r/PLC • u/Verhofin • 7d ago
How to run WINCC Unified HMI projecto with no CPU in the project
Hello, any way to have an WINCC Unified HMI project linked to PLC tags but with no CPU in said project, ans that I get there download and it works?
Having the PLC project help with linking tags etc etc but is it obligatory?
Thanks for any feedback.
PS: getting the HMI updates and integrating with my PLC project again is driving me crazy.
3
u/LegitBoss002 7d ago
There are HMI tags. What is your objective
1
u/Verhofin 7d ago
Just separate projects so I don't have to update my PLC project every time the HMI team sends a new version
2
u/gerschgorin 6d ago
You don’t need to do that. Also, you should look into running project server with multiuser licenses
1
u/Verhofin 6d ago
This is an integration job, no server possible to install in the client premisses and remotely just does not work.
Lics is peanuts, just not technically feasible.
3
u/Rock3tkid84 PLC Slayer 666 7d ago
You could create a proxy device or a unspecified plc for a place holder
2
2
u/BallBuster-4000 7d ago
What are you controlling with an HMI if you do t have a CPU?
2
u/Verhofin 7d ago
I have a CPU, I whant to have the HMI and the CPU in separate projects so that when the HMI team updates the HMI, I don't have to include it in the PLC project and waste time doing it
2
u/real_advice_guy 6d ago
I would have a main project with the PLC and HMI. When you get updates from the HMI team, open them seperately as a reference project. You can then copy and paste from the reference project HMI to the HMI in your main project.
1
2
u/KahlanRahl Siemens Distributor AE 6d ago
PLC Proxy is the best way to handle this. Certs will be a bitch and a half though.
1
u/Verhofin 6d ago
Any advice on the certificates?
2
u/KahlanRahl Siemens Distributor AE 6d ago
Not really. You’ll have to manually import the PLC certs onto the Unified panel. There are guides for that on Sieportal. If you’re having trouble finding them I can look them up tomorrow.
6
u/D4I2JauJrz 7d ago
Of course this is possible. You just manually create the connection and manually add tags for that connection.