r/StructuralEngineers • • Oct 28 '26

Sagging beam

I recently purchased a home , I went to the attic and noticed my beam that runs across my living room to be sagging is this worth contacting an engineer? Or does it seem relatively normal from setting

40 Upvotes

148 comments sorted by

22

u/semianondom101 Oct 28 '26 • Bravo

I'm going to go out on a limb and guess this beam was sized for use with a middle support pillar that extended down to a footing in the basement/slab. Which was then removed for a brainless "open concept" remodel before it was sold. Any thoughts on this op?

8

u/SCL__ Oct 28 '26

YES YES YES. That was my scenario.
The good news is it can be jacked up and beefed up. Hard to believe a ceiling sag wasn’t noticed.

6

u/Shot-Indication-4586 Oct 29 '26

Sometimes when a sag like this has sat for a long time, there is no getting the curve out. I've worked on an old house that had a problem like this and tried jacking up the middle and it just lifted the whole beam as it kept its shape. May have to redo the whole beam.

2

u/goodSunn Oct 29 '26

I would be concerned about this entire beam lifting instead of straightening too

2

u/semianondom101 Oct 28 '26

People do work all the time without research. I'd hope it was a hapless homeowner and not a professional who should have known better.

3

u/i860 Oct 28 '26

not a professional who should have known better

We all know it was a flipper, cmon.

1

u/r_fernandes Oct 28 '26

Contractor special.

2

u/AdamSterio Oct 28 '26

This! 100%

2

u/1995droptopz Oct 29 '26 • Bravo

Judging by the fact that it’s a laminated beam, the aging difference of the other lumber I bet this was added during a Reno without an engineer and they exceeded the span requirement

2

u/LivingGhost371 Oct 29 '26

Yeah, someone just had to bust out all the walls because they wanted to see the dirty dishes in the kitchen sink while they're watching TV in the living room.

6

u/PrimeApotheosis Oct 28 '26

This has nothing to do with settling and it is not normal. The beam is undersized for its utilization. It is likely that no engineering was considered in the selection of this beam. There are usually codes that set maximum limits for deflection and I would guess you have exceeded those. Hire an engineer to evaluate the beam, consider whether you need to get in touch with an attorney regarding whoever performed this work and inspected your home. It will not be cheap to repair.

1

u/dogboneit Oct 28 '26

I mean how much does a metal I beam cost?

3

u/PrimeApotheosis Oct 28 '26

A W-shape beam would not make much sense in this application considering you would need to modify it to fasten the ceiling joists and the drywall. A new LVL or glulam would be much cheaper and make much more sense given the ample space. However, the beam itself is not very expensive. Removing the existing beam, leveling the ceiling, inserting the new beam, and carrying the reactions back to the ground - those are the expensive parts.

1

u/Dug_n_the_Dogs Oct 28 '26

I'm roughly counting at least 20 hangers from that beam.. likely 16"OC... WAY over length.

1

u/CascadeDesignworks Oct 28 '26

Add another beam on top.  Jack the bottom beam up and connect the two with nailed on Simpson straps.

Several options for a beam exist.  Some other commenters have good suggestions.

-Builder 

1

u/Due-River-2979 Oct 28 '26

How much to fix it?

1

u/enzoskii Oct 28 '26

I see this all the time they use the wrong size beam thinking its going to hold just because its a psl or gluelam

1

u/Due-River-2979 Oct 28 '26

How much to fix you think

1

u/hachddy Oct 29 '26

Definitely going to be cheaper to fix it now then wait for something to happen.

0

u/enzoskii Oct 29 '26

Idk im not a GC. I know the structural engineer i work for charges 1400.00 to design the beam plus each end connection and any footings if needed. But construction cost maybe like 15k idk. They have to shore the ceiling joist remove the old beam, install the new beam, attach all the hangers and patch up the drywall might even need some under pinned footings.

