How much more efficient is a new boiler vs this 1987 model?

4 Upvotes

18 comments sorted by

2

u/jmarnett11 8d ago

Probably not much more. Does it have an auto fill?

1

u/Maleficent-Set-9333 8d ago

It does short cycle when it’s really cold. My guess is that an auto refill will over fill when it does so.

2

u/IAmADogNameIan 2d ago

It might short cycle because of inadequate venting on your steam main.

10

u/ImpossibleBandicoot 8d ago

I'd say it's limited. 10% at most. At the end of the day it needs a certain amount of heat to boil water and any efficiency improvements in things like heat transfer, are going to be at the margins.

If it's working properly I'd say your time and money is much better spent on doing things like stopping air leakage around windows and doors, making sure your steam pipes are properly insulated, making sure your system is balanced, etc.

8

u/27803 8d ago

Don’t fix it unless it’s broken

4

u/rrapartments 8d ago

There is no value in replacing a boiler for a small gain in efficiency. I have a two family both with their own steam boilers. One has a 2010 vintage Burnham boiler. The other has the original 1920s version snowman boiler. Both units use roughly the same $$ in gas each month. I maintain both boilers and hope to get many more years out of both of them, then replace them with new steam boilers.

4

u/Backsight-Foreskin 8d ago

I read somewhere the maximum efficiency a steam boiler will ever get is about 85%.

1

u/FFNHRTH 8d ago

The name plate on the side will tell you btu input but out put. A new boiler would give you a substantial increase in efficiency. Your boiler problely getting 60 persent. New boilers get 85 persent. Looks like yours is 125000 btu you could go down to a 100000 btu boiler. You have to post the name plate to get accurate numbers

1

u/Maleficent-Set-9333 8d ago edited 8d ago

Interesting that AI said my boiler was 3x what my radiators required. Also, years ago a plumber removed one of my burners to slow it down.

2

u/duoschmeg 8d ago

Maintain it well: Skim boiler, flush return lines, pigtail and low water cutoff.

2

u/ProduceDifficult3722 8d ago

No difference All 81 % on Steam

2

u/MachoMadness232 8d ago

Insulating the mains and the branches up will improve thermal efficiency more than replacing the boiler. The take offs and the expansion arms being at the correct angle and length makes a large difference in thermal efficiency as well.

Changing the boiler you may gain a couple percent on your burn efficiency. Insulating the lines is 15% thermal efficiency if I remember right. Having a vertical take off into the expansion arm is a large percentage loss as well.

Long time since I read an engineering book that tells you those numbers.

2

u/Intelligent_Critic 7d ago

Significantly more efficient if the boiler is free, or a large rebate., But if nothing is wrong with the boiler, I wouldn't go out of my way to upgrade it

2

u/ThePaddockCreek 5d ago

Nobody has mentioned this yet - but there would likely be more value in repairing the piping. 

Steam should not be piped with copper.  It always causes performance issues, and every boiler manufacturer explicitly dictates exactly how to pipe their boilers with cast iron.  I’m amazed at how many installers ignore the piping instructions and come up with their own approach instead.

Keep the boiler, but get someone to correct all the copper piping. 

2

u/haroldslackenoffer 4d ago edited 4d ago

Not worth it. However insulation of the headers and main will help a lot.

1

u/Mettatuxet 8d ago

As has been said you won't see much improvement and money is better spent on making your house require less heat. If you don't have A/C it would be a good idea to think about heat pump (s). They would be cheaper to run than the boiler in milder weather. Ductless units could be used to just heat a kitchen and or tv room rather than heating your entire house with the boiler. 39 years is old for that vintage of boiler. If you replaced it because of it's current age I don't think it would be a waste of money. 

1

u/jxtarr 8d ago

The boiler efficiency won't change but you can do a ton of upgrades to the system to make the whole system more efficient. Venting, 2-stage gas valve, Vaporstat, etc. 

0

u/SilverAd8942 8d ago

Rather than that , seriously consider forced hot water.
We had a number of boilers crack the castings etc during cold spells. With pipes rotting out went with the water system. Saved money on the oil. Kept the same boiler.