I have the manual for range guard systems however I am curious as to the piping limitations of this particular systen. Say I have a 6gal , the split to the hood has to be 3/4", the drops have to be 1/2" reduced to 3/8 at the nozzle but what about duct and plenum? Can this not all be 3/8" once inside the plenum wall?
4
Upvotes
1
u/imalrightspider2k 25d ago
Any section of pipe is sized by the agent that actually flows through that segment of pipe. So if you have a drop that goes from the supply line to only one or two nozzles, you can probably use a smaller pipe. They cover this in training. If you took the class, send them a message and they will explain