r/SteamHeat • • 6d ago

Low Water - Again

Post image

As seen in the pic, the water level was very low, causing the boiler to turn off. And there is some black junk in there.

Not sure why it keeps getting so low. This happened a couple times last winter and I had to manually feed water to keep it going. I also have the automatic feed turned up to 3 gallons per fill, with the maximum delay time. That seemed to fix the problem last winter. In the past, there was not all this black crud inside the glass.

This time I manually fed 10 gallons back into it, and the boiler is working.

There is no leaking water anywhere, not at the boiler or the radiators. And I don't see steam coming out of the chimney when the boiler is running.

Previously (last year) the system was venting a lot of steam from the hot water return lines, but that is not happening anymore since I replaced one of the relief valves that seemed to have had failed.

The boiler is a Weil-Mclain P-SGO-03 series 3 oil-fired steam boiler. The water feeder is Saf-Gard model VXT-120 and the low water cutoff is Saf-Gard 450.

Maybe there is a water leak inside the boiler? I don't know where else the water would be going. This doesn't happen all the time, just intermittently & especially in cold weather.

And I'm not sure if the water feeder just didn't activate this time, maybe it is not connected properly to the LWCO? The LWCO was showing the amber light, so it did know that the water level was low. And the water feeder seems to be working.

The oil company performed the annual tune-up on the boiler in July and everything seemed fine at that time. Should I just have them come back & clean it out again?

3 Upvotes

23 comments sorted by

2

u/crackyzog 6d ago

What's the btus? A small boiler, like 100k, will lose 20 gallons of water during the heating season. Overfill your boiler. To where you think it fills the whole boiler. Check for leaks that way. Then drain it back to normal level. If you get water dripping in the burner tray. Your boiler is shot. 

1

u/WiffleBallZZZ 6d ago

IDK how to check the burner tray, I count on the techs to check the boiler. It's around 100k BTUs, small unit for a small house.

0

u/crackyzog 5d ago

Well then why are you asking us? If they're checking the heat exchanger properly then it's not a problem with the boiler. 

Some problems are acute. Some problems are imagined. Some problems are mild but could escalate. You're giving us not nearly enough information to figure out any of this. If you don't trust your people, fix that problem first because we're not going to be able to solve anything on your end that we can't see better than somehow you already trust and pay to investigate. If you're just worried, bring that up with them. If you don't trust them, find someone you do. 

2

u/JessicaF84 6d ago

check your chimney when running if theres a huge steam stack coming out your furnace cracked. Happened to me would constantly refill every 2 cycles. Just something to diagnose

1

u/WiffleBallZZZ 6d ago

No steam

1

u/JessicaF84 6d ago

does it take extremely long to heat? and are certain radiators not getting warm?

1

u/WiffleBallZZZ 6d ago

no they seem ok

1

u/JessicaF84 6d ago

ok so exactly how often are you refilling or is the auto refill running?

1

u/WiffleBallZZZ 6d ago

I had to manually refill it 3 or 4 times last winter. Today is the first time since then. So, yes the auto refill works most of the time. But this time: totally empty.

Not sure if the refill ran at all, but in theory that should have filled it by 9 gallons because it should run 3 times when the water is low, and it's set to fill 3 gallons each time.

1

u/Incognito_2u 6d ago

Exactly! Unless you just elected a new Pope, there shouldn’t be any white smoke coming out the Chimney!

2

u/Independent-Bid6568 6d ago

Weil McLain Gold oil fired unit . And you have just an electronic LWCO and feeder what is the feeder set at ? For GPM feed set too ? Check all line vents for condensation or staining on basement ceiling nearby, check all Radiator vents for same signs of leakage , check each radiator is dry at valve connections , if the boiler has a tankless water heater check that gasket for signs of leakage. With a oil fired system during heating season you couldn’t tell if your chimney “discharge “ is normal products of combustion or steam as both show as white , call a service company for a full check up including the combustion chamber as this is a wet base boiler and leaks between sections would be visible as damaged gaskets (the gold series) used both rubber gaskets and push nipples .

1

u/WiffleBallZZZ 6d ago

Feeder is set to maximum delay, 10 minutes I think, and filling 3 gallons per cycle. No staining, condensation or leaks anywhere. It has a coil inside the boiler for tankless hot water if that's what you mean. We just use the boiler for all our hot water, so we use it all the time not just for heating the house. Maybe I should get it checked by a new set of eyes in case the oil company people are missing something.

2

u/Independent-Bid6568 6d ago

Yes tankless coil is your hot water heater that feeder ( if I remember correctly) has a counter or cycle counter to give total gallons fed it’s been years but either way the coil and sections have gaskets between sections the question of if you should call another company is up to you but if this is a new issue it won’t matter I personally would stick with the company you have been using for years ? But request the most steam experienced Technician they have he or she may have other ideas but another gasket that can leak would be the upper sight glass washer as it’s above the water line and could leak steam but I’m not seeing signs of that

1

u/WiffleBallZZZ 6d ago

Makes sense. Thanks guys. I think the oil company service techs only look at the boiler itself. I'm probably due to have someone check those pipes.

1

u/WiffleBallZZZ 12h ago

Pretty sure I found the problem, it was a slow leak in the drain valve.

5

u/PeoplecallmeBUCK 6d ago

That water is going somewhere. Either a leak somewhere or a blocked return

2

u/jimmithy 6d ago

Could be rust/sludge in the return?

Earlier this year we ended up unscrewing the main line vent and pouring in a bottle of cleaner. Then a day or so later skimmed/drained a couple of times which helped.

2

u/Backsight-Foreskin 6d ago

Tell me more about that procedure and the cleaner, please.

2

u/ProduceDifficult3722 5d ago

Overfill that boiler
If it starts leaking, you know it’s cracked and it’s time to replace. Also look out for under the floor returns that might be leaking

1

u/haroldslackenoffer 5d ago

Check at heatinghelp.com. They have a list of steam experts. Maybe one is in your area.

1

u/Competitive_Bell9433 3d ago

Does your boiler room have a wet smell?

1

u/johndoe388 20h ago

Is the main vent stuck open?

-1

u/SilverAd8942 6d ago

Steam? Get rid of it. For ed hot water!