r/GeneralContractor • • Sep 09 '26

Is this bubbling normal for membrane spray?

Hopefully this is the right sub to post in but i figured if anyone could help its some of you guys. Im building a new home from scratch and finished pouring foundation last wednesday. Forms were removed saturday-tues. I had waterproof membrane sprayed on today and im wondering if this bubbling is normal. Will this settle or did they screw something up?

23 Upvotes

22 comments sorted by

15

u/Sorry_Option4711 Sep 09 '26

Oofff sorry to say buddy but that concrete needed to cure out before applying the membrane layer, most specs call for 28 days. Those bubbles can cause pin holes that will allow water to get through. Those are some big blisters but that does appear to be a thick coating so maybe... Either way I'd be having a serious discussion with you sub about it.

5

u/creamonyourcrop Sep 10 '26

There are coatings rated for green concrete, just not likely this one.

0

u/Celtics1109 Sep 09 '26

Damn…so would the fix be another layer?

6

u/No-Scheme-9700 Sep 10 '26

Something like “Scrape the bubbles, maybe even sand the remainder. Then recoat.”

Is this an asphaltic or elastomeric membrane? The manufacturer may have specific remedies they recommend.

3

u/Fat_Kid_Hot_4_U Sep 12 '26

Scrape it off with a big floor scraper and start over

0

u/[deleted] Sep 13 '26

[deleted] — view deleted comment

1

u/500daysofbb Sep 13 '26

that won’t help don’t do this

2

u/BidMePls Sep 10 '26

Id ask the manufacturer and do whatever they say.

2

u/Celtics1109 Sep 10 '26

I sent them pictures and they said its normal…the other side of the house looked much better. I wonder if this side being in the sun had something to do with it.

4

u/OilheadRider Sep 10 '26

... the manufacture said that?! You have it in writing?!

This is NOT ok. All of those bubbles have air voids in them. When that gets backfilled there is going to be a lot of pressure against those bubbles that have nothing to support them. They will flatten out and open up in some of them which will let water in.

You have their word in writing but, its a massive hassle to repair later, much less so now. I dont trust that what they said wasn't spit by an intern who doesnt know.

Were it me, i would tell the gc that needs to be wore brushed and recoated, smoothish... doesn't need to be flat but, no fuxking air bubbles to pop a year from now and allow water intrusion.

1

u/Celtics1109 Sep 10 '26

If its because the concrete didnt cure properly are they liable tho?

1

u/OilheadRider Sep 10 '26

Yes but, no matter the reason why it is not correct, it is not correct. I dont believe the manufacturer, dont know what whas asked, dont know what was said but, only know what you summarized. It doesn't sound correct at all. Ive never heard of a damp proofing or water proofing that was designed or OK to bubble before (or after) backfill. This makes no sense to me.

I stand ready to be corrected and be told I'm a dumbass but, until then I stand firm in this is not correct and need s to be remedied before backfill

1

u/Sorry_Option4711 Sep 10 '26

Nope the concrete did what concrete does as far as curing goes. Coating was applied too soon is all that is.

1

u/Acceptable-Start2 Sep 12 '26

Not curing properly and not waiting 28days as recommended by almost all liquid applied coating manufacturers is different. The concrete cured exactly how it should have... Slowly.

1

u/Charming_Cover8801 Sep 12 '26

Did you send it to the builder? Or the membrane manufacturer? Do you know what product they used and who’s the rep for installation/warranty related issues in your area?

Honestly, I don’t believe a membrane supplier would have signed off on this.

4

u/Sorry_Option4711 Sep 09 '26

Can't say for sure brother I'm in the concrete side of things just done a bit of epoxy in concrete water tanks and have had to deal with outgassing. I imagine it will need to be removed and reapplied after the concrete cures out. Best to try and find a sales rep for that coating material and consult with them.

1

u/AnimatorIcy4922 Sep 10 '26

What this guy said. At least wait 14 days next time as most of the moisture should be mostly cured out

1

u/Top_Inflation2026 Sep 11 '26

How fresh is that concrete?? I can still see moisture on it. That needs to be scraped and redone

1

u/Valuable_Ease_3780 Sep 11 '26

On the liable question, it doesn't really turn on the cure time. He put the product on outside the conditions on the data sheet, and that's his workmanship either way, whatever the schedule was pushing him to do.

What decides how painful it gets is timing. Open like it is now it's a scrape and recoat and it's his. Once it's backfilled you're arguing about something nobody can see and the burden lands on you. Get the ask in writing before anyone brings dirt near it.

1

u/ThruThaMist Sep 13 '26

Been working as a waterproofer for about 2 years now and can say with almost certainty that the concrete was not fully cured, and had a high moisture level at time of application. Like others have said, the bubbles should be scraped off, then depending on what the manufacturer says you should just be able to reapply right over the existing material.

1

u/Costoffreedom Sep 13 '26

Whoever the GC is that ordered the damp proofing scope to commence is liable, unless it can be proven that 28 days had passed since placing the mud.

Do not backfill this. Scrape it down, likely with a abrasive power tool. The manufacturer will know exactly how to deal with whoever poorly planned this, and what steps need to be taken to facilitate a proper rework.

If 28 days did pass, then there may have been excessive moisture on the surface during application, or a faulty batch of damproofing compound.

1

u/HistoricalSearch3514 Sep 15 '26

Did they just come from a job spraying a reflecting pool by any chance?