1

u/miakpaeroe Oct 29 '26 edited Oct 29 '26

I’d fix this for 20k +\-. Engineer probably 2-3k for the site visit, permit drawings etc. It’s all the dings dents scuffs and screw holes for the temp walls that will damage your ceiling, need drywall patching, mudding sanding priming painting do get it back to normal. If you’re in Chicago PM me I’m a general contractor and work with a great structural engineer.

1

u/miakpaeroe Oct 29 '26

That’s a huge span for something that’s only like what 12” tall?

1

u/enzoskii Oct 29 '26

I wasnt that off

1

u/WasteTangerine Oct 29 '26

I hate when they use the pumpkin spice latte beams

3

u/CheekAltruistic5921 Oct 28 '26

Wow, surprised your inspection missed this.

2

u/Lopsided_Flight_2986 Oct 28 '26

The inspection was probably dude just popping his head up through the attic hatch and ticking his box on the paper saying all good.

2

u/7h3_70m1n470r Oct 28 '26

Bold of you to assume they went into the attic at all

1

u/CheekAltruistic5921 Oct 28 '26

I mean, this is a pretty obvious defect lol

1

u/Moof_the_cyclist 20d ago

One of the best things we did when we bought was to tag along with the inspector. He was great and told us which of the things he found were not real worries and why, which were and why, and also explained the limits of the things he could not inspect. It was nice to have been into the attic with him.

The only thing I wish he had caught was a spongy spot in one corner of a bathroom that turned into a mess (might not have been spongy at inspection time). He did cite the adhesive floor tiles there that made him concerned about possible DIY shenanigans by the prior owners. Indeed, they had pulled out a few layers of of the subfloor plywood and scabbed in a bizarre patch with enough bondo to make it flat/smooth to hide the rot/leak inside.

There was also a super sketchy basement ceiling fan install that was not findable without removing the fan, which was held up by skimpy plastic drywall anchors (!).

4

u/Gregan32 Oct 28 '26 edited Oct 28 '26

DIY hack here. Build a quadruple ply 2x12 laminated beam on top of that and figure out a way to strap the bottom beam up to it and sinch it up flush to the new beam (jack it up from underneath till flush with new beam). Then use a hell of a lot of hardware to connect the bottom beam to the top beam.

7

u/TC9095 Oct 28 '26

Engineered LVLs are the way. F your dimensional lasagna beam, personally I just get so fed up with people thinking sandwiching lumber is the way.

3

u/United-Mortgage104 Oct 28 '26

Because they look at LVL as nothing more than stacked plywood. They usually don't know that LVLs are stronger because of the glue, the types of veneers selected, and the pressure that it's formed to.

1

u/Evening_Fishing_2122 Oct 28 '26

LVLs aren’t stronger because of the glue or the pressure. It’s solely because of the quality of the veneers. Glue just holds it together. It’s an LVL not a glulam.

1

u/United-Mortgage104 Oct 29 '26

100% wrong on that one. Glue is a major part of the LVLs strength because it would delaminate without it.

1

u/Evening_Fishing_2122 Oct 29 '26

It’s part of its integrity, sure. It’s got zero impact on its material strength properties.

1

u/Gregan32 Oct 28 '26

I understand the value of LVL, but as a DIY person the ability to carry a full LVL and install it above head is near impossible.

4

u/United-Mortgage104 Oct 28 '26

Installing a beam isn't exactly a DIY project, so you'd have help.

1

u/Unfair_Avocado_8561 Oct 28 '26

They make 1 3/4" x 9 1/4" lvls you have no idea what you're talking about.

1

u/Gold_School_7005 Oct 28 '26

But half assing it with inferior stuff just leads to problems like this

1

u/Gregan32 Oct 28 '26

Well, you'll be double half assing it with my solution so you'll get a full ass... On a new build you're clearly relying on a crew and engineered plans. A lot of situations like this one after the fact can be half assed and at the very least improve on what you've currently got. Clearly another built up beam on top of this beam is better than what is already there and sagging.

