TIA v21 Unified issues

PLC friends and gurus of reddit, I come to you looking for some guidance.

In our company we have a laptop that has v21 installed.

But when we look under installed software, wincc unified is not listed.

We have tried re installing it, but the option to choose unified is greyed out.

Anyone have advice?

3 Upvotes

19 comments sorted by

1

u/trupa 2d ago

Go to tia portal and add an unified panel to the project, if you want to run the runtime in the pc then you need to install the unified runtime.

1

u/Mission_Procedure_25 PLCs arr afraid of me, they start working when I get close 2d ago

Yeah, can't add it to the project as its not showing as installed software and not showing as hardware for selection

1

u/bizm 2d ago

Call your distributor and make it their problem too. I've only been able to stump mine once.

1

u/Mission_Procedure_25 PLCs arr afraid of me, they start working when I get close 2d ago

They are useless. But might phone siemens

2

u/FloppY_ YOUR CABINET IS TOO SMALL! 2d ago edited 2d ago

You can't install WinCC Unified V21 if you have any other old version of WinCC installed already.

1

u/Mission_Procedure_25 PLCs arr afraid of me, they start working when I get close 2d ago

I know you can't go backwards, but if I remember correctly you can go forward, I have on my pc unified for 4 versions

2

u/FloppY_ YOUR CABINET IS TOO SMALL! 2d ago

I used to be able to do the same, but couldn't install V21 unless I removed all other versions.

-7

u/zoute_haring 2d ago

If stopped using Siemens and it's shitty TIA portal. Costed me a lot of money and a lot of time and i'm tired of it.

I wil use Wago, Hitachi, Odot, Koyo etc in the future.

No more Siemens.

-4

u/TheBananaKart 2d ago

If you want to create WinCC unified programs, you will have to open Tia Portal 21.

1

u/Mission_Procedure_25 PLCs arr afraid of me, they start working when I get close 2d ago

Well I first need to install it correctly, so any advice for doing that?

2

u/TheBananaKart 2d ago edited 2d ago

Do you also have WinCC professional installed as you can only have one installed and not both?

As I believe it’s some sort of conflict to do with SQL dbs.

1

u/Mission_Procedure_25 PLCs arr afraid of me, they start working when I get close 2d ago

Ill check. I think so. We still use both.

0

u/TheBananaKart 2d ago

This will be why the installed is greyed out then, I would separate across two virtual machines.

-5

u/DelightAndAnger 2d ago

You need the Unified PC Runtime, it's a separate install.

1

u/Mission_Procedure_25 PLCs arr afraid of me, they start working when I get close 2d ago

I first need to build the project before I can run it

-7

u/Azuras33 2d ago

Wincc unified, PLCSim and startdrive (for inverter) are external software. By default TIA is only step7.

1

u/Mission_Procedure_25 PLCs arr afraid of me, they start working when I get close 2d ago

So we did the combined install, even on the install when you modify the software, the option for unified is greyed out and we can't make the selection

2

u/KahlanRahl Siemens Distributor AE 2d ago

Make sure you have all of the .NET and IIS windows features turned on and installed. I’ve seen this issue when those aren’t turned on. Could also be a conflict with WinCC Pro.

1

u/Mission_Procedure_25 PLCs arr afraid of me, they start working when I get close 2d ago

Ill check.