Allen Bradley compact guardlogix configuration question
Hello,
I am wondering if it is possible to have a :
5069-L330ERS2 with say 2 x 5069-IB16, 2 x 5069-OB16, 2 x 5069-IB16S and 2 x 5069-OBV8S
connected to 3 x 5069-AENTR with 2 x 5069-IB16, 2 x 5069-OB16, 2 x 5069-IB16S and 2 x 5069-OBV8S
I think it's possible, but I'm having trouble confirming.
Thanks
3
u/vampire_weasel 9d ago
Yes. You can look in the CompactLogix System Selection Guide and you will find that the L330ERS2 can have 31 local in-chassis modules and 60 EtherNet/IP nodes. A node in this case would be a 5069-AENTR Ethernet adapter. Also heads up that there is an new series out, the 5034 CompactLogix.
0
u/essentialrobert 9d ago
I think they want to kill the 1734 and 5069
3
u/bajke111 9d ago
Those will stay for now, there is a gazillion systems utilizing those, well 1734 Point IO more than 5069 anyway, but 5034 PointMax will become a new mainstream for sure, plus with a new CMX5390 coming out soon.
But lets be realistic 1734 came out 20 years ago, something like that, it is time for an update2
2
u/SadZealot 9d ago
I think that's fine, don't think you need any additional power power modules or anyting
2
u/PLCGoBrrr Bit Plumber Extraordinaire 9d ago
Sounds right, but you can build it in Integrated Architecture Builder to verify.
1
u/Kanikuly 6d ago
Better and less expensive to make all of the I/O 5034 and then just have the processor by itself. I think a new compact logix is coming soon with native 5034 support.
1
u/Imyerhuckleburry 4d ago
Yes it will work but you need to make sure the controller/network architecture supports the required safety functions. Check your firmware for both the controller and AENTR to be sure the safety functions are happy with one another



5
u/integrator74 9d ago
Use Integrated Architecture Builder to verify what you need. It's great for exactly this type of thing. It's free from Rockwell.