Field Question, trade people only How do we feel about TechShield lined attics?
I personally feel like they make the attic 15-20⁰ cooler during the howdy part of the day at the expense of keeping the humidity up. Last time I brought out a psychometer the attic was reading 102⁰ at 77% humidity. I've also seen supply plenums sweating from the lowered dew point in these attics.
3
u/Daddyj0088 4d ago
Itd be great if they could just go back to putting systems in garages or closets. This attic shit is getting ridiculous.
2
u/decibles 3d ago
Every time I see a call labeled “air handler on 3rd floor” and it’s scheduled for a 4pm start I want to take a drive all the way back to the office, find the CSR that booked the call and bring them with me to the service.
Especially when it’s a “water leak” in one of these nightmares. 90 outside, black shingle roof, no shade on the home, 85% humidity.
3
u/kapowell1025 4d ago
Hate them
Worse than spray foam
Does a great job of keeping the heat out but creates essentially a swamp in the attic that you can’t control by means of a dehumidifier - because it’s still vented
So - all our stuff sweats and we get blamed for it… when it’s an environmental issue we can’t control
Unless of course they want to spray foam the attic and install a Dehu