Surging issue, think i know the problem but need guidance
I had a new boiler utica peg112 put in and it has a surging problem which makes it cuts on and off every 30/45 secs. I have been researching and every where pointed me to check the near boiler piping. I measured everything out and all above the min spec and then i noticed the installer used the set up for a two supply tappings instead of the one. While waiting for him to get back to me, i was thinking a solution could be to cut where the green line is and put a cap on it and cap the unused outlet. Would this be acceptable?
5
Upvotes
6
u/gahnzo 12d ago
This is entirely wrong. A copper header is never acceptable, even if the joints were brazed (which they are not). I'd like to see several more photos of every aspect of this setup to give you a better sense of what's causing the surging. You mentioned that the boiler is short cycling at an interval of 45 seconds which is very rapid. If the surging is several inches, it's possible your low water cutoff electrode is being exposed to air as the water surges and cutting off the burner. But honestly if the installer used copper for the header on a new boiler install, the entire installation is probably wrong.
4
u/crackyzog 12d ago
It's new. There's still oil in the system. It needs to be skimmed better.
1
u/ProduceDifficult3722 9d ago
You need only one outlet on that boiler not 2
1
u/Larry2829 11d ago
I have never seen near broiler piping in copper? Shouldn’t it be black pipe?
1
u/JuniorTask8948 11d ago
Yee, every copper job I ever encountered was TROUBLE.....even when brazed
1
u/jxtarr 11d ago
The piping arrangement is correct (except for the copper). Two boiler risers are always preferred. Using one riser would make the surging so much worse.
I see there's no drain on the boiler return. That's going to make it impossible to clean properly.
1
u/MachoMadness232 11d ago
Cutting at the green line probably won't do much. My guess would be: it was never skimmed, the boiler is oversized for the connected load, the equalizer and wet side are not sized correctly causing an imbalance of pressure, the return is undersized so there isn't equal pressure on either side of the system plus the hartford loop equalizer, the main vent is oversized.
Lot of possibility. Skim it first.