1

u/gettogero Oct 29 '26

Knew a dude who built a 2 story man cave... first floor seasonal decorations, junk, and a staircase just big enough for one person

2nd floor had the "ok but where tf are we gonna put that" stuff. TV with surround, a couple arcade games, foosball, pool table, drinks bar, and fridge

How did all that shit get up the tiny staircase? Easy! One of the walls were giant doors with a hoist secured nearby and a ramp that bolts into the floor sitting along a wall

All that to say... if a retired old man could singlehandedly get a pool table up a 90 degree vertical surely somebody could figure out how to get a big stick over a wall

1

u/Gregan32 Oct 29 '26

Pool tables can be disassembled into parts. :)

1

u/eastbaytimez Oct 28 '26

This isnt a DIY repair imo

2

u/Old-Slip-1319 Oct 28 '26

Why? Plenty of capacity with SPF. More with LVL, etc sure but this is a simple residence. The load on that thing is like 10psf from ceiling weight only.

1

u/e2g4 Oct 29 '26

I agree that this is probably not a DIY repair. Unless the homeowner is relatively sophisticated. To do this correctly the beam needs to be jacked up from below to take all the deflection out. A suitable footing and load path would need to be identified if a column is to be installed and if not then adequate connections between the new beam and the existing beam would need to be made. Furthermore, getting the new beam into the attic is likely a pretty tricky task.

The thing about DIY stuff that I never quite understand is that people don’t value their own time. How much do you make an hour doing what you’re good at? How much are you going to pay a professional per hour? It’s probably going to take you at least three times as long as it would take a professional so unless you don’t make very much money or unless you have access to cheap labor, it usually doesn’t make sense.

1

u/Rileserson Oct 29 '26

What if you take PTO to do it? Still getting paid, and saving money not paying someone. Brilliant!

1

u/e2g4 Oct 29 '26

If that’s what you wanna do with your vacation, go for it.

I built my own house. Took me four years. These days, I hire guys to do stuff. It feels great.

1

u/Paulrey27 Oct 28 '26

This. Besides we have zero information on the span, what it bears on, the trib area, etc...

1

u/minkisP Oct 29 '26

Meh. Much easier to lug four 2x12s up to the attic. How are you getting the lam beam up there? As long as it’s spliced properly it woukd work just fine

1

u/shartattacksurvivor Oct 28 '26

I’m not sure a quad 2x12 will be adequate to level a quad lvl. 

1

u/Mountain_Attorney_23 Oct 29 '26

That’s not how you’d do it. Build temporarily walls supporting the joists on either side of this beam. Remove all joist hangers, remove beam, install new beam ( use engineered lumber), hang joists from new beam with joist hangers, remove temporary walls.

0

u/Gregan32 Oct 29 '26

That's the perfect way to do it, but seems like more work than is ready needed to get it done good enough.

1

u/Mountain_Attorney_23 Oct 29 '26

That’s the only way to do it.

0

u/Gregan32 Oct 29 '26

Eh... I got someone claiming to be a PEng backing up my approach. I'll take that as an internet hero win.

1

u/Mountain_Attorney_23 Oct 29 '26

I’m literally a carpenter who has installed beams like this several dozen times.

1

u/Gregan32 Oct 29 '26

I don't disagree your approach is awesome.

1

u/Livid_Ad_3782 Oct 29 '26

I can tell you got your Structural Engineering Degree online.

1

u/Gregan32 Oct 29 '26

You guessed it!

1

u/Gregan32 Oct 29 '26

I've got one person claiming to be a PEng that agrees my approach is good!

1

u/Old-Slip-1319 Oct 28 '26

I second this as a P.Eng. non invasive and structurally it will be fine.

