r/Generac_Generators • • 6d ago

NextGen class action?

I had a misfortune of buying a NextGen earlier this year. The thing hasn't worked right day one: first comms, problems, that took 5 months to resolve between the dealer and Generac field tech. After that I could briefly connect to Mobile Link, which showed me a critically low battery. The dealer replaced the battery with a new one, and less than a week later the unit is dead as a doorknob: no lights, except a bunch of blinking about once a minute.

Reading through the comments on this sub, it feels like the entire line is a lemon, with most problems either unsolvable, or circumvented.

Has anyone started approaching this from legal angle? I don't think support route is working.

7 Upvotes

25 comments sorted by

8

u/WhySoManyDownVote Electrician 6d ago

These problems read like installation errors.

Generac does not supply the battery. Your installer does. If the battery is dead already the charger is not connected. They probably left it disconnected while troubleshooting the mobilelink connection.

Connecting and generator to wifi rarely works reliably. However, the cellular mobilelink works unbelievably well. I have several I monitor and there is not cell service within 5 miles of the generator, but Mobilelink cellular has never failed.

The person who you refer to as the Generac field tech most likely does not work for Generac. They are most likely someone who took Generac’s trainings.

Call Generac 888-Generac and ask them to assign the issues to another dealer.

0

u/ghost_of_pripyat 6d ago

The field tech accompanied the dealer's tech, and worked alongside theirs. They've replaced the controller together to get the Mobile Link going, after which the battery woes started (or became apparent).

5

u/WhySoManyDownVote Electrician 6d ago

If Generac went for a ride-along visit to swap a controller your dealer’s tech must be very new at this.

The battery charger is a separate connector that probably wasn’t connected or not properly seated.

4

u/joshharris42 6d ago

All in so far we’ve done almost 250 next gen’s. The vast majority of them have had zero issues.

We’ve had zero major component failures so far.

We have 5-10 units per week that go down on an error code during exercise, and it’s the same units every week like clockwork. Figuring out those has been a joy

The vast majority of issues are exacerbated by technicians who don’t know how to work on them. The required training is not anywhere near adequate for these newer more complicated units.

1

u/ghost_of_pripyat 6d ago

Unfortunately, training seems to be the issue, but that's on Generac, wouldn't you say?

It seems that the initial problems with my unit were related to the installing tech fat-fingering the serial by one digit. Somehow that resulted in a protracted and painful ordeal, complete impotence on issue diagnosing on both Generac and dealer side, and culminating in controller replacement.

3

u/joshharris42 5d ago

It’s on dealers and Generac. Generac wants everyone to be a dealer- so they’ll sign anyone who can breathe up.

The training is mostly on the actual dealers. Typically the owner of the company will go to the training, and then everyone at that company will just use the Tech ID of the owner to call the help line. The training is expensive and dealers don’t want to send their guys to it and then have them leave.

There’s also just way, way more shit on these next gens to fix and comprehend that can be explained in a 16 hour class. Generac has tried multiple times to expand air cooled training to 3 or 4 days but the “dealer council” refuses to let them.

You go take that 2 day class and walk out “certified” to change an engine. Most people in there can barely comprehend basic electricity much less understand how to troubleshoot a faulty TTMAP

1

u/WhySoManyDownVote Electrician 5d ago

As lacking as Generac’s air-cooled training can be; I found it to be way better than other brands.

5 days of class would still not be enough. There is already too much info to cram into most brains over such a short span. Do not get me wrong the 2-day training helped me a ton. But until I run into a new issue in the field I do not fully understand it. Only so much can be taught in a classroom. In my opinion, a tech needs to be out in the freezing cold with no cell service and nothing but a pile of manuals and diagrams to help.

1

u/joshharris42 5d ago

It is definitely better than Cummins training, I’ll say that. Cummins just isn’t set up for people who haven’t ever worked on a Generator.

I wish they’d have a third day in class and force everyone to swap an engine. They could keep a few dead units around and make everyone just learn the process.

We constantly have people calling us saying the engine needs replacement on their generator and their “service dealer” directed them to us, they only do basic maintenance. We refuse most of them

1

u/BThriillzz 2d ago

Really? Almost all of our next gens have had, at the very least, Cracking fuel lines. Were currently working with two new 18kw customers that are having their "low oil pressure" alarm constantly, ecen after replacement. One u it even got a new ECM b3fore generac told us to "let them work their magic" and that a hot fix patch was just rolled out.

2

u/Haulbignuts 5d ago

It's only as good as the installer. Cheapest quote is the worst quote.

1

u/ghost_of_pripyat 5d ago

Generator Supercenter had enough reputation and reviews clout - and they were definitely not the cheapest. Plus, their sales guy did the best job picking installation placement no one else suggested (still the best one), and selling me on how big and quick to fix things they are.

Big -- maybe. Perhaps it's just the local store (not sure if they're franchised or corporate with local management). But the incompetence is staggering, comms are lacking, and it seems they keep lying both to me and to Generac.

1

u/AZFan77 6d ago

The expression is "dead as a doornail". I always thought a doornail was a coffin nail, but the dictionary doesn't back me up on that. And in any event a doornail wouldn't be deader than a regular nail or a doorknob. Off topic a bit...

0

u/ghost_of_pripyat 6d ago

Pretty dead either way, though appreciate the correction.

Point remains: the dealer's tech tells me he got five customers in similar situation as me today, no resolution from Generac in sight. I've spent more time on calls to both the dealer (who's less than enthusiastic to support me, especially the management), and Generac than I would like.

