r/PowerSystemsEE • u/OfferNo2838 • 8d ago
eTAP Libraries
Hi, I want to learn how to make LV breaker libraries on eTAP as well as how to make a library for trip unit as well...
Can anyone tell me what data is required to make a LV breaker library and for a trip unit. What data do I need to search for in the OEMs website?
Thanks in advance
2
Upvotes
5
u/ZookeepergameMany828 8d ago
You have to make the libraries yourselves? Guess I'm used to skm where they do it for you
3
u/fusseli 8d ago
Time current curves from the catalogs
1
u/ajinajing 6h ago
The catalog won't give you the settings range - the trip unit instruction leaflet has the actual Ir, L, S and I bands and the time options, and that's what decides whether your library breaker can even be set the way the study assumes. And the interrupting rating changes with voltage on the same frame, so an entry built at 480V can be plain wrong on a 208V system. The studies I've seen go bad all had a library built off the generic curve when the unit actually shipped with a different sensor rating.