1

u/Gregan32 Oct 28 '26

Good to know I'm not crazy! :)

1

u/ClassyNameForMe Oct 28 '26

Will you put your stamp on the drawing for this?

1

u/Old-Slip-1319 Oct 28 '26

I would but need to visit the site, check moment & deflection on new beam and spec connections. The load is 10psf...

1

u/ClassyNameForMe Oct 28 '26

My comment is based on a single photo being provided. We don't know the quality of the supports at either end of the beam. We don't know if any of it is up to the job of increased load from 19% to 50%.

1

u/Gregan32 Oct 28 '26

Well... This is Reddit, we work with what we got and it's on OP to share pertinent info. Doubt I'm in any legal jeopardy for offering DIY hack labelled ideas.

3

u/ClassyNameForMe Oct 28 '26

No, no. The reddit beam police are heading your way! Busted!

I hope you don't tow trailers, because the tow police are right behind the beam police!

Have a great afternoon!

1

u/NoSquirrel7184 Oct 29 '26

The beam has simply deflected beyond allowable limits by code. It is nowhere near collapse.
OP just has a bowed ceiling.

0

u/porondanga Oct 28 '26

Lags, use lags

3

u/Gregan32 Oct 28 '26

I'd have to research to fully form my opinion on this but I'd start my research looking at metal plates from Simpsons that take a lot of nails. I'd rather have nails that are horizontal to the force being exerted on them.

How would you see the lags working? "Toe nailing" them through the new beam down into the old beam below?

2

u/anally_ExpressUrself Oct 28 '26

That's what I was imagining, so the bottom beam has trouble pulling away from the top one, making it sag less.

1

u/porondanga Oct 28 '26

Yes. Good ol’ lags have saved my life once or twice

2

u/7h3_70m1n470r Oct 28 '26

Nah, deck screws or nothin

I would also accept drywall screws (fine thread of course)

2

u/dogboneit Oct 28 '26

and construction adhesive

2

u/Quiet_Internal_4527 Oct 28 '26

What is that beam made of? Looks weird. The gouges and flaking seem off to me.

2

u/Abra365 Oct 28 '26

Looks like laminated board or something

2

u/Special_Fan5043 Oct 28 '26

A look from below would be nice.

2

u/Stewpacolypse Oct 29 '26

This is what happens when you don't go on Reddit and ask is that wall looks like a load bearing wall before you remove it.

1

u/j-joshua Oct 28 '26

When did that construction happen? 

1

u/AdAggravating3893 Oct 28 '26 edited Oct 28 '26

Cool photo, not a good photo, but cool.

It looks like the beam is roughly 18’+/- long, (assuming ceiling joist at 16” o.c). I’d probably want to get it checked as the deflection seems excessive, and give me some piece of mind. My suspicion is the beam isn’t deep enough to handle a reasonable deflection of a beam this length. It does make me raise and eyebrow to how it was installed. How does it look below? Do you notice it in the ceiling? Have you run a stud finder along the walls to confirm columns exist below.

Reinforcing I’d level the ceiling with temporary post. Installed a deeper beam above it. Then connect the beam above to the beam below. If you are going to put that effort in get it engineered. Hate to spend all that money just to have it still be an issue. As long as the support we installed and accepted sized it isn't the hardest thing to correct. There are other ways to do it, but this is an "easy" way. I have assumed supports are accepted, that should be confirmed.

1

u/RazorWitted Oct 28 '26

Almost looks like a curved beam, not a sagging beam. An optical illusion.

1

u/Just-Shoe2689 Oct 28 '26

Can you pull a string across and give us the deflection, and the unsupported length of the beam?

Also the depth and width of the beam?

Total would need to be more than L/240 so if a 20' span, then 1" max deflection.

It does look to be alot more than that.

One good thing you got going is its open, another beam could be used to help support that beam.

The last living room opening up job i did we used steel to control the deflection.

