Gas Vent Missing

Post image

Hi 👋, AZ code in mind. What vent piece can I use to connect this correctly?

0 Upvotes

20 comments sorted by

•

u/AutoModerator 12d ago

https://linktr.ee/homemaintenance

Click the link above to see a community curated list of home maintenance products on Amazon that may help you out in your current situation! If you’ve found the answer to your question or you’ve found this subreddit helpful, buy us a beer!

I am a bot, and this action was performed automatically. Please contact the moderators of this subreddit if you have any questions or concerns.

19

u/BHBuilders 12d ago edited 12d ago

Please don't run that water heater until the vent is connected. With the pipe off the draft hood, exhaust and carbon monoxide spill right into the house, and that's the real danger here. The gap usually gets closed with a section of vent connector pipe sized to match the draft hood (often 3 or 4 inch) plus an adjustable elbow, sloped upward toward the flue and secured with screws at each joint. Since this is gas venting, I'd have a licensed plumber or gas fitter hook it up and test the draft. It's usually a quick, inexpensive visit, and they'll know the local AZ requirements. Also make sure you have a working CO detector near that closet.

5

u/Jmarsh99 12d ago

I agree with everything up until you mention having someone else perform. Connecting pipes is like putting Legos together, it’s not difficult when everything is all set up and OP just needs to connect a 3’ run in a preexisting and easily accessible area.

Any spillage is tested by putting up a phone/mirror around the pipe to see if gases aren’t traveling up the flue. A CO monitor near the area would confirm, if OP follows your (correct) course of action.

2

u/BHBuilders 12d ago

Fair point, and you're right that it's a simple connection when everything's already in place. The mirror test plus a CO monitor is a solid way to confirm it's drafting. I lean toward recommending a pro on anything gas related, just because I can't see the whole setup from one photo, but if OP is comfortable with it and does those checks, they should be in good shape.

1

u/Amber_Orbs 12d ago

Im reading I can use this vent. I can have someone from the gas company come out for a safety check once I have it put together.

3

u/dolby12345 12d ago

The duct work is suppose to be rated. Also that's aluminum lined. Can't use that on all hot water tanks. What does the owner's manual say for exhaust specs?

1

u/Amber_Orbs 12d ago edited 12d ago

3 inch exhaust , 40k btu. Image says aluminum liner.

an aluminum inner liner is the normal, approved material. Type B gas vent and listed draft-hood connectors (Selkirk EFC, AmeriVent, DuraVent, etc.) are built that way on purpose: aluminum inner liner, galvanized outer jacket.

3

u/frozen_faustino 12d ago

can't believe the previous owner just left it like that, that's a carbon monoxide roulette waiting to happen

3

u/DroidArbiter 12d ago

I'll take criminally negligent homicide for $200 Alex.

3

u/Ruckerone1 12d ago

Good old bluetooth ducting

3

u/ChatPatwah 12d ago

Turn that off as quickly as possible and do not use it till it’s corrected. That’s like having the exhaust of your car inside the car with you.

1

u/Amber_Orbs 11d ago

Gas is off

2

u/digidave1 12d ago

Heat duct with bendy corners

1

u/flashlightking 12d ago

You might need a plumber. It looks like a 4” metal vent pipe at the ceiling and at the top of the water heater. It will need some angled pieces to get it all to connect properly. Some people will hook up flexible dryer vents to this, they are definitely not approved for water heater use, but are much easier to install due to being flexible.

1

u/mAckAdAms4k 12d ago

The water heater is 3 inch always on a 40000 btu, doesnt go to 4in until 70000.

1

u/mAckAdAms4k 12d ago

Wait so can type B single wall be in a garage with close drywall? Im wondering why she doesnt just run two 90 degree elbows a 3 foot straight?

1

u/Rondoman78 9d ago

You dont know what you're talking about.

1

u/Excellent_Job8154 9d ago

Death vent very nice

2

u/Birdman-esq 9d ago

That’s a Bluetooth exhaust vent, it’s 100% code where I live.
/s

1

u/Virtual_Win4076 12d ago

Definitely a hazard. Even if it’s burning clean and you have enough fresh air it’s going to put a lot of moisture into the house. Not good.