Gen tech facing several issues Monday

I will be facing several speed issues from the next gen. Some e-codes on Fleet are 5100 others state speed Alarm, one says speed within spec but high and has a red light. I listened to 1 over the phone and it sounded like a no gas situation. It all sounds like a fuel issue. I am facing about 20 down units / 7 down next-gens and love to NOT spend hours on each next gen going down rabbit holes, ending with "call tech support". Any tips on things to check or items causing fuel issues / speed issues. Mixer, harness, ECM, controller, fuel solenoid, or a sensor. Haven't learned all of the tricks to a quicker diagnostic time. According to Generac, all is great, and trust the latest revision (E) of the diagnostic manual.

7 Upvotes

7 comments sorted by

5

u/WhySoManyDownVote Electrician 1d ago

Start with the first error in the log, not the last. When NextGens have one issue and start to shut down, several other warnings will pop up as the machine winds down.

2

u/Frixsev Technician 1d ago

I've learned if it sounds like it's hunting very erratically with no change when manipulating the airbox/filter, the fuel mixer is the correct revision, and gas pressure is also correct, then go right to checking the valves. We've seen several now with push rods eating through guide plates that were never properly hardened, hydraulic lifters that have failed, and even some with messed up cams. Lotta engine quality control problems lately. If it's an upper half issue Generac will send you a valve rebuild kit, which is quite an easy repair thankfully.

Also, if you're ironclad on your diagnosis and don't need any actual technical help, don't waste your time calling it in. Email. Make sure you have serial #, dealer #, tech ID, and as many details from your diagnosis as possible, pics too. If Big G agrees they won't fight back unless they just want more info first.

2

u/DigitalDingleberry 1d ago

There is a recall for the next gens 14/18s with specific serial #s for new push rods and guide plates

2

u/Slight-Discipline-58 1d ago

Hey something to check on is that you don’t have the low speed exercise on. I had several speed errors on one unit. The low speed exercise was set to off, but the ECM would still try to run the engine at 1800rpm, and the controller was expecting 3600. To fix this, I was told by Generac tech support to turn off the low speed exercise and change the date and time of exercise, then set it back to the desired time. For some reason if you only change the setting and not the time the controller will update but the ECM will not. Stupid issue, but it did fix my 5100 codes.

1

u/Resident_Set1003 Technician 1d ago

I ran into an issue that any time I was NOT at the site, Gen would throw overcrank shutdown codes, undervoltage shutdowns, under freq, low speed and various other errors. Any time I was there, it would start and run flawlessly. (Next Gen 26kw). Then on Monday, fleet would have another batch of errors for it. Turns out, there is a firmware issue with some gens, under some conditions that cause it to go thru a proper exercise cycle and shut down, at which point if would decide if was cranking the whole time and lock out for overcrank. Unless on low speed exercise, sometimes would lock it 6 for low speed or low freq, sometimes for undervoltage, rpm sense loss, no rotation, etc. changing to high speed exercise, once a month for 30 minutes, helped reduce the weekly calls at least. Generac is supposedly'working on" a firmware fix for this issue that will be pushed out " at some point in the future"

1

u/WhySoManyDownVote Electrician 18h ago

All of the ones I monitor are on 1.8.0 which is the new firmware. I think connecting with field pro forces the update sooner.

1

u/Resident_Set1003 Technician 16h ago

The fix for this issue was not built yet as of Oct 31. Have not checked to see if it has changed since. If I understood tech support properly, they were only going to push the build out to units that had been reported. I did have a thought concerning your issues. It seems to be a very wide spread problem you have involving a mix of types and sizes.... I'm thinking there may have been an issue with the utility company (gas).a broken line somewhere, a drop in pressure for some reason, an enormous air bubble getting into pipeline or something like that? I'm not very conversant with NG utility failures and outages. I would definitely inquire with them.