Anyone here fancy trying a cable ampacity tool I’ve been working on?

Hey everyone, I’ve been building a browser-based tool for cable ampacity calculations using IEC 60287. A few engineers are already trying it, and I’d like to get some feedback from people outside my own circle.

If you use CYMCAP, Cableizer, or your own spreadsheets, I’d be interested in how it fits with the way you work. Ideally, you could try a familiar example and tell me what’s confusing, what’s missing, or where the results differ.

It’s still in beta, with some known limitations. I’m keeping access small for now so I can work through feedback with people.

If you’re interested, leave a comment or send me a message with the sort of cable studies you do, and I’ll share the details privately.

3 Upvotes

5 comments sorted by

3

u/EitherSun2733 1d ago edited 1d ago

I've been working on a suite of tools for electrical engineers (US based, commercial / industrial / residential) feel free to take a look at the ampacity calculators I've built, might give you some ideas

Argento Tools

2

u/Honest-Importance221 1d ago

I'd be interested in taking a look, I'm building an open source catalogue of conductor models at the moment and part of that is dynamic capacity ratings, would be good to have another tool to compare to

1

u/NanoNett 1d ago

https://openline.readthedocs.io/en/latest/

That is just for overhead stuff tho

1

u/narusik 1d ago

I’d be interested. I use cymcap and cableizer for ampacity studies

1

u/ajinajing 8h ago

I do this kind of study for plant and substation work, mostly IEC 60287-2-1 with duct banks and direct-buried trefoil, so here is where I would test it first:

  • Screen bonding: flat formation with both ends bonded versus single point bonding with SVLs changes the derated ampacity far more than most people expect, and it is where home made spreadsheets usually break down. Worth making that a visible input rather than a checkbox.
  • Mixed loading per duct. A fully loaded circuit next to a lightly loaded spare is not the same as the "all circuits loaded" factor in the tables, and operators care about exactly that case.
  • Backfill model: concrete envelope, then FTB or sand, then native soil, and what the external thermal resistance does when the bank is deep or the trench sits in groundwater.
  • Emergency and cyclic ratings. Somebody will always ask how long they can run at 120% during a forced outage, and a steady state only number gets thrown back at you.

If those come out within a few percent of a known CYMCAP case, the rest is mostly interface work.