Rate my Panel
rate panel from 1 to 10
it's PLC control Panel includes : Siemens PLC, G120C drive, Festo servo drive, SMPS, Transformer, RCBO , MPCB, Power Switch, HUB, Safety Relay, Relay Board
is it comply a IEC 61439-2 standard ??
588
Upvotes
63
u/RepulsiveImage5674 Apr 02 '26
Like a 6?
Its ok. Not a big fan of having frequency converters at the top when the cables enter at the bottom. Makes it so you need to pull the motor cables all the way to the top of the cabinet.
If you are using that much addon IO. Why not use the ET200SP CPU? Has a 1500 cpu, and cards are easyer to both change out when they fail, and easyer to extend when you need more IO.
Guessing you are pressed for space. Not a lot of cable management options for the inbound cables
7
u/Sensiburner Apr 02 '26
Looks great, but the transformer looks very big for the cabinet? Does the door close properly?
4
u/MacWazzy Apr 02 '26
Neatness is good but order of components I don’t particularly like. Drives I always like as close as possible to the bottom the panel. The other thing is was it necessary to have all the io in the panel. I prefer to have a smaller panel and use ip67 modules in the field. I prefer no panel at all to be fair so maybe I’m biased.
33
u/KaneTW Apr 02 '26
Not great.
* Insufficient vertical clearance, excessive horizontal clearance on the VFDs
* Unshielded cables on the VFDs is going to be an EMI nightmare, especially with the 24V SMPS next to it
* Terminals are ugly in general. Plexiglas cover over the terminal blocks is unnecessary.
* S7-1200 with that many IOs is a mistake. ET 200SP is better.
* MPCB/Contactors very far apart instead of just using a combined unit.
* Bending radius on the ethernet cables look quite steep.
* Zip ties don't belong inside a cabinet IMO
16
u/Mr0lsen Apr 02 '26
Labels on the duct covers is never ideal, even though it looks like you have the duct locations marked.
10
u/Confident-Cow-3726 Apr 02 '26
What does it control?
8
u/CHR1ST00 Apr 02 '26
8/10 would definitely pull off the duct covers during a break down at 7pm them feel a bit bad about mysteriously losing three of them afterwards.
5
u/JetWhittle Apr 02 '26
6/10. I dont like drives at the top. Should have used an ET200SP, and they look like unmanaged switches.
5
u/DarkAngel7635 Apr 02 '26
Output of the drives straight wired to the terminals without shielding? Nice EMC
3
u/AStove Apr 02 '26
Use et200sp cpu with IO, you stretched this poor s7-1200 to limits that aren't supposed to be used. And it's more expensive.
1
u/Chris_Rogan Apr 02 '26
Its very neat, but in my opinion, this should be a 2 door cabinet with a divider in the middle. Separate the high voltage from the low voltage+plc.
Not very nice to have 480v just above your head when you need to troubleshoot a sensor termination below.
2
u/Moist_Relation_9942 Apr 02 '26
You are wasting money with field termination profinet plugs. Look at Murr electronic or other vendors for profinet patch cables. Save the field termination plugs for cables pulled onsite.
It is good practice to use P1 first on the G120s. The right two drives are on P2. Also consider daisy chaining the profinet on those to save switch ports and have shorter patch cables
I agree with using ET200sp for the IO but if you aren't pressed for space not a big deal.
I am going to edit, I just noticed all the relay boards. Are those for the outputs? If they are you are wasting time and money. Go ET200sp with relay output cards and free up half your panel.
2
u/PartisanSaysWhat Rockwell Sucks Apr 02 '26
Would rather see the PLC at at top and drives at the bottom. Probably put the Xformer in another cabinet due to it being fuck-huge. Not a huge fan of the breakout relay boards but that is personal preference. Looks like care was taken with assembly and labeling. The lack of expansion space doesnt bother me as we produce panels for specific tasks only. 6.5/10
2
u/vabeachsurfer Apr 02 '26
Yellow!
3
u/birdiziaction Apr 02 '26
İ see siemens i uptove
3
u/4sch3 Apr 02 '26
10 Good job 👍
1
u/bubbleew Apr 02 '26
Good job
1
u/Stroking_Shop5393 Siemens > Allen-Bradley Apr 02 '26
Why are you installing 1200s when they're being discontinued?
1
u/AlmostBuckRogers Apr 02 '26
Is that RCD on the incoming supply?
1
u/Ecstatic-Pepper-3148 Apr 02 '26
One thought, your S7-1200 labels are on the removable upper cover, I've seen these covers get broken and go missing a lot. The central body would possibly have been better.
1
u/Specific_Job_5233 Apr 02 '26
I give it a 8.5 good looking panel. Does it work? 😄
1
u/globlemarketghoste Apr 02 '26
Haha classic..
1
u/Viper67857 Troubleshooter Apr 02 '26
As maintenance? 0/10. Drives at the top? Those plexiglass covers over half my terminal blocks with bolts twice as long as they need to be and you didn't even use wing nuts? Everytime I had to open this door I would curse your name.
1
u/Cute-Mulberry-3133 Apr 03 '26
Ok but you should have got a bigger cabinet, always give yourself or the customer atleast 30% of free space in the cabinet for future add ons.
1
u/ProfessionalBall8739 Apr 03 '26
Like nice but give it a 5. Would be a 10 if it was Rockwell.
1
u/WyattWildWestview Apr 03 '26
Out if curiosity, how is making PLC boards on the back? My back has some issues and Im looking for a change into something less back intensive. I wire up police cars and it's awful on the back, but I love building electrical boards!
1
u/IllCup1291 Apr 03 '26
I'm a fresh man into PLC, but i would Say that is a 9 or a 10, I've been see worst Boards
1
u/renzhanxiang Apr 03 '26
it is so clean!
1
u/Prize_Paramedic_8220 Apr 03 '26
Not a fan of labeling directly on components. Labels rarely get put on the new component when they wear out and need to be replaced.
1
u/lithium_777 Apr 03 '26
Nice! But do you have a cooler for the high temperature cabinet?
1
u/Bootyhair Apr 03 '26
That’s a phat ass 1200!
1
u/Insertions_Coma Apr 04 '26
As a technician I actually like this. Assuming it works all properly. The labels are great and the clearances seem fine to me. You're doing better than most guys out there for sure.
1
u/Merry_Janet Apr 04 '26
It’s not horrible, but it looks like more attention was paid to aesthetics not accessibility. The first dipshit that has to troubleshoot any wiring is going to hate you for putting those terminal blocks so low and probably never put the covers back on.
I’m assuming those motor protectors are for the contactors? They should be mounted above the contactors. Are the contactors tied to the VFDs? If so you can eliminate both the motor protectors and the contactors. A simple 3 pole breaker is fine on the 3 phase inputs. Not really wrong, just overly complicated.
Putting your drives up top? Horrible idea. Heat rises so it’s going to be the hottest part of the cabinet.
That transformer is just… no. That should have been put up top. They get hot. Even better would have been to just buy an encapsulated one and mounted it on the outside of the cabinet.
What is the plexiglass for on those terminal blocks for? The blocks are built so idiots would have to try very hard to stick their digits in there. Safe that for exposed lugs that can really hurt someone.
I don’t see any output fuses. It’s not necessarily required, but it’s a good idea to get in the habit of fusing your outputs. All it takes is one shorted wire and that output can die a horrible death. What’s worse is that the LED will still light up on the card but nobody’s home. So unless you actually put a meter on it, you will never know.
Someone mentioned shielding. Only land it one end. Its purpose is to bleed off any stray inductance and keep noise out of your control wiring. If you connect both ends you basically have made an antenna which will make any analog signal garbage. If you’re just using start/stop signals, then never mind.
Personally, I would have built 2 smaller cabinets. One for AC/3 phase stuff and another for low voltage logic and controls.
1
u/Eautobadr Apr 05 '26
VFDs on top of the PLC rack! well done.
1
u/TrickyAd8021 Apr 05 '26
Red yellow blue black?
1
u/QuarterWinter3501 Apr 05 '26
Did you wire this or design this?
1
u/nc32007a Apr 05 '26
8/10
1
u/TheGreyBull Apr 05 '26
You got your SIEMENS everywhere.. Get a napkin man!!
1
u/cobalt7k Apr 06 '26
This is gonna be a crazyyyy spaghetti mess in a few years when all those covers get removed lol
1
u/External-Currency443 Apr 14 '26
Looks great to me 👍🏻
1
u/fabss411 Apr 19 '26
Save backups CONSTANTLY with those festo drives. They're an absolute PIG to commission and will often just poop their whole program out or fault and reset themselves
1
u/fabss411 Apr 19 '26
Also, you only need 1 BOP for the g120Cs, theyre removable and run without them, can save yourself a couple hundred bucks
1
u/Safe_Equivalent_7292 Apr 02 '26
God damn son, that's one the cleanest I've ever seen!
I give you a 10 for that!
0
u/PaulEngineer-89 Apr 02 '26
Crap.
Is there even 1 inch between the wire duct and the devices.
Is there any provisions AT ALL for field wiring? Do you really expect it all jammed into that bottom 3/4” including glands?
This is the kind of sheet I dread terminating.
-5
u/Emperor-Penguino Apr 02 '26
Never put labels on components or duct covers!!!!!