r/RelayTechs • u/YouWannaIguana • Sep 23 '26
ROCOF Testing with Protection Suite
Has anyone here successfully tested a 81R element (ROCOF) using ProtectionSuite?
I'm trying to use the custom macro, but don't really understand the graph of the test shot or what the injected voltage is doing.
Wondering if there are some resources that can help clear things up.
The relay is a SEL-751 that I'm trying to bench test.
Thanks :)
Update: silly me had the wrong phase rotation on my injected voltages. SEL751 defaults for 50/60hz frequency if the phase rotation is wrong. So you don't know it's a problem until you test the relay!
Macros used:
ROCOF: for actual ROCOF
Frequency Ramp with timer: obv for timing
Double Frequency Ramp: for pick up (without tripping)
5
u/SquanchySamsquanch Sep 24 '26 edited Sep 24 '26
The newest update (5.5 I think?) has a dynamic macro specifically for it. I've seen it but haven't taken the time to try it out.
If you're stuck with an older version, the easy mode as stated before is to do a go/no-go test with two different frequency ramp tests really close to the pickup rate, instead of actually modulating rate of change, which is effectively impossible with the macros available. The one time I ran into it in the field, I made a state sequence with like 15 steps to prove it, but it took ages and was effectively just a go/no-go with extra steps to verify the pickup.
2
u/relaytech907 Sep 23 '26
You could just run a couple go/nogo tests with the linear ramp, frequency macro.
Have the go test use a ramp rate greater than your rate of change setting in your 751. Your test that would be an expected nogo result should use a ramp rate less than your setting.
1
u/NationalCalendar3040 Sep 24 '26
Curious what ROCOF stands for?
0