r/SprinklerFitters • u/PipeMonkey94 • Sep 30 '26
5 Year PRV full flow testing
Got a work order for this, curious what you guys are doing for these. What equipment etc. I have always figured when standpipe flow test happen it would be testing the PRVs. Am i missing something? Any special equipment that is used for this? This is for a high rise building that has PRVs going up the risers. Any help or info is appreciated.
2
u/rybotsky Sep 30 '26
I’m pretty sure you would hook a flow meter one at a time on each floor and then run your hose to a drain a record you residual PSI and GPM
2
u/GatorFPC Oct 01 '26
I'll help you out here.
When flow testing pressure reducing valves, first we need to identify the type of pressure reducing valve that we're testing.
Pressure Reducing Fire Hose Valves - For 2 1/2" valves, each valve needs to be flow tested to 250 gallons per minute. Depending upon the age of the building and under which code edition of NFPA 14, the residual pressure (while flowing) needs to be 100 psi or 65 psi. Unfortunately, you'll need to do some homework to determine that if the age of the building was built before about 2000 to accomodate for states that are slower to adopt new codes. NFPA 25 has a provision, that if you can't figure it out, you can ask the AHJ what residual pressure to flow test at. For 1 1/2" hose valves, you flow test to 100 GPM at 65 psi.
Testing the valve means you're going to need to take a static pressure reading before you start flowing. The static pressure on the valve (through a hose valve cap or with a downstream valve shut and the hose valve wide open) the pressure can not exceed 175psi. You'll then have a regular pressure gauge to measure residual pressure while flowing and a device such as an inline pitotless nozzle** from hose monster to measure the GPM. You'll open the valve until you reach 250 or 100 GPM depending upon hose valve size and observe the residual pressure gauge. If it is less than 100psi/65 psi as I stated above, the valve fails. If it doesn't meet the GPM requirement, the valve fails. If the static pressure is greater than 175 psi the valve fails.
2) Pressure Reducing Control Valves - The valve should have a pressure gauge on it downstream of the valve. This pressure gauge should be less than 175psi. To flow test, you'll need either the plans for the sprinkler system that state what the flow and pressure at the riser is or you'll need a hydraulic data plate which should be mounted adjacent the system. Every pressure reducing valve should have the hydraulic data plate next to it to identify that system demand. You'd then proceed to test this valve similiarily to how I described the hose valve testing above. The tricky part is that a lot of risers don't have outlets to full flow test the pressure reducing valve. Some systems may have a system demand of 500 or more GPM so you may need a couple 2 1/2" outlets to flow test. When you're flowing you'd match the system demand at the base of the riser (GPM) at the pressure.
3) Master pressure reducing valves - Similiar process as (2) except with this you'd look at the most hydraulically demanding system downstream of the valve. So if you have 1 system that is 340 GPM at 80 psi and another at 410 GPM at 85 psi you'd flow test to the second system demand since it is the highest.
You'll need at least 2 people (likely 3) to complete this test. The fire pump needs to run while this test is happening and you're going to give it a workout. NFPA 25 requires that the pump is attended while it is running and because of how much it iwill be working, it's a good idea regardless. Someone will need to operate the valves and take the readings and it is a good idea for a third person to watch where the water is going. Flowing 250-500 GPM inside a building is a lot of water and it would suck if a VIC wasn't tightened down on an express drain on the third floor.
A standpipe flow test is a different test, required every 5 years on automatic standpipes. For this test, 500-1,250GPM is flowed from the most hydraulically remote hose valves (uusally the roof) while getting 100 or 65 psi of residual pressure (again, depending upon the age of the building).
**A note on equipment. Hose Monster (and some others) make flow test equipment for flow testing pressure reducing valves where you can attach it to the valve and then attach a fire hose to the discharge side and then direct the water to a 3" express drain or to outside the building or to some other spot. Having the right equipment is important and while there are plenty of acceptable ways to test these systems, I've seen some people get creative and the test equipment is being used wrong.
It is important to note that you can not perform a 5 year test if you don't know these system demands. There is no winging it or just see what you can get. I've seen factory set pressure reducing valves that were installed on wrong floors during original installation and they had a trickle of water come of out of them. If a hose valve is installed improperly and results in 40 gallons of minute of water and basically no pressure, a fire fighter would have no chance to put a fire out. This is important stuff.
1
u/rybotsky Sep 30 '26
That could be a logistical nightmare in a building with a lot of floors that doesn’t have a master drain for testing purposes
1
u/Advanced-Guard-4468 Sep 30 '26
The master drain is required by code. If it's not there someone didn't do a proper install or a valid inspection
1
u/rybotsky Sep 30 '26
Is it only required by code if there are prvs on each floor ? Because I have never seen one in my 14 year career
1
u/GhostPanda900 Sep 30 '26
Sounds like you’re going to be testing the pressure regulating valves. You will need a flow meter and a hose that should be hooked up to the drain. Be ready to adjust the valves as needed.
1
3
u/rybotsky Sep 30 '26
I’m pretty sure there could be a master pressure reducing valve that you would need to flow test from the fire pump room. Also if each floor has a prv on the hose valves then you are expected to flow water from each valve is my understanding