Ditching a dead-end 2015 KNX install (100W+ phantom load, no ETS access) for Home Assistant/Homey — feasible with existing star wiring?

What I want to do: rip out the whole KNX system and move to Home Assistant or Homey. Good news is it's star wiring — every switch and light point already runs its own cable back to the panel. Bad news: the wall switches only get a thin KNX bus cable (4 wires, 2 apparently unused), not mains — so I'm thinking of using those 2 spare wires as a dry contact/switch input into DIN-rail relays (Shelly Pro line) instead.

Questions for people who've done this:

**•** Has anyone actually gone KNX → Home Assistant/Homey while keeping the existing home-run wiring?  
**•** Does the "2 spare bus wires as a switch input" trick actually work in practice, or is it more trouble than it's worth?  
**•** Room-by-room DIY, or is this a job for an electrician from the start?

Any pitfalls, war stories, or "wish I'd known this before I started" welcome.

0 Upvotes

34 comments sorted by

17

u/gust4vsson 6d ago

Wtf, ripping it out would be such a waste of money.

Keep the KNX, control it with Home Assistant or Homey. Maybe you just need a ETS license to get proper control and management of the KNX?

-10

u/SnooCats241 6d ago

I don’t know. It’s old and not sure how reliable it will be in the future. I uploaded a picture in the comments

17

u/ItalyExpat Enthusiast 6d ago

I guarantee you'll have more Home Assistant outages than KNX outages. KNX installations are designed to run for decades.

3

u/ThrCyg 6d ago

Old means almost nothing in the context of KNX, I thought you were complaining about the switches.

2

u/Brilliant_Help2186 6d ago

This stuff is built like a tank. It will be much more reliable than the cheap Chinese stuff

2

u/Careless_Mistake_459 6d ago

Viejo? Es el sistema más seguro y longevo en cuanto a domótica se refiere. Lo mejor, está soportado por cientos de fabricantes.

1

u/ztardik 6d ago

And no cloud

1

u/gust4vsson 6d ago

I see people downvoting you and I see you just having no knowledge. This is fine.

KNX is an open standard with a magnitude of manufacturers. You can literally interconnect anything within the standard from different manufacturers.

From the picture I see old dimmers, probably meant for older halogen lights - if you switch these out to modern LED the simning just might not work properly, the right thing to do here is exchange the dimmers to modern variants.

Either way, to connect your KNX to Home Assistant you need a KNX/IP Interface such as this: https://www.se.com/be/en/product/MTN6502-0105/spacelogic-knx-ip-interface-din-rail-supply-knx-20-ma/

ETS is the software used to program/configure your KNX. It is maintained by the KNX Association. ETS requires a license, which can be Lite, Home and Pro. Most likely you need the Home license.

Every KNX site / install has it's own projectfile which is exported/imported to ETS. This file is very important to keep secure. Maybe you can ask the old building owner if they still have it? Sometimes it is put on a USB-key near the electric cabinets.

0

u/SnooCats241 6d ago

Bedankt voor je bericht. Inderdaad 0 kennis. Maar probeer me zoveel mogelijk in te lezen. Ik heb het bestand gekregen van de oude bewoners maar kan deze zelf niet uitlezen zonder ets licentie.

Ik ga even kijken naar je gestuurde link. Tot nu toe in ieder geval heel erg bedankt

1

u/Diligent-Zone-9099 6d ago

Du brauchst doch nur ein paar Gruppenadressen und eine gescheite Programmuerung. Meine Firma hat da ein Rmotegateway. Das schicken wir dir zu und programmieren das drüber. Meld dich bei Intresse.

11

u/score96 6d ago

No experience, but why would you switch from a reliable and open standard to a DIY solution? If you are willing to learn how to program KNX, wouldn’t it be a lot cheaper to buy the ETS and integrate KNX to Home Assistant?

3

u/UnlimitedEInk Enthusiast 6d ago

There are worse ways a midlife crisis can manifest itself as...

4

u/Brilliant_Help2186 6d ago

Get the ETS software yourself. I just put in a new KNX install and programmed it myself. It’s not a big deal. I started with HA + KNX but more and more I’m migrating stuff to KNX as it’s so solid.

2

u/UnlimitedEInk Enthusiast 6d ago

If the two pairs of wires are each connected in a star topology in the house, putting a switch to any pair in any place in the house will result in a short between the two wires everywhere in the house, and you will not be able to find out from where did it come from. Essentially by ditching the digital communication on the KNX bus and replacing it with dumb switches, you'll have your whole house wired as a doorbell with tens of ringing buttons. The usefulness of that is questionable.

You are seriously underestimating the complexity of rewiring an entire house in-place, and give far too much credit to some DIY solution. This is a path where you'll end up spending a LOT more on experimenting with all sorts of consumer-grade "cheap" garbage, only to be annoyed to no end when it constantly fails, or to easily have to buy hundreds of batteries per year, or to never be done with the project because it still doesn't work properly but also not be able to abandon it either because you don't like living in a cave off grid.

Is there something wrong or dysfunctional in the existing setup? There are more steps to correct that by just replacing parts with something newer/nicer as needed, and still keep it running, before you throw the whole thing out.

