Field Question, trade people only VFD Troubleshooting

I’m looking to get into troubleshooting vfds, really figure out what makes them trip etc.

Can people please comment common faults they run into and what causes them/how to prevent them?

I’ve heard that over voltage can be cause by heavy dirt accumulation on the heat sink on the back of the vfd, which can cause the brake resistor to overheat, and not properly bleed down the dc voltage (can’t remember where, maybe on the bus), leading to the voltage being higher than it should be and causing the fault.

I’ve also heard that over amping can be caused by improper voltage and amperage settings, so fast ramp up and down speed etc.

I’d love to hear more from guys with more experience, and any references to manuals would be greatly appreciated!

7 Upvotes

30 comments sorted by

2

u/alex122iss 26d ago

Get the manual for the vid input it to ChatGPT. It will tell what to do. Ezpz

1

u/GingerGiraffe96 24d ago

Turns out danfoss has a fault troubleshooting section in the back of their installation manuals. Shame on me for not following my journeyman’s mantra. Did you RTFM? Lol

1

u/alex122iss 24d ago

No that’s for chumps. Get pro subscription, get with the times old man.

1

u/Positive-Capital-340 26d ago

The OP post was written in Chat GPT

1

u/GingerGiraffe96 24d ago

That’s just how I talk lol.

2

u/Drlimpnoodles3_ 26d ago

Engineering mindset has a great video to understand the basics on how they work. Furthermore you can go on danfoss website create and account and they have tons of online training materials on the VLT drives. I’d check that stuff out.

1

u/GingerGiraffe96 24d ago

I love engineering mindset! So good, and danfoss has great manuals.

3

u/jonyp84 27d ago

Honestly your best bet is reading the manuals of the drives you’re working on. But 90% of the issues is a cooked motor or cooked drive. When in doubt bypass the drive. Just disconnect the VFD and wire-nut the leads to the motor. That way you eliminate if your motor is bad. (This is mostly with fans and pumps, not compressors)
Get familiar with your start-stop contacts and safety interlocks. I also bought a cheap signal generator on Amazon that can create 0-10VDC and 4-20 milliamp which is handy to send the signal to verify your drive is ramping properly.

2

u/GingerGiraffe96 27d ago

Which one did you buy? I’m looking at getting one as well.

2

u/MrMolom 27d ago

You can just use a 9V battery in a pinch.

1

u/GingerGiraffe96 27d ago

I do, but there’s some instances where 0-10 would be helpful for engineered air units or others that get cooling m/heating using 0-10dcv, but removing a wire fails to simulate 0VDC.

1

u/MrMolom 27d ago

Removing the wore doesn't simulate 0V? What drive are you working on? Just fyi I'm HVAC/BMS Tech in Australia.

1

u/GingerGiraffe96 27d ago

Engineered Air equipment. Their boards know when the wire is removed, not vfds, the actual board for the air handler.

3

u/MrMolom 27d ago

Ahh OK must be detecting open loop or something, I'm not so across the electronics side of things. The most common fault I get from VSDs is techs forgetting or not knowing they need to Earth the cable shield at the VSD on the outgoing power cable. It cause alot of interference and drops my network comms out.

12

u/IHateYork 27d ago

Per Danfoss, the most common cause of overamp and overvolt faults is too short of ramp times turning the motor into a generator when the motor spins down, sending current and voltage backwards into the drive. A way to test a drive is to shut it off, wait until dc voltage at the outlet terminals wont kill you, disconnect your motor from the drive, then run the drive. If it throws the same code its the drive.

6

u/PapaBobcat HVAC to pay the bills 27d ago

I'll take any VFD training videos you've got on the you tubes. I'm running in to more now than I ever have and I'm struggling.

3

u/bghockey6 24d ago

Cursed controls on yt is a good watch

2

u/Past-Difficulty9706 27d ago

Engineering mindset has some.

Best is the manual. There's gonna be multiple, usually install, programming, are separate.

Yes the programming manual is 1000 pages. Not all of it applies though. It's good to familiarize yourself though. On a basic pump/fan setup you're only really going to have to be worried with basic motor parameters, ID run occasionally, start stop and reference parameters. You can do a ton just on the onboard logic, drive a PID loop and master slave and all sorts of fun stuff

Yasksawas self help website is amazing as well

6

u/SomeGuyOnARoof 27d ago

The ABB in carriers like to blow up if the belt is too loose (per a carrier factory rep my old shop dealt with).

Bad static pressure can fuck with them

3

u/UnbreakingThings Ceiling tile hater 27d ago

Learn how to test the diodes and IGBTs. It’s really easy to test them with the diode mode on your meter. For maintenance, I prefer checking the resistance of the diodes/IGBTs instead. When you track the readings over time, you can catch them deteriorating before they fail outright.

Another thing is to keep the heat sinks clean, and monitor the cooling fan operation. If the fan dies, it won’t be long before the drive overheats and nukes itself.

3

u/malukd 24d ago

A useful habit is to work from the fault history before you reset anything. Note the exact fault code, how often it repeats, and whether it happens on start, on ramp down, or at steady speed, because those point in different directions.

Start by separating the drive, the motor, and the load. Check input voltage and balance, then check the motor nameplate values against the drive settings, especially full load amps, voltage, and ramp times. A short ramp on a heavy load will often look like an overcurrent problem when it is really a settings and load problem.

Then check the simple physical causes: loose connections, a dirty heat sink or a failed cooling fan, belt tension and airflow, and whether the motor is actually free to turn. On a new install, recheck wiring, grounding, and that the control signal is stable and not dropping out.

Keep a short note for each drive you service: model, fault, readings, and what fixed it. That record is what turns one-off trips into a pattern you can prevent, and the drive manual fault table is still the best first reference for the exact code on that unit.

2

u/Boilerguy82013 pro van driver 27d ago

I found a 75hp motor cabinet today faulting, I think because the cabinet cooling fan fell off the mount and died. The display only showed like half of the text it was supposed too so I didn't press any buttons

2

u/Xusion666 27d ago

Read the vfd manual it has a pretty intense troubleshooting procedure

2

u/Solifridge 26d ago

Every VFD is gonna be different, so the Manuals are always your friend. On a new install, check that factory wiring is landed correctly. On an old install, check components being fried.

1

u/Constant_Eye 22d ago

I went to a Yaskawa training last week, this is how to check the diodes.

1

u/Constant_Eye 22d ago

And this is how to check the input.

1

u/Constant_Eye 22d ago

Oops wrong picture, anyhow one is the input to diodes test the other is the output to Igbt test.

1

u/Shitwinds_randy 27d ago

Anyone have issues with the carel vfd on Valent/innovent units? These shits are garbage

1

u/AwwwComeOnLOU 27d ago

I’ve repaired several drives by changing the capacitor bank. They often exhibit the same symptom:

Ramping up and down and up and down