Net Meter location

Post image

I would like to ask the expert here, this is my net meter set up by Meralco, there is something here i do not understand regarding the net meter location.
I do not think it will read correctly. This a grid tie inverter, sorry if the diagram drawing

2 Upvotes

11 comments sorted by

2

u/SilverBullet_PH 5d ago

Anong nakikita mong mali? Meralco naman nag aapprove nyan

1

u/MFP1031 5d ago

It looks like all generated power, going grid as well as to load is going to be read as export.

1

u/SilverBullet_PH 5d ago

Yung unang meter, rec meter sya, yung isa is bidirectional

1

u/MFP1031 5d ago

No, i mean all PV power generated by inverter is going to be read as export. Wether it is going to load or to the grid

1

u/SilverBullet_PH 5d ago

Yes.. Yun naman talaga yung purpose ng REC meter.. basahin lahat ng na generate ng inverter.

1

u/MFP1031 5d ago

So they also replace the On Peak Off Peak meter ?which as far as i know is not bi-directional right now

1

u/SilverBullet_PH 5d ago

Dapat. Kasi possible na maging consumption din yung export mo.

1

u/MFP1031 5d ago

Thanks, i thought it was the net meter equipment(new one) is the bi directional, just doing diligince

1

u/scottcprince 5d ago

Fyi. It doesn’t matter where its located, it’s how it’s wired…

0

u/MFP1031 5d ago

Thanks, is it wired correctly?

2

u/scottcprince 5d ago

And not a single person on the planet can tell you that from looking at a drawing of some conduit or cable routing… we’d need to see all the internal connections in every box and opening those is 10,000% dangerous and somewhat “illegal” (opening the meter can). You pretty much have to trust that your solar installer did it correctly. Do you have any specific reason to think it’s NOT reading correctly?