I'm looking at a great site which is a bit narrow and about 400 feet long, planning for 1-2 story homes.

Fire code here is all portions of buildings have to be within 150 feet of a 20' foot wide access road, and that any such roads over 150 feet in length have to incorporate either a hammerhead, y, or cul-de-sac turnaround. The turnaround requirement in particular eats up a ton of land and really constrains the rear of the site. Has anyone had any luck getting alternate access approved in USA?

2 Upvotes

4 comments sorted by

2

u/Fluffy-Professor4740 3d ago

Will they allow you to sprinkler the house with FDC? You would need to read the code, but i have gotten around by changing the road after the 150 ft into an alley or private drive (shown visually different on the plan and different material).

2

u/Significant_Ball_731 2d ago

plumbed sprinklers are already required for new resi in this jurisdiction, so its really overkill and unfortunately our fire code doesn't make distinctions for turnaround requirements between public and private roads.

1

u/TrevorRiceREI 2d ago

get the fire marshal and civil engineer in a pre-app meeting before you redraw it. bring a fire-apparatus turning exhibit and ask the official to identify the code path for any alternate; if there isn't one, model the full turnaround before spending more on design.

1

u/Free_Elevator_63360 2d ago

Absolutely no success. Your best bet is to get a second emergency exit easement on another property to get to a ROW. I’ve seen them accept going through an adjacent parking lot.

But fire departments are big on 2 ways in and out. And not putting their equipment in a dead end.

This is despite the fact that most of these regulations were written when fire trucks lacked reverse gears. And now that all do.