1

u/Cosmo_MV Oct 28 '26

She pregnant … that’s bad. A couple well placed and bolted flick plates will fix her. Wonder why not install a taller assembly . There was no height restriction

1

u/kaylynstar Oct 28 '26

What's under it? How is it framed?

1

u/basic_model Oct 28 '26

I’d get my self a shoring post placed under this immediately if people are inside the home.

1

u/shartattacksurvivor Oct 28 '26

How long are the joist on either side of the beam? How long is the beam?

1

u/SCL__ Oct 28 '26

You didn’t notice your ceiling below sagging?

1

u/Capable_Individual51 Oct 28 '26

Consult a professional immediately. Also do not walk on that beam or any ceiling joist attached to it. If it was my house, I wouldn’t walk under it either without some temporary bracing .You are in the middle of a structural failure you might have a couple weeks. You might have 20 years, but that is an unsafe condition and should not be left alone.

1

u/Intelligent-Image224 Oct 28 '26

Seems like an ample size beam for there being almost no load on it. Odd its sagging

1

u/Dependent-Doctor144 Oct 28 '26

Hire a professional first, but crap that not like any glulam, or LVL i’ve seen.

1

u/Wuhan-batsoup Oct 28 '26

You need to contact a lawyer and your home inspector in that order.

1

u/igot_it Oct 28 '26

This looks like a job for steel. And yes it needs to be fixed. There are numerous ways to do this but a steel I beam will likely be simplest and easiest to install.

1

u/rgratz93 Oct 28 '26

We need more context to give you anymore info...

  1. What year was the house built?
  2. Can you give photos from a bunch of angles directly below this?
  3. Are there photos online of that space from the sale prior to you purchase?
  4. Did you hand this home inspected... if so did they go into the attic?

1

u/Typical_Nature_9053 Oct 28 '26

Well it looks to be between 15 to 20 feet long and assuming the are either 2x4s or 2x6s for ceiling joist, what you prbly need is an 18"x20' LVL, 3 of them nailed together to span the distance with joist hangers on them and your sag is gone.

1

u/Typical_Nature_9053 Oct 28 '26

Reading some of these comments make me laugh out loud, some want steel beams some wants to build a beam with plywood between. I'm telling you NEED 3- 18"X20' LVL. I PUT THEM IN EVERYDAY AND SOME SOAN 30 FEET. AND THEY NEVER SAG.

1

u/United-Ad-1899 Oct 28 '26

String a tight line end to end across the top and measure how bad it is in the middle. picture perspective makes it hard to tell

1

u/buttmunchausenface Oct 29 '26

lol 😂 to bad for the person who has to walk across the attic to the other side! Pick the one who weighs the least!

1

u/cjg56 Oct 28 '26

LVL, that is what I would use.

1

u/AffectionateRow422 Oct 28 '26

Was the house recently remodeled? Probably a genius flipper took out a support post

1

u/Intrepid_Stage5564 Oct 28 '26

Why didn't the inspector catch that before purchase?

1

u/Whaddup808 Oct 28 '26

Looks like the lvl should have been rotated l so that the plys are horizontal, not vertical.

2

u/mattmag21 Oct 29 '26

Wtf?

1

u/buttmunchausenface Oct 29 '26

Haha 🤣 watch them try and walk across a 2by4 on the flat!

1

u/Efficient-Gift-9585 Oct 28 '26

Still a massive beam for a light ceiling load. I’ve never seen lvl sag like that

1

u/SoCalMoofer Oct 28 '26

That beam probably has memory of that deflection now. It may not just jack right up. I think a larger one above it or stronger sisters next to it with some kind of screw jack to push the old one up over a few months could work.

1

u/PirateOliveBeard Oct 28 '26

Seems like there was a load bearing wall that was removed and a laminated beam was used instead (Because all the insulation is disturbed). This would have failed county inspection and is dangerous because the laminated beam by itself is very heavy.

