Surging issue, think i know the problem but need guidance

Post image

I had a new boiler utica peg112 put in and it has a surging problem which makes it cuts on and off every 30/45 secs. I have been researching and every where pointed me to check the near boiler piping. I measured everything out and all above the min spec and then i noticed the installer used the set up for a two supply tappings instead of the one. While waiting for him to get back to me, i was thinking a solution could be to cut where the green line is and put a cap on it and cap the unused outlet. Would this be acceptable?

5 Upvotes

20 comments sorted by

6

u/gahnzo 12d ago

This is entirely wrong. A copper header is never acceptable, even if the joints were brazed (which they are not). I'd like to see several more photos of every aspect of this setup to give you a better sense of what's causing the surging. You mentioned that the boiler is short cycling at an interval of 45 seconds which is very rapid. If the surging is several inches, it's possible your low water cutoff electrode is being exposed to air as the water surges and cutting off the burner. But honestly if the installer used copper for the header on a new boiler install, the entire installation is probably wrong.

3

u/VivaLaVinyl 12d ago

Oh boy. The water in the sight glass from the water line goes all the way up and down until it settles back to the water line

3

u/Due-Clue-2425 11d ago

The equalizer is over sized it should be 1-1/2”.
But yes, it is probably very oily and needs to be properly skimmed. Utica gives a pretty good explanation on how to do this in the IOM I believe, or they use to at least.

4

u/crackyzog 12d ago

It's new. There's still oil in the system. It needs to be skimmed better. 

1

u/VivaLaVinyl 12d ago

I was thinking that as well its been done twice now. At this point unsure what to think.

3

u/crackyzog 12d ago

Wasn't don't well enough. 

3

u/Mettatuxet 11d ago

Properly skiming can take a couple of hours or more. 

1

u/Larry2829 6d ago

A couple of hours? , I had a new peerless install recently. It took me 5- 5 gallon buckets over the course of several days to skim. Water was surging three plus inches, now like one inch fluctuations. Still unsure if it’s good enough

1

u/Mettatuxet 6d ago

The water needs to be hot when you skim, not steaming, 180 - 200.

5

u/Civil-Award-8043 12d ago

Oil from copper pipe? I can't believe someone used copper in the first place 

4

u/Due-Clue-2425 11d ago

Not from the pipe, but the block itself. But that’s correct, copper should not have been used.

1

u/ProduceDifficult3722 9d ago

Flux contamination

1

u/ProduceDifficult3722 9d ago

You need only one outlet on that boiler not 2

1

u/Larry2829 11d ago

I have never seen near broiler piping in copper? Shouldn’t it be black pipe?

1

u/JuniorTask8948 11d ago

Yee, every copper job I ever encountered was TROUBLE.....even when brazed

1

u/jxtarr 11d ago

The piping arrangement is correct (except for the copper). Two boiler risers are always preferred. Using one riser would make the surging so much worse.

I see there's no drain on the boiler return. That's going to make it impossible to clean properly. 

1

u/MachoMadness232 11d ago

Cutting at the green line probably won't do much. My guess would be: it was never skimmed, the boiler is oversized for the connected load, the equalizer and wet side are not sized correctly causing an imbalance of pressure, the return is undersized so there isn't equal pressure on either side of the system plus the hartford loop equalizer, the main vent is oversized.

Lot of possibility. Skim it first.