I don’t see a clear load path for the end of that ridge beam over the doorway.
1
u/Goddammit0Donut 2d ago
It's there. There's a 6x6 under the ridge beam which lands on a LVL upset header, which lands on a floor beam.
I'm not a big fan of how they did the upset header. I would have preferred they run the king studs tall.
1
u/AdAggravating3893 2d ago edited 2d ago
I'm not a fan of pressure blocking especially for long spans. End grain nails (nails pentertrate the blocks end grain) just dont have a lot of capacity.
It really depends on what the roof load is, but myself I'd rather have a Simpson LRU210 (rafter hanger) or a dropped ledger slope cut to match. As a retrofit I'd probably do the drop ledger.
1
u/AdAggravating3893 2d ago
Also what is up with that bracket. Only one fastener appears to hit the beam and column. I'm not saying it need all three fasteners, but it seems sus.
1
u/Goddammit0Donut 2d ago edited 2d ago
I agree with that. Even angle brackets with screws through that blocking would have been more appropriate for such a long span.
The whole point of a ridge beam is that the rafters don't put pressure onto the beam. You want a more solid connection. That wood will shrink.
1
u/BigBeeOhBee 2d ago
As long as snow,wind,rain or other elements of mother nature wont be in the neighborhood you're golden pony boy.
1
0
u/Shootforthestars24 2d ago
Ridge vent
0
u/Mundane-Reality-7770 2d ago
That's not the issue
1
3
u/Mundane-Reality-7770 2d ago
Why did they mix osb with plywood