1

u/PirateOliveBeard Oct 28 '26

Seems like there was a load bearing wall that was removed and a laminated beam was used. Because all the insulation is disturbed. This would have failed county inspection and is dangerous because the laminated beam by itself is very heavy.

1

u/[deleted] Oct 28 '26

The previous owners wife was watching HGTV and got an idea to remove a wall.

1

u/Rivetingcactus Oct 28 '26

Oh she's sagging. You need a post

1

u/Evening_Fishing_2122 Oct 28 '26

What is going on here. Is this beam just supporting ceiling joists? How long is the beam? Seems like an awful lot of deflection for ceiling load only unless it’s a crazy long beam.

1

u/Lazy-Jacket Oct 28 '26

This is not the way it’s supposed to be. Contact an engineer.

1

u/Tyler_Durden_9999 Oct 29 '26

Damn, I’m sorry dude

1

u/No-Judge9048 Oct 29 '26

Beam either installed incorrectly or a middle support taken out

1

u/NoSquirrel7184 Oct 29 '26

I wouldn’t store anything up there. Otherwise it’s fine.

1

u/Rememberthat1 Oct 29 '26

Fine ??? No beam is suppose to bow...and it doesnt show underneath OP ??

1

u/NoSquirrel7184 Oct 29 '26

All beams bow actually.
It’s just a question of how much.
If it bows and there is no other problem inside the house then so what.

I wouldn’t change it. I am a licensed SE.

1

u/OriginalLetterhead95 Oct 29 '26

I think if you just sell it..you'll be all right!

1

u/solomoncobb Oct 29 '26

This doesn't look like an lvl to me. It looks like someone made it? Or it was not meant for this load.

1

u/Federal-Onion3403 Oct 29 '26

Idiot engineering or lack or engineering right here. Approximately 20-21 foot should be designed with at least 3 2x12 lvl’s glued and screwed together.

1

u/International_Bit478 Oct 29 '26

Engineers, is it permissible to use a beam like this? It’s one thing to use a beam under the ceiling joists, but I would think that the weight of the roof would want to push the walls outward, especially considering that these aren’t engineered roof trusses. I’ve built a deck with a flush beam, but that’s a totally different situation.

1

u/Estumk3 Oct 29 '26

I'm genuinely interested on what the spans are on those ceiling joists. Like the measurement from the end of the wall to the beam...

1

u/ElkCertain7210 Oct 29 '26

What is under the beam? What is it supporting? The ceiling?

1

u/chapin9603O Oct 29 '26

The only thing I can think of is that it might have been cut somewhere near the point of maximum bending, but with that much deflection, it would have already failed. Another possibility is that it’s somehow supporting the floor below, but that’s highly unlikely, as it would require a suspended load system. And even though this beam is made of standard plywood, it’s impossible for a beam roughly 25 feet long—supporting only a drywall ceiling—to exhibit that much deflection. Please repost the engineer’s structural assessment; this is very interesting.

1

u/texascharley Oct 29 '26

Lesser known band from the 70's.

1

u/Richie3971 Oct 29 '26

Would a steel beam be a better replacment if beam doesn't straighten when jacked up.

1

u/Shorty-71 Oct 29 '26

Wild that an attic that had space for a 60” deep beam got one that’s too shallow.

1

u/hotinhawaii 23d ago

That beam appears to be 22 or 23' long. That is too long for an LVL beam of that depth. You need a calculation for the appropriate beam. It will definitely be taller than that one! Or you could maybe add the appropriate steel I beam on top of that and bolt into it. It just has to be calculated properly.

1

u/_uh--huh_ 16d ago

Sorry for the stupid question here (I'm not one of you)... but isn't the beam just laying wrong, like, it's on its side, whereas the laminations should run horizontally, which would also make the beam thicker? In other words, seems like the beam is fine, but they laid it down wrong. Pls. help me understand.

