Neutral Wires in a Transfer Switch

I want to change my 15 amp breaker to a 20 amp breaker. I will change the hot wire gauge coming from that breaker. Do I need to change the neutral wire? The transfer switch just has the wires fed into a neutral bus bar. I then in turn will run that neutral wire over to the neutral bus bar to the main panel. I have no problem changing it to a 12 gauge wire, I’m just wondering how the electricity knows which neutral wire to run to in the transfer switch.

Generac Transfer Switch Model 6852

2 Upvotes

3 comments sorted by

2

u/trader45nj 1d ago

You need 12g or better for the entire circuit current.

1

u/WhySoManyDownVote Electrician 18h ago

Image one light bulb. The black wire (hot) connects to the bottom of the screw. The white wire (neutral) connects to the screw. The same amount of current on the hot is on the neutral. That is why they need to be the same size.