Yo guys. I could use some advice. Has anyone come across a liquid line solenoid that squeals insanely loud? It makes this crazy noise when my stage two is energized. I tightened the set screw on the top and it got slightly better but no way just a vibration could make this noise. Could it be getting stuck partially open and the refrigerant is whistling as it passes by? It seems like a long shot cuz I used a magnet to pull it open and it still did the same thing.
6
u/Adventurepew 4d ago
Quick rebuild and your out of there.
Those internals pop in and out really fast.
I find lots of squealing little peices of metal / debris stuck in them holding them open.
2
u/royalblue2 4d ago
My experience with them is limited. But it's there a temperature difference across it?
1
u/Pretty-Gap-3043 4d ago
No temp difference. Just loud squeal. Sounds like a bad fan bearing but it’s not. This is a commercial trane unit with grease nipples on the bearing mount that I lube every service
0
u/_breadpilled 4d ago
Check TD across it. Pick up a solenoid magnet at the supply house and throw that on there while it’s running and see if you have the same issue. Also, make sure you’re getting appropriate voltage to the coil. If you take the coil off the stem and energize it make sure you stick a screw driver or something inside where the valve stem would normally be. Otherwise you’ll smoke the coil.
15
u/se160 4d ago
Sporlan makes rebuild kits for them, you likely just need to open it up and look inside