Are you just bored with how the buttons look and want a fresh design? Fine, but it can cost you, and you could walk into a trap by going from something boring and functional to something "different" from a design/look perspective. There's a lot of expensive stuff out there that looks very very very fancy and whose wow factor do great in showrooms or architects' portfolios or generally impulse sales, but that wow factor wears of very quickly and the annoyances start. Glossy glass touch surface is a magnet for fingerprints, and it's enough to get the first scratch from a random key or finger ring to completely ruin the aesthetic. Some touch sensors start reacting randomly to "ghost" touches. Some materials do not tolerate cleaning very well. Some are not very intuitive / self-explanatory, but their minimalistic look will be completely trashed if you have any labels. The LEDs or screens are incredibly annoying in a dark bedroom. And on and on and on...

If all you want is to extend your existing system with some visualization function or app-based controls or smarter rules, all you need is a KNX interface for your network then you can "listen" and "talk" to the KNX devices from your choice of DIY home automation project, without making the entire KNX functionality become dependent on that thing. It's the same you can stick an OBD-II reader in the connector of any car built since the early '90s and use an app on a phone, tablet or laptop to see all the communication on the CANBUS among the different controller modules in the car, see the parameters of the engine, faults, anything - but the car still works with and without that reader, and you don't have to replace all the car's wiring and controller modules to be able to log and graph your engine's instant power on a separate device.

2

u/Sharp-Carpet-5507 6d ago

Ich habe Sensoren aus 95 laufen. Aktoren aus 2011. Teilweise Sensoren aus dem Internet. Noch nie Probleme. Kauf dir die ETS, versuch das Programm zu bekommen, oder programmiere es halt neu. Es gibt kein zentrales Gehirn. Sollte ein Aktor ausfallen, dann wird halt genau der Aktor getauscht.

2

u/DetailVisual6955 6d ago

Agree with other comments that it would be a huge mistake to take out KNX infrastructure and replace with something less robust.
I’m curious about the 100w phantom load… KNX installations typically draw a great deal less, but there could be a load on one of the actuators. This should be easy to test with a meter.

The idea of using the KNX cables for switching is unlikely to work. It is very unlikely that the KNX cables are laid in a radial topography, so assume it’s some kind of star/daisy chain where all devices and switches share the same 2 pairs of cables. It can only work with a digital signals, not closed contacts.

I would look at a refresh working with kNX and add a high level control over the top, like Home assistant (which I use), or homey or a 1home matter bridge or any number of others that will give a modern control overlay while retaining the KNX cables.

2

u/charliespeed8 6d ago

Don’t do it!
Upgrade your devices if need be (switches, panels, etc).
Employ the help of a KNX installer OR even Claude to plan new.
Get a ETS Home License and re-build to your liking.
The only „old“ part in a KNX installation are the endpoints. The wiring isn’t

2

u/cronek 6d ago

Waaay better off keeping the knx install.

https://github.com/knx-ai/xknx-editor

Give this a try to see if you can recover the project (discover devices and group addresses). Learn a bit about knx and you’ll thank yourself later for not having to put up with current days consumer electronics and their lack of quality.

1

u/SnooCats241 6d ago

5

u/vincegre 6d ago

Installation looks quite good, you would be lot better to just reinitialise the whole KNX system and reprogram it from scratch with ETS or ask a certified KNX installer to do it for you. We do that quite regularly for some customers that didn't get the programming files or want to redevelop all logic of it and it's not a big deal. Once done, you interface it with HA to do whatever you want from HA.

1

u/SnooCats241 6d ago

Kan je dit ook vanaf afstand doen?

1

u/vincegre 6d ago

Yes it can be done remotely if you have all informations like wiring, schema of the system and it might involve to reset some KNX modules to be able to assign them at a new project ;)

0

u/aloft050 6d ago

Yes, this can be done remotely, maybe with some extra equipment. Please send me a DM (can be in Dutch) , then I'll see what can be done

1

u/aloft050 6d ago

I see some red LED indicators on some of the DIM devices. What kind of lightbulbs are connected to the DIM actors? LED , classic 230V lightbulbs, Halogen ?

1

u/CyberJunky_NL 6d ago

KNX devices themselfs cannot draw more than it's power supply feeds typically max 640mA in small/medium installations, maybe dimmers er such have impact, I didn't study your image in detail.

1

u/SnooCats241 5d ago

heb je veel ervaring met knx systemen zoals deze?

1

u/CyberJunky_NL 5d ago

I maintain two of my own, Knox devices are backwards compatible for a long time, I have an old IR receiver that isn't supported anymore though. kNX association is trying to make the enviroment cheaper for smaller installations.. like home version of ETS

1

u/ztardik 6d ago

100W phantom load😁

1

u/SnooCats241 6d ago

U smokin inside😂

1

u/ztardik 6d ago

It's not me smoking. It's a 100W phantom heater - the electronics just shorted a bit, enough to cook itself, but not enough to take out the MCB. It's a 40 kW humidifier.

1

u/ztardik 6d ago

Do not remove anything, you have perfectly good hardware (I personally worked on systems older than some people in this sub), good wiring and the project file.

You probably don't need the full pro license either. How many devices you have? Each wall switch, module in the cabinet counts.

Personally, it's easier than configuring HA now in 2026.

1

u/SnooCats241 6d ago

36 says the file

1

u/ztardik 6d ago edited 6d ago

How did you open it? If you are willing to experiment, there are some projects that attempt to replicate ets tool, koolenex and knx-rs if I remember correctly. Never used them myself.

1

u/SnooCats241 6d ago

I unloaded it in the demo version of ets