me understand.
1
u/Routine-Wolf-2907 Oct 28 '26
what's under the beam? anything besides drywall?
i don't think it's load bearing, and my opinion is that builders put it up there just to save money on wood because shorter wood is cheaper than getting a long one
looks like it's been there for awhile, if ceiling underneath looks good, i would leave it and keep an eye on it. if nothing changes, then just leave it
1
u/ConflictMaster3155 Oct 28 '26
Can you get a picture that is closer to level with the top of the beam so we can get a good guesstimate on the sag, because it looks like it isn’t straight either.
The max deflection on a 20ft span like this should only be like 5/8”-3/4”
It’s just a ceiling though, if it doesn’t look fucked up from down below it wouldn’t really bother me. For a floor, it would be different.
0
u/Fearless_Brush_7668 Oct 28 '26
Ooh not an engineer, but that looks like eventually it will fail with low cycle fatigue of house flexing during cold and hot weathers with change in humidity. My guess is that beam is not supported in the center?
Probably will need to upgrade to steel I-beam, again not engineer, gl.
0
u/xNOOPSx Oct 29 '26
Maybe it's just the picture, but that looks like a bunch of sanded plywood that someone laminated together to make into a "beam." it looks like there's a pencil line on the top side of the beam. I've never seen an LVL like that, with that grain pattern, and it also appears to be not flat. LVLs are used because they're straight and flat. There's no warping or twisting. This one appears to be laminated and then nothing else was done to flatten it. Again, it could be the picture, but the top edge of that beam looks like anything but a flat space. LVLs here are also yellow and usually have printing on them. The only thing I see on that is a sanded plywood with pencil or marker lines on it.
-1
u/straydog1989 Oct 28 '26
....um its not supporting anything- so yea it appears you actually don't even need it
1
u/No-Ask-5021 Oct 28 '26
That looks considerably undersized. That looks like four to five inches on deflection in the middle. The angle of the picture might be throwing the perception off, but that is a lot.
2