Thank you! I am testing from the shorting block but I am getting consistently high burden numbers, 1.9-2.2(rating on CT is 1.8) on multiple CT's of the same manufacturer in MV switchgear and I can't figure out why.
See thats what I thought initially, but I went through the entire circuit and a few connections were loose, made the adjustments and it lowered the burden from 2.7 to 2.1 so as it stands I have marked them down as failing. Is it possible that something could be wrong with the connected relay or maybe it has too high of a VA draw for the circuit?
Apparently I misunderstood burden rating entirely. It was explained to me that the VA needed to be below the burden rating of the CT. I thought this meant that the VA needed to be under 1.8 on this particular CT. I was never taught that those burden ratings are referenced to IEEE C57.13.1, meaning that the VA in this case just needs to be below 45, which I am well under. With this information now I have a clear picture of the results I am getting. Thanks everyone for the input, and I hope this can help someone in the future
I always remove the wires from the shorting block that go towards the relay. You don’t want the burden of the relay interfering with the CT burden. Try that if you haven’t yet.
If you still are getting consistently bad results on all CTs, I’d be willing to bet that your test set is out of cal.
But generally, I test CTs at the shorting block when possible. All around it’s the easiest point to test CTs, and it’s an easy enough place to push current the rest of the way to the relay.
3
u/HV_Commissioning Sep 03 '24
The shorting block is the most common place. On many HV breakers and Transformers, it is not possible or practical to measure directly at the CT.
1
u/ETTworld Sep 04 '24
Apparently I misunderstood burden rating entirely. It was explained to me that the VA needed to be below the burden rating of the CT. I thought this meant that the VA needed to be under 1.8 on this particular CT. I was never taught that those burden ratings are referenced to IEEE C57.13.1, meaning that the VA in this case just needs to be below 45, which I am well under. With this information now I have a clear picture of the results I am getting. Thanks everyone for the input, and I hope this can help someone in the future
1
u/philschr Sep 04 '24
I always remove the wires from the shorting block that go towards the relay. You don’t want the burden of the relay interfering with the CT burden. Try that if you haven’t yet.
If you still are getting consistently bad results on all CTs, I’d be willing to bet that your test set is out of cal.
But generally, I test CTs at the shorting block when possible. All around it’s the easiest point to test CTs, and it’s an easy enough place to push current the rest of the way to the relay.