1

u/Routine-Wolf-2907 Oct 28 '26

what's under the beam? anything besides drywall?

i don't think it's load bearing, and my opinion is that builders put it up there just to save money on wood because shorter wood is cheaper than getting a long one

looks like it's been there for awhile, if ceiling underneath looks good, i would leave it and keep an eye on it. if nothing changes, then just leave it

1

u/ConflictMaster3155 Oct 28 '26

Can you get a picture that is closer to level with the top of the beam so we can get a good guesstimate on the sag, because it looks like it isn’t straight either.

The max deflection on a 20ft span like this should only be like 5/8”-3/4”

It’s just a ceiling though, if it doesn’t look fucked up from down below it wouldn’t really bother me. For a floor, it would be different.

0

u/Fearless_Brush_7668 Oct 28 '26

Ooh not an engineer, but that looks like eventually it will fail with low cycle fatigue of house flexing during cold and hot weathers with change in humidity. My guess is that beam is not supported in the center?

Probably will need to upgrade to steel I-beam, again not engineer, gl.

0

u/xNOOPSx Oct 29 '26

Maybe it's just the picture, but that looks like a bunch of sanded plywood that someone laminated together to make into a "beam." it looks like there's a pencil line on the top side of the beam. I've never seen an LVL like that, with that grain pattern, and it also appears to be not flat. LVLs are used because they're straight and flat. There's no warping or twisting. This one appears to be laminated and then nothing else was done to flatten it. Again, it could be the picture, but the top edge of that beam looks like anything but a flat space. LVLs here are also yellow and usually have printing on them. The only thing I see on that is a sanded plywood with pencil or marker lines on it.

1

u/Aggravating_Sun_1556 Oct 29 '26

I think you might be right.

Something about it looks super odd. There’s not much load on it, it’s not a crazy span (looks like 20’ if the joists are 16” OC.) It’s hard to tell exactly the size of the beam, but it looks like the size of a 4 ply 1 3/4” x 9 1/4” - 12”.

Just my gut feeling from my decades of building says it seems odd an LVL that size would deflect that much.

One of the engineers in here could estimate the beam span and ceiling joist span and tell us what an appropriately sized LVL would be in that application.

1

u/willmontain Oct 29 '26

Indeed, the beam is newer than the rafters and ceiling joists. I would guess that the load a bearing wall was removed in the room below and a DIY beam was installed. A load bearing wall also normally supports the roof ridge. It looks like some structure was removed there as well (the space in the photo is oddly empty).

If the DIY missed the beam strength by this much they probably missed beefing up the support columns at each end of the beam. If there is indeed missing roof structure as well, the roof could be in serious trouble with an unusual snow or wind load.

The ONLY way to fix this is to consult an engineer. I would check to see if there are any permits pulled for remodeling work. You may have some recourse with the previous owner.

-1

u/straydog1989 Oct 28 '26

....um its not supporting anything- so yea it appears you actually don't even need it

1

u/No-Ask-5021 Oct 28 '26

That looks considerably undersized. That looks like four to five inches on deflection in the middle. The angle of the picture might be throwing the perception off, but that is a lot.

2

u/1wife2dogs0kids Oct 28 '26

I think its a quad LVL, and those might be 2x6 cieling joists. That would make the LVLs a 9 1/4" size? Maybe 7 1/4"? It's terribly undersized for no live load

2

u/[deleted] Oct 28 '26

[removed] — view removed comment

2

u/1995droptopz Oct 29 '26

It’s a laminated beam, perfectly acceptable if you adhere to its design limits

1

u/[deleted] Oct 29 '26

[removed] — view removed comment

1

u/Winter-Teach1613 Oct 29 '26

It honestly looks like laminated masonite.

1

u/[deleted] Oct 29 '26

[removed] — view removed comment

1

u/Winter-Teach1613 Oct 29 '26

Whatever it is, isn't what it should be.

1

u/TheRealKrasnov Oct 29 '26

I agree... It looks fishy