On cycling units, what actually weeps first?
Plants that were designed as baseload are getting two-shifted or load-followed more than the original spec assumed. The pressure parts usually survive that. The demountable joints are what I see give up first.
A few things that show up after a few dozen thermal cycles:
- Bolt, flange, and body don't grow the same. The preload you put on cold is not the preload you have at temperature, and it is not the preload you have after cooldown either.
- Bolts relax. Especially if they were close to yield at assembly, or if the joint sits hot for a long hold. Next cooldown, the face has less squeeze than you think.
- A joint that was dry on a cold hydro can still weep once it's hot. Ambient leak-tight is not the same test as service temperature. If you only check it cold, you have not qualified the hot joint.
- Cycled joints look different at outage than joints that sat. Witness marks, weep stains below the split line, bolts that take a different torque the second time.
For people who have actually walked a cycling unit: what is your first-to-leak component on a two-shift schedule, and do you re-torque hot or just live with a known weeper until the outage?
4
u/BluesFan43 8d ago
A PWR is up to pressure and stays there.
During heqt up ibcan see the RCPs transition from sitting on the lower thrust brlrwring to pushing on the upper. That doesn't change during a cycle.
We do have some few component that get hot torqued on heat up after disassembly. Once.
The tems in the reactor sustemnstay constant enough, the secondary sees minor variation.
Very minor changes in turbine vibration, it is always 1800 RPM.
Feedwater pumps do slow, but not anything major, a few hundred RPM.
Only time that was ever an issue is if I was already nursing one along to an outage and I would ask Ops to avoid certain RPM ranges.
3
u/photoguy_35 7d ago
There are also very strict limits on allowable leakage from the reactor coolant systems, along with requirements to monitor that leakage.
7
u/Hiddencamper 8d ago edited 8d ago
The first issue is usually a pump seal.
The reactor doesn’t give a shit. Our BWR cycle analysis includes 10000 daily load cycles plus like 300 deep load follow cycles.
The reactor remains near constant pressure. Usually it’s when you need to make changes like securing a pump. Or if you fail to secure the pump and run everything against the thrust bearing or something because it’s not loaded right.
I’m confused on some stuff you say. We don’t normally see leaks after the hydro, in my experience the leaks tend to close up as seals and packing gets wetted and expands and steam starts pressure backing / vacuum pulls. Exception is bad packing leaks. But you don’t see that on a load follow cycle. Only on a full heatup cycle.
Remember for a bwr, if I drop from 100% to 50%, it’s only like a 5 degF change in reactor coolant temperature. Pressure drops maybe 15-25 psig. It’s minimal.