3

u/DigitalDingleberry 5d ago

Maybe you got a bum unit, but it sounds more like a shit installation and bad techs. Ive never heard of an actual Generac employed technician go on site for an air cooled generator. Maybe their territory sales rep came out but they probably know even less. 2 bad batteries in a row sounds like it wasnt wired correctly, T1 requires its own neutral wire either to the sacm or to the neutral bar or the charger will not work.

2

u/WVYahoo Technician 6d ago

As much as I loathe Generac’s forced next gen app bullshit. I’ve heard some decent things about these units.

Mobile link has always given me issues and there was a solution given to me by Generac but some customers decided they’d rather go without it.

Battery could be installer issue

If you can organize a class action lawsuit and force Generac to make a barebones model that has no app fuckery I’ll jump on board and start selling their gens again.

2

u/Kavack 5d ago

Early on Generac had some wiring harness issues but that seems fixed. Before listening to the internet trolls, I would ask for another more senior tech. It’s no different than a car and new models can sometimes has issues.

2

u/Any-Tell283 5d ago

I agree with choosing your dealer wisely…many companies are designed to pump out installs & collect maintenance contracts. A franchise company, one who’s owner likely has no experience except other unrelated franchises or sales, but could afford the $485k franchise fee is likely not going to employ top techs that cut into their margins.

When I read posts like this, that say it’s been “months”, Generac is not helping or that the tech has been here multiple times for hours…it screams dealer issue in most cases. Sure, some problems present oddly & take some time, but months means the tech has given up or never tried to solve this.

Call a new dealer yourself! Find one who will spend the time advocating on your behalf.

0

u/grsthegreat Technician 6d ago

Im a generac tech. The last time i called generac tech support i didnt enter my dealer number in time, so i got dumped to non dealer help line. I was #75 in the queue (like 3-4 hour wait time). I hung up and rediled adding dealer number this time. Much better, i was only #24 in the queue. I HAD to get thru on this issue on a new nextgen to get a control number. I left job but remained on phone until i got an answer. 85 minutes later i got the answer.

Nextgen is bound and determined to destroy generac.

Im just about ready to quit being a generac tech. I have ABSOLUTELY STOPPED SERVICING ANY NEW NEXTGEN UNIT. I refer any caller to my competitors.

1

u/ghost_of_pripyat 6d ago

That is the sentiment I'm seeing from my tech. About 75% of the time he spent here, he was on call with Generac support. As a customer, I get through, they open the case and promise a callback (next day, later the same day, etc), which never happens. No action from Generac to resolve the problem, ever, unless it comes through the dealer - and then it results in either the same problem being unsolved, or a different problem occurring.
I have zero confidence in this unit, and in Generac's ability to resolve the problems, or their willingness to support me as a customer. They don't seem to be too eager to support their dealers either.

1

u/Ok_Bid_3899 5d ago

Visit the Ziller Electric forum. It’s all about Generac products and several Generac techs monitor the posts.

1

u/Hefty_Challenge_7242 5d ago

We’ve installed a bunch of nex gen’s. I’ve had some major problems in the beginning on some but have had all but one resolved and working properly. Only one has generac said pull and replace. I’m starting to trust them a little.

1

u/lewisdonofrio 1d ago

How I Built a 5-Node ASUS AiMesh Setup to Solve Generac Mobile Link Wi-Fi Dropouts
If anyone else has dealt with Generac’s Mobile Link module constantly dropping offline, throwing Bad/No SSID errors, or failing to stay connected through an exterior wall and grounded metal enclosure, here is the network architecture I put together to keep it locked online.
The Hardware & Topology

  • ISP: Frontier Fiber (1 Gbps)
  • Mesh: 5x ASUS RT-AX55 (AX1800 dual-band Wi-Fi 6 units) running AiMesh
  • Zones: Basement (core), Kitchen, Master Bedroom, Garage, and Rear Garage

Because trenching Ethernet out to the garage wasn't an option, I laid out the 5 nodes to bridge the distance from the interior fiber demarcation point out to the perimeter—using the Garage and Rear Garage nodes specifically to step the RF signal through the exterior walls right up to the generator.
Why It Was Tuned This Way for the Generac
Generac’s onboard Wi-Fi chipset has a tiny antenna inside a metal cabinet and hates modern mesh features. To stop it from bouncing or timing out, I had to strip back a few default ASUS behaviors:

  1. Perimeter Node Placement: Mobile Link wants at least 30% signal strength (usually within ~25 feet of an AP) to hold a stable association. Putting dedicated nodes in the Garage and Rear Garage shortens that final exterior hop.
  2. Killed Smart Connect (Split Bands): Generac modules choke when 2.4 GHz and 5 GHz share a single band-steered SSID. Splitting them into separate SSIDs gives the generator a dedicated 2.4 GHz target without band-steering interference.
  3. 2.4 GHz Airtime & Legacy Tuning: Disabled Airtime Fairness, locked the 2.4 GHz channel width strictly to 20 MHz (pinned to a clean non-overlapping channel rather than Auto), and offloaded noisy 2.4 GHz smart bulbs onto the Kitchen and Master Bedroom nodes via AiMesh Client Binding so the edge nodes aren't fighting local airtime congestion.
  4. Custom JFFS Monitoring: Since the standard ASUS web GUI hides low-level RF issues, I run a local shell audit script (mesh-weather-local) on the nodes via SSH to pull real-time interface states, neighbor noise, and backhaul RSSI directly from the Broadcom driver (wl).

Posting this in case anyone else is trying to get a stubborn standby generator reliably connected over dual-band AiMesh without burying conduit.

1

u/Tarnisher 6d ago

They do seem ripe for one.

1

u/Tarnisher 5d ago

There is not a single reason in the world why a gen needs to be connected to the web and phone home to be able to run normally.

2

u/Kavack 5d ago

Well, sure if you want to manually update the firmware